Transformer exceeding its rated maximum temperature

AI Thread Summary
The discussion focuses on calculating the operational limits of an oil-filled transformer rated at 500 kVA when subjected to a load increase from 600 kVA to 750 kVA. The transformer can operate continuously at an ambient temperature of 35°C with a maximum oil temperature of 85°C, allowing for a temperature rise of 50°C. The heating curve equation indicates that the temperature rise is influenced by the time constant of 1.5 hours and the ratio of copper to iron losses. Participants clarify the meaning of "e" in the temperature rise equation, confirming it represents Euler's Number. The user seeks further guidance on calculating the impact of the increased load on the transformer's temperature limits.
clembo
Messages
8
Reaction score
0

Homework Statement



An oil-filled transformer has a c.m.r. of 500 kVA which allows it to run continuously in an ambient of 35°C with an oil temperature rise of 50°C. The transformer has a time constant of 1.5. hours and the ratio of copper losses to iron losses at c.m.r. is 1.5:1.

After switch-on, the transformer supplies a load of 600 kVA for one hour and the load then rises to 750 kVA. Calculate the period of time that the transformer can supply this load without exceeding its rated maximum temperature. Sketch the heating curves for the two loads.[/B]

Homework Equations



The temperature rise of a transformer is given by the equation
[/B]
-t/τ
θ = θm ( 1 - e )

where

θ is the temperature rise at any time t,
θm is the final steady temperature,
τ is the heating time constant (determined by the heat capacity and efficiency of cooling).

The Attempt at a Solution



From the above equation I understand the temperature rise, final steady temperature and time constant. But what does anyone know what the "e" signifies. Any help on this question would be very appreciated. I can't find much information on this topic online.

Many thanks

Andy[/B]
 
Physics news on Phys.org
Another thing - it is not really clear in your notation, but it should be $$θ = θm(1 - e^{-t/τ})$$
to indicate exponential "decay" upward toward θm.
 
scottdave said:
Another thing - it is not really clear in your notation, but it should be $$θ = θm(1 - e^{-t/τ})$$
to indicate exponential "decay" upward toward θm.
Thank you Scottdave that is very helpful.
 
So far I have:

The max temperature my oil filled transformer can handle without damage or ageing occurring is 85 deg.

With an ambient temperature of 35 deg and a load of 500 kVA the transformer will run continuously quite happy.

My transformer time constant is 1.5
Ratio of copper losses to iron losses at CMR is 1.5:1

For a 500 kVA transformer I can work out using:

θ=θm(1−e−t/τ)

= 50(1-e-t/1.5)

=24.33 deg

This would mean that my transformer is running at 59.33 deg

I am struggling to work out where to go from here. Is it just a % of this figure as 600 kVA is 20% overloaded?
 
If you highlight the characters you want superscript then press the x2 button above the textbox.
 