System Loss In Terms of I why not V?

AI Thread Summary
System loss in transmission lines is primarily calculated using the formula i^2R, which highlights the importance of reducing current to minimize losses. However, an alternative calculation using v^2/R suggests that reducing voltage could also be beneficial. The discussion emphasizes that at radio frequencies, energy loss occurs mainly due to resistance, and the relationship between voltage and current is defined by the line's characteristic impedance. Power attenuation is the critical factor, particularly in the presence of reflected energy. Losses are typically expressed in logarithmic ratios, measured in dB per unit length, to effectively communicate the impact of these losses.
eee_engin33r
Messages
2
Reaction score
0
We all know that the system loss in transmission line is i^2R. So, in order to reduce the loss we diminish the current flow through the line by means of transformer.
My question is i can also calculate system loss by the formula v^2/R where v is the potential across transmission line. So, shouldn't we reduce the voltage instead of current in that sense?
 
Engineering news on Phys.org
in this case it would be the V DROP along the T line... not the applied voltage.
 
  • Like
Likes pocho and eee_engin33r
At radio frequencies, as a signal travels along a transmission line energy is lost, mostly by I2R to the resistance of the line. But the ratio of voltage to current on the line is determined by the characteristic impedance of the line. So, stricktly speaking, it is power that is attenuated along a line of fixed characteristic impedance, unless there is reflected energy.

That is why losses are specified using logarithmic ratios, in dB per set length.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top