Why is Flux Through Core Doubled at Transformer Start-Up?

  • Thread starter Thread starter djsourabh
  • Start date Start date
AI Thread Summary
At transformer start-up, the flux through the core can double due to the simultaneous zeroing of both voltage and current, leading to a transient current surge. This surge occurs when the voltage is applied at a maximum phase, which can cause the core to approach saturation. The remanent induction from the previous cycle contributes to this effect, potentially tripling the induction value when the voltage reaches a positive peak. The resulting inrush current can be significantly higher than normal load current, sometimes reaching up to 14 times the rated current. This phenomenon highlights the importance of understanding transformer magnetizing characteristics and their impact on inrush behavior.
djsourabh
Messages
69
Reaction score
0
hello,i am se electrical student. I want to know why in a transformer at start up the flux through the core is doubled?
 
Last edited:
Engineering news on Phys.org
When a transformer is disconnected from a power source, the current is interrupted and the magnetic field or mmf driving flux through the core is reduced to zero. As we have seen in the preceding section, the core retains a residual induction which is called the remanence when the hysteresis path is on the positive descending (negative ascending) branch of a normal loop. In other cases, there could also be a residual induction but it would not have as high a magnitude. In order to drive the core to the zero magnetization state, it would be necessary to gradually lower the peak induction while cycling the field. Since the intrinsic normal hysteresis loops for oriented Si-Fe have fairly flat tops (or bottoms), the remanence is close to the peak induction. However, the presence of gaps in the core reduces this somewhat. When the unit is re-energized by a voltage source, the flux change must match the voltage change according to Faraday’s law. For a sinusoidal voltage source, the flux is also sinusoidal, where øp is the peak flux. Assuming uniform flux density, we have

øp=Bp.Ac

where Ac is the core cross-sectional area. Hence the peak voltage, using w=2пf, where f is the frequency in Hz, is

Vp=2пf.N.Bp.Ac

Thus to follow the voltage change, the induction must change by ± Bp over a cycle. If, in a worst case scenario, the voltage source is turned on when the voltage is at a value which requires a -Bp value and the remanent induction has a positive value of nearly Bp, then the induction will triple to nearly 3 Bp when the voltage reaches a value corresponding to +Bp. Since Bp is usually ~10 to 20 % below saturation in typical power transformers, this means that the core will be driven strongly into saturation, which requires a very high exciting current. This exciting current is called the inrush current and can be many times the normal load current in a transformer.


--------------------------------
Creative thinking is breezy, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
djsourabh said:
hello,i am se electrical student. I want to know why in a transformer at start up the flux through the core is doubled?
Normally when a transformer (without load) is running steady state on a sinusoidally varying voltage, the voltage leads the current by 90 degrees (e.g., V = L dI/dt). So during steady state operation, when the voltage is zero, the current is at a negative maximum. But at startup, both the voltage and the current are initially simultaneously zero (i.e., not 90 degrees apart). When the voltage is switched on at a phase where applied voltage is maximum, there is a transient current surge that wants to double the maximum core flux. If the inductance L is a nonlinear function of current, the current surge is worse.

Bob S
 
Bob S said:
When the voltage is switched on at a phase where applied voltage is maximum, there is a transient current surge that wants to double the maximum core flux.

Excuse me my dear friend, I think vice versa the increasing of flux (saturation condition) is origin of inrush magnetizing current, also mentioned phenomenon is related to transformer magnetizing characteristics (core material) not angle difference between voltage and current.

--------------------------------
Creative thinking is breezy, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
m.s.j said:
Excuse me my dear friend, I think vice versa the increasing of flux (saturation condition) is origin of inrush magnetizing current, also mentioned phenomenon is related to transformer magnetizing characteristics (core material) not angle difference between voltage and current.
I thought I was careful to state that the "surge that wants to double the maximum core flux". In addition, if the core saturates (i.e., dL/dI is negative), the current surge is much larger. I have one transformer that will often create so much current surge that all the lights in the building flicker when I switch it on.

Bob S
 
Bob S said:
I thought I was careful to state that the "surge that wants to double the maximum core flux".
Bob S

Dear Bob S,

Your description is related to RL circuit transient behavior due to circuit switching in time frame about milliseconds to a seconds which is an electromagnetic phenomenon regardless transformer magnetizing characteristics. As you know inrush current of transformer can be very huge ( up to 14*In ) with several times of mentioned time frame.

Best Regards
m.s.j
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...