Thermal Resistance due to Convection Heat Transfer

Click For Summary

Discussion Overview

The discussion revolves around calculating thermal resistance and conductance for a wall construction in a single-family residence, specifically addressing the impact of convection heat transfer on these values. Participants explore both theoretical calculations and practical implications, including assumptions and comparisons between different materials.

Discussion Character

  • Homework-related
  • Mathematical reasoning
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant outlines the construction details and initial calculations for thermal resistance and conductance, including the thermal properties of each wall layer.
  • Another participant clarifies that a temperature difference is not necessary to calculate total resistance or U-value, which can be derived from the given heat transfer coefficients and thermal conductivities.
  • A participant expresses confusion regarding the relationship between heat loss and gain, indicating a need for further understanding of the problem setup.
  • One participant confirms their understanding of the first part and attempts to clarify the relationship between U-factor and total thermal resistance using the formula 1/U = (1/h1) + (1/ktotal) + (1/h2).
  • Another participant questions the accuracy of the initial conductance value, suggesting a possible error in the conversion factor from watts to BTU/hr.

Areas of Agreement / Disagreement

Participants generally agree on the need to calculate total thermal resistance and conductance, but there are discrepancies in the calculated values and methods, particularly regarding the conversion factors and the interpretation of the equations involved. The discussion remains unresolved with multiple competing views on the calculations.

Contextual Notes

Participants express uncertainty about the assumptions made in the calculations, particularly regarding the definitions of thermal resistance and conductance. There are also unresolved issues related to the conversion factors used in the calculations.

Who May Find This Useful

This discussion may be useful for students studying thermal dynamics in building construction, particularly those interested in the effects of material properties and convection on thermal performance.

EmilyO89
Messages
4
Reaction score
0

Homework Statement



1) A typical wall construction for a single-family residence might consist of 0.375 inches of outer sheathing (insulating board, hardwood siding, etc.), 3.5 inches of mineral fiber insulation and then a 0.375 inches inner surface (gypsum, etc.). Typical thermal conductivities for these materials are 0.1 W/m-C for the siding, 0.046 W/m-C for the insulation and 0.17 W/m-C for the inner surface. Determine the total thermal resistance (hr-ft2-F/Btu) and total wall conductance (Btu/hr-ft2-F). Also find the percent of total resistance for the three different materials. Provide step-by-step calculation procedures. Discuss/comment to include as a minimum things like assumptions, effects of each wall-layer on heat flow, etc (2.5 points).

2) Part 1 neglected thermal resistances due to convection heat transfer on the inner and outer wall surfaces. Recalculate the total thermal resistance (along with percent) and the wall U-factor including convection heat transfer using an outer wall convection heat transfer coefficient of 6.0 Btu/hr-ft2-F (15 mph wind in the winter) and an inner wall value of 1.46 Btu/hr-ft2-F. Provide step-by-step calculation procedures. Discuss/comment to include as a minimum things like assumptions, comparisons, etc (2.5 points).

Homework Equations



Rth (thermal resistance ,R-value) =1/U-value=L/k (h∙ft2∙F/Btu)

U-value (thermal conductance) = k/L (Btu/h∙ft2∙F)

Fourier’s Law: qcond= kA (T1–T2)/L

where,
k=thermal conductivity(Btu∙in/h∙ft²∙F or W/m∙K)
A=area through which conduction occurs
T1= higher temperature
T2= lower temperature
L= thickness of material

The Attempt at a Solution



Part 1)

Siding

0.375in thickness or 0.375in×2.54cm/1in×1m/100cm=0.009525 m

k=0.1 W/(m×℃)

Insulation

3.5in thickness or 3.5in×2.54cm/1in×1m/100cm=0.0889 m

k=0.46 W/(m×℃)

Inner Surface

0.375in thickness or 0.375in×2.54cm/1in×1m/100cm=0.009525 m

k=0.17 W/(m×℃)

Note: As the common SI unit for Thermal Resistance is (m^2×℃)/W it is necessary to convert the thickness value into meters.

Thermal Resistance (R)

〖R_th〗_siding=L/k=0.009525m/(0.1 W/m℃)=0.09525 (m^2×℃)/W

〖R_th〗_insulation=L/k=0.0889m/(0.046 W/m℃)=1.9326 (m^2×℃)/W

〖R_th〗_inner=L/k=0.009525m/(0.17 W/m℃)=0.056029 (m^2×℃)/W

〖R_th〗_total=〖R_th〗_siding+ 〖R_th〗_insulation+ 〖R_th〗_inner=(0.09525 (m^2×℃)/W )+(1.9326 (m^2×℃)/W)+(0.056029 (m^2×℃)/W)=2.08 (m^2×℃)/W

or…

2.08 (m^2×℃)/W ×1W/(0.2931 Btu/h)×(10.76ft^2)/(1m^2 )×(9℉)/(5℃)=137 (hr×ft^2×℉)/Btu

Percentage of R value per material:

Siding: ((0.09525 (m^2×℃)/W)/(2.08 (m^2×℃)/W))×100=4.6%

Insulation: ((1.9326 (m^2×℃)/W)/(2.08 (m^2×℃)/W))×100=92.9%

Inner Surface: ((0.056029 (m^2×℃)/W)/(2.08 (m^2×℃)/W))×100=2.7%

Note: Both the siding, and the inner wall surface have provide very little R-value. The insulation allows for thinner walls, as it would take an abundant amount of either siding or inner surface to achieve an acceptable level of thermal resistance.

Wall Conductance (C)

C=1/R=1/137 Btu/(hr×ft^2×℉)

Note: Wall conductance is simply the inverse of the R-value, often expressed as U-value. It measures the rate of heat flow though a unit area of a material. This should not be confused with thermal conductivity (k), which is an inherent property of the material.

Part 2) I have been staring at this for hours trying to understand what I'm not understanding! I know it must have something to do with the heat loss on the inside being equal to the heat gain on the outside, but I just cannot figure out how to get started on this problem without knowing the temperature difference.

Any help, tips, or hints would be greatly appreciated!
 
Physics news on Phys.org
Regarding part 2): You don't need a temperature to calculate the resistance (or the u-value), you only would need it if you want to calculate the heat passing the wall. So you simply can calculate the total resistance/u-value with the given heat transfer coefficients and the thermal conductivities.

Regarding part1): I didn't check it, because it seemed to be finished. Need something special with that?
 
I think I understood the first part fine. I just included in in case anything was needed from it for part 2.

I think I get the second part now...the use of different terms to refer to the same variable was throwing me off.

I should just use 1/U=(1/h1)+(1/ktotal)+(1/h2). U will equal the U factor, and 1/U will equal the R factor (total thermal resistance)...correct?

Thank you the help!
 
You're welcome!

Basically the formula is correct, but just to be sure about the (1/ktotal)-part. In your first post you defined k as the heat conductivity in W / (m⋅K). If ktotal has the same dimension, the equation isn't finished.
 
I don't get the same answer as you for part 1. I get a conductance value of 0.08 ##\frac{BTU}{hr-ft^2-F}##.

Your conversion factor from watts to BTU/hr looks flipped.

Chet
 
Last edited:

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
Replies
1
Views
5K
Replies
1
Views
3K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 1 ·
Replies
1
Views
4K
Replies
7
Views
2K
  • · Replies 2 ·
Replies
2
Views
5K
  • · Replies 4 ·
Replies
4
Views
3K
Replies
2
Views
2K
Replies
3
Views
2K