The force of water from a fosset

  • Thread starter Thread starter TSN79
  • Start date Start date
  • Tags Tags
    Force Water
Click For Summary

Discussion Overview

The discussion revolves around calculating the pressure loss and flow rate of water from a faucet in a building project. Participants explore the implications of pressure measurements, pipe specifications, and faucet characteristics on water delivery, focusing on both theoretical and practical aspects of fluid dynamics in plumbing systems.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant calculates a pressure loss from 3.7 bars in the basement to 1.8 bars at the top floor and questions if this pressure is sufficient for water flow when the faucet is fully opened.
  • Another participant notes that in the US, a design standard of 2.5 gallons per minute is common, but emphasizes that actual flow depends on faucet and piping specifications.
  • A participant inquires about the source of water supply, suggesting that municipal supply pressure must be higher than the building's top level for adequate flow.
  • Details about the apartment's required flow rate of 0.4 l/s and the pipe's internal diameter of 12 mm are provided, along with the faucet's pressure loss of 1 bar.
  • Concerns are raised about the implications of a hypothetical scenario where the faucet experiences a pressure loss equal to the available pressure, questioning whether any water would flow in that case.
  • One participant introduces a flow equation for valves, discussing how to determine flow coefficients and the relationship between flow rate and pressure drop.
  • Another participant comments on the relationship between pressure drop and flow, suggesting that losses must be less than the driving pressure difference for flow to occur.

Areas of Agreement / Disagreement

Participants express varying views on the adequacy of the pressure and flow rate calculations, with no consensus reached on the implications of the pressure losses or the sufficiency of the setup for water delivery.

Contextual Notes

Participants mention various assumptions regarding municipal supply pressure, peak flow rates, and the specific characteristics of the faucet and piping, which may affect the overall analysis but remain unresolved in the discussion.

TSN79
Messages
422
Reaction score
0
I'm doing pressure calculations for a building project. I'm added all the bends and lengths of pipe up to the fosset on the top floor to find the pressure loss. In the basement there is 3,7 bars of pressure. At the top I'm left with 1,8 bars. Is this enough? What I wonder is how I can figure out what kind of force and amount the water will bring as the fosset is opened fully? Any help is appreciated.
 
Engineering news on Phys.org
In the US, we design for 2.5 gallons per minute, but don't actually calculate how much water you'll get. That depends as much on the faucet as it does the piping, and they are regulated . But if you calculated 1.8 bar at whatever flow rate you need you should be fine.

What size piping are you using, how long is it, how high does it go, and what flow rate are you looking for?
 
Are you running straight from a municipal supply, or do you have your own pumping station and reservois? If the former, then your top level has to be lower than the city water tower. Those are usually designed to feed at between 50-70 psi (sorry, I don't know from bars). You'll have to estimate your peak flow rate, as opposed to average. That will depend very much upon what kind of building it is. A large apartment complex, for example, will have a far higher peak usage in the morning (showers, toilets, etc.) than an office tower.
 
russ_watters said:
What size piping are you using, how long is it, how high does it go, and what flow rate are you looking for?

The apartment needs approx 0,4 l/s, and the pipe that is to provide this measures about...12 mm inside. The water comes from a municipal supply which delivers 3,7 bars (370 000 Pa) static pressure to the basement. As mentioned, I'm left with 1,8 on top (before passing through the faucet) after taking into account all bends, height etc. The manufacturer says the faucet has a pressure loss of 1 bar.

Say the faucet had exactly 1,8 bars of loss, what would be the outcome then? Would there come any water at all?

Confused...
 
The manufacturer says the faucet has a pressure loss of 1 bar.

Say the faucet had exactly 1,8 bars of loss, what would be the outcome then?
Flow through a valve is given by equations shown here:
http://www.engineeringtoolbox.com/flow-coefficients-d_277.html

In metric units:

Cv = 11.7 q (SG / dp)^.5

where
q = water flow (m3/h)
SG = specific gravity (1 for water)
dp = pressure drop (kPa)

If you don't know the Cv of the valve, and if the manufacturer of the valve can't give it to you, you can determine that in various ways. One way would be to take the flow rate at a given pressure drop and simply put it into the equation above. Another way is to calculate it from the geometry inside the valve. That's a bit more tricky.
 
In real life, the delta P across an object is proportional to the flow. Also, you will always have atmospheric pressure on one side. That means that if you just happen to have 1.8 bar(g) on the inlet, and you just happen to have a delta P across it of 1.8 bar, you will still have the same scenario as if you had 1.8 bar(g) inlet and no losses. Again, in reality, the losses have to be less than the driving pressure difference.
 

Similar threads

  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 14 ·
Replies
14
Views
4K
Replies
2
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 20 ·
Replies
20
Views
11K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 6 ·
Replies
6
Views
5K