The discussion centers on the discrepancies between calculated and reported U-factors for single glazing, with a focus on thermal losses. The user calculated a U-factor of 262.5 W/m^2.K based on thermal conductivity, which contrasts sharply with the commonly cited value of 5.7 W/m^2.K. The conversation highlights the importance of considering convective heat transfer, which can significantly affect heat loss calculations. It is noted that the overall U-value is influenced by three thermal resistances: convection inside the room, conduction through the glass, and convection outside. Accurate U-values depend on specific conditions, including temperature differences and wind speed, indicating that standard values may vary.
lust
Messages
2
Reaction score
0
Hello,
I have looked through various websites, which show single glazing heat losses (U-factor) to be 5.7 W/m^2.K.
But when I use thermal conductivity basic formulas, the yielded results are quite different:
k of glass is 1.05 W/m.K; L -> glass thickness is 4 mm = 0.004 m; so:
U = k/L = 1.05 / 0.004 = 262.5 W/m^2.K

I tried transparent vynil sheets 800 microns thick (vynil-crystal, used as wind shields) and it yields better results, at k = 0.19 for PVC, U factor is about 190 W/m^2.K.

This is for an outside "winter garden", which I "single glazed" with vinyl crystal. Currently I am not able to heat it up above 10 degrees celsius, the roof is polycarbonate multi-wall sheet, supposed U factor given from manufacturers 3.4 W/m^2.K. 50 m^2 of room area.

So, my main question is, what is the CORRECT heat loss from single glazing? The one from the internet or the one that I have calculated?
 
Science news on Phys.org
Your result is wrong (too high) because you ignored the convective heat transfer between the glass and the air, on both sides.

If the room air temperature is say 20 degrees C and the outside air temperature is 0, the surface temperatures of the glass will be less than 20, and greater than 0. In fact if your number and the website are both "right", the glass surface temperatures are more like 10.2 and 9.8 degrees than 20 and 0.

I don't know if the website value is "right". An accurate value would depend on the wind speed outside the window, for example.

There is some information on convective heat transfoer from a flat plate to air here:
http://www.thermal-wizard.com/tmwiz/convect/natural/vp-isot/vp-isot.htm
 
Well, I've tried to understand what you've said, but I'm a non-physicist... Do I need to get the temperature difference in a different manner? I have filled the calculator you gave me with the following data:

specific heat: 840 J/kg.K
thermal expansion: 0.0000059 m/m.K
conductivity: 1.05 W/m.K
dynamic viscosity: 10 kg/m.s
density: 2800 kg/m^3
emissivity: 0

width: 1.0
height: 1.0
plate temperature: 15
ambient: 2

The results yielded 253 W as convective heat transfer, and 19 W/m^2.K for the coefficient;
I don't know for sure if this is the holy truth, and still need a more clear explanation on how convection can actually LOWER the heat loss.
Any further explanation I welcome :)
 
The numbers you supply are supposed to be the properties of air, not of the glass. The defailts are for air at 20 C which is probably near enough.

Basically you have three thermal resistances in series.

Convection between the air and glass inside the room
Conduction through the glass
Convection between the air and glass outside the room.

If you have the three "U" values, the overall "U" value is
$$\frac{1}{\frac{1}{U_1} + \frac{1}{U_2} + \frac{1}{U_3}}$$

So assuming your 19 W/m^2 K was right (it isn't, because the material propertires are wrong) the overall U value would be
1 / (1/19 + 1/262.5 + 1/19) = 9.2 W/m^2 K

Because the glass is a much better conductor (U = 262) than the convection between the glass and the air (U = 19), you can make the approximation that the temperature of both sides of the glass is mid way between the inside and outside air temperatures.

You will probably find the "U" values for the convection change a lot depending on the temperature difference. To compare with the glazing web site, you need to know what temperature difference they use as a standard value for comparing different types of glazing.
 
I need to calculate the amount of water condensed from a DX cooling coil per hour given the size of the expansion coil (the total condensing surface area), the incoming air temperature, the amount of air flow from the fan, the BTU capacity of the compressor and the incoming air humidity. There are lots of condenser calculators around but they all need the air flow and incoming and outgoing humidity and then give a total volume of condensed water but I need more than that. The size of the...
Thread 'Why work is PdV and not (P+dP)dV in an isothermal process?'
Let's say we have a cylinder of volume V1 with a frictionless movable piston and some gas trapped inside with pressure P1 and temperature T1. On top of the piston lay some small pebbles that add weight and essentially create the pressure P1. Also the system is inside a reservoir of water that keeps its temperature constant at T1. The system is in equilibrium at V1, P1, T1. Now let's say i put another very small pebble on top of the piston (0,00001kg) and after some seconds the system...