The discussion focuses on calculating the equivalent circuit parameters of a 200 KVA, 4000/1000 V transformer based on its efficiency and voltage regulation. The efficiency is established at 0.97 for both full load and 60% load, leading to the determination of copper and iron losses. The full load current is calculated as 50A, resulting in an equivalent resistance of 0.0967 ohms when referred to the low voltage side. The voltage regulation is derived to be 5% at a power factor of 0.8, with the voltage E calculated as 4200 V. The user seeks assistance in finding the reactance parameter X2, indicating a preference for solving without using the per unit method.
jaus tail
Messages
613
Reaction score
48

Homework Statement


For 200 KVA, 4000/1000 V transformer. 1 phase.
Efficiency is 0.97 at full load and 60% load at unity power factor.
No load pf = 0.25
Full load Voltage regulation at 0.8 pf lag is 5%
Find transformer ckt parameters for referred to lv side

Homework Equations


efficiency is output / (output + copper loss + iron loss)
cu loss varies as square of current
or as square of percent load

voltage regulation is (|E2| - |V2|)/|V2|

The Attempt at a Solution



Well efficiency is 0.97 at both times:
full load and 60% load. both times unity pf.
so
.97 = output/(output + losses_
0.97 = 200000/(200000 + Pi + Pcu)
and
for 60% load
0.97 = 200000*0.6/(200000*0.6 + Pi + .36Pcu)

I got Pcu at full load = 3868.98 VA
Pi = 2319.59 VA

Full load current at unity pf = 200000/4000 = 50A
So Pcu = 502 * R(eq)
So R(eq) = 1.545 on HV Side
R(2) = 0.7725 ohm
Referring to LV side by multiplying by (4000/1000)2 I get 0.0967 ohm. (This matches book answer of 0.0961)

I don't know how to find out X parameter of leakage impedance.
The formula for voltage regulation is
(|E| - |V||)/|V| = 0.05 (given 5% regulation at 0.8 pf lag and full load)
V is 4000 V
So I get |E| = 4200 V.

Now:
E2 = V2 + (IZ) --- All vectors
V2 = 4000 V and is reference so angle is 0
I is 200000/4000 = 50A at angle 36.87 lagging V2 (given pf is 0.8). ---> I'm not sure whether I should be 50 or 50/0.8 A as pf is 0.8 at full load.

Z = R2 + jX2
R2 = 0.7725ohm.
I have to find X2.
So
4200 (at unknown angle) = 4000 + 50(lagging angle is 36.87) * Z(also some angle)
I don't know how to proceed to find X2.
Do I have to split the above equation in imaginary and real terms?

Book has used per unit method, but I want to try without per unit method to see if it works.
 
Physics news on Phys.org
jaus tail said:
Full load Voltage regulation at 0.8 pf lag is 5
You can use the formula for approximate voltage regulation here.
Regulation= (IRcosΦ+IXsinΦ)/V2, where R and X are referred to lv and I is the secondary full load current.

(Note IR/V2= Rpu and IX/V2= Xpu).
 
  • Like
Likes jaus tail
Got it. Thanks. I was using R as only R secondary and not the R equivalent.
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 2 ·
Replies
2
Views
6K
  • · Replies 28 ·
Replies
28
Views
7K
  • · Replies 30 ·
2
Replies
30
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
7
Views
3K