Transformer Impedance Discussion

Click For Summary

Discussion Overview

The discussion revolves around calculating the short circuit current rating of a transformer, specifically a 7.5KVA transformer supplying a 120 volt panel. Participants explore the relationship between transformer impedance and short circuit current, discussing both theoretical and practical aspects of transformer operation.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant calculates the short circuit current using the formula P=IV, arriving at 62.5 Amps and questions how the impedance of 0.03 relates to R + jX.
  • Another participant emphasizes the need for complex calculations in AC circuits, mentioning the importance of active power and reactive power, and the role of cos(phi) in power calculations.
  • A different participant suggests that the 3% impedance might be a per-unit value and provides a method to calculate short circuit current using per-unit systems.
  • Several participants discuss the implications of the 3% impedance, with one suggesting it represents the maximum voltage drop under full load conditions, and another calculating the transformer secondary resistance based on this percentage.
  • Complex representations of current and impedance are introduced, with one participant detailing the relationship between primary and secondary winding resistances and reactances.
  • Corrections and refinements to earlier claims are made, particularly regarding the formulas for calculating impedance and short circuit current in both single-phase and three-phase systems.

Areas of Agreement / Disagreement

Participants express differing views on the interpretation of the 3% impedance and its implications for short circuit current calculations. There is no consensus on how to best relate R and jX to the given impedance value, and multiple approaches are presented without resolution.

Contextual Notes

Some calculations depend on specific assumptions about the transformer and circuit conditions, such as whether the 3% impedance applies to both windings or just the secondary. The discussion also highlights the complexity of AC circuit analysis and the need for careful consideration of definitions and units.

psparky
Science Advisor
Gold Member
Messages
884
Reaction score
31
I was working on trying to find the short circuit current rating of a 120 volt panel fed from a 7.5KVA transformer.

Using P=IV you get 7.5KVA=120 * I

I = 62.5 Amps.

Then I believe you divide that current by the impedance of the transformer. .03 is the impedance in this case in the transformer specs. So I do the math and I get about 2,000 amp short circuit rating.

Great. My question is this. If impedance is R + JX, how does .03 relate to that?

Is it possible the R+jx add up to be .03? Or is that nonsense? I believe they even state the .03 as 3% as well.
 
Last edited:
Engineering news on Phys.org
Ok, I am not an expert in electronics but if you have a circuit with impedances then its automatically an alternating current circuit. In this case I am only able to use complex way to calculate. (Z_complex * I_complex = V_complex)
You have apparent power and therefore effective/active power and reactive power.
There has to be a cos(phi) in your calculation of power. active power should be defined as P=V*I*cos(phi)
You can't easily divide P by U for the current.
U is the source voltage, but there is also R, and X (capacity or inductivity)
that means you have dropout voltages on R and X (Vr and Vx)
Also impedances generally have units, it's Ohm
 
Sparky - I believe you are getting to the right answer.

I was taught a simpler method
Your 3% impedance is probably per-unit

so 1 per unit volts / 0.03 per unit impedance = 33.3 per unit amps
and your per-unit amperage is 62.5 .

62.5 amps X 33.3 = 2081 amps into a zero impedance fault, about what you got

(That's why your household 15 amp breakers say something preposterous on the back like 10,000 amps - don't [STRIKE]use[/STRIKE] attempt to use one downstream from a source capable of more fault current than that .)

i've not seen it broken down into R and X for small transformers.

Clearly the impedance of interconnecting wires and of the circuit breaker itself aid in limiting fault current.

old jim
 
Interesting approach Jim.

I'm still looking for the relation of R+ jx to the transformer impedence (.03)

I will hit up my old electronics mentor from college. I have yet to stump him.
 
120V, 7.5kVA; I = 62.5A
R load = V / I = 1.92 ohm

I believe the 3% is the maximum percentage of voltage drop to be lost in the transformer secondary and circuit under full load conditions.
3% of 1.92 ohm = 0.0576 ohm transformer secondary resistance.
Short circuit current will be V / R = 120 / 0.0576 = 2083.3A

If you know the current rating of the panel, you do not need to know the line voltage.
Short circuit current will be 63A * 100% / 3% = 2100.A
 
If we’ll represent the current flowing through transformer in complex:
I=I*[cos(fi)-j*sin(fi)] and [neglecting the magnetic circuit of Xm and Rfe] the transformer impedance will be: Z=R1+R’2+j*(X1+X’2) where R1= primary winding resistance R’2=secondary winding resistance referred to primary and X1=leakage magnetic flux reactance of primary winding X’2=secondary winding leakage reactance referred to primary.
Then we may take R1+R’2=R and X1+X’2=X and Z=R+j*X.
abs(I*Z)[complex]=abs(I*[cos(fi)-j*sin(fi)]*(R+j*X)
I*Z=I*{[R*cos(fi)+X*sin(fi)]+j*[X*cos(fi)-R*sin(fi)]}
abs(I*Z)=I*SQRT{[R*cos(fi)+X*sin(fi)]^2+[X*cos(fi)-R*sin(fi)]^2}=I*SQRT(R^2+X^2)
abs(I*Z)[complex]=abs(I)*abs(Z)=V1-V’2 [Voltage dip-or voltage sag- through transformer.
This voltage dip -if the current will be Irated- it is the short-circuit voltage[vk] and it is represented in p.u.-vk%=vk/Vrated*100.
Z=vk%*Vrated/Irated for single-phase [or two-phase] system and Z=vk%*Vrated/sqrt(3)/Irated.
By multiplying [and dividing] by Vrated Z=vk%*Vrated^2/Srated where S=SQRT(3)*Vrated*Irated [the apparent rated power of the transformer].
 
Correction:
Z=vk%/100*Vrated/Irated for single-phase [or two-phase] system and Z=vk%/100*Vrated/sqrt(3)/Irated for three-phase system.
By multiplying [and dividing] by Vrated Z=vk%/100*Vrated^2/Srated.
Ik1=Vrated/Z or Ik3=Vrated/Z/sqrt(3).By substituting Z=vk%/100*Vrated/Irated
Ik1=Irated*100/vk% or Ik3=Irated*100/vk% as Baluncore already said.
 
I believe the 3% is the maximum percentage of voltage drop to be lost in the transformer secondary and circuit under full load conditions.
3% of 1.92 ohm = 0.0576 ohm transformer secondary resistance.
Short circuit current will be V / R = 120 / 0.0576 = 2083.3A

Secondary? or both windings, ie lumped ?

One per unit load gives voltage drop numerically equal to per unit Z, without having to worry about turns ratios .
Handy, eh? That's why there's 'per unit' .
 
Of course, if you will consider a Zbase=Vrated^2/Srated then vk=Z/Zbase[p.u.] or vk%=Z/Zbase*100
 
  • #10
Babadag said:
If we’ll represent the current flowing through transformer in complex:
I=I*[cos(fi)-j*sin(fi)] and [neglecting the magnetic circuit of Xm and Rfe] the transformer impedance will be: Z=R1+R’2+j*(X1+X’2) where R1= primary winding resistance R’2=secondary winding resistance referred to primary and X1=leakage magnetic flux reactance of primary winding X’2=secondary winding leakage reactance referred to primary.
Then we may take R1+R’2=R and X1+X’2=X and Z=R+j*X.
abs(I*Z)[complex]=abs(I*[cos(fi)-j*sin(fi)]*(R+j*X)
I*Z=I*{[R*cos(fi)+X*sin(fi)]+j*[X*cos(fi)-R*sin(fi)]}
abs(I*Z)=I*SQRT{[R*cos(fi)+X*sin(fi)]^2+[X*cos(fi)-R*sin(fi)]^2}=I*SQRT(R^2+X^2)
abs(I*Z)[complex]=abs(I)*abs(Z)=V1-V’2 [Voltage dip-or voltage sag- through transformer.
This voltage dip -if the current will be Irated- it is the short-circuit voltage[vk] and it is represented in p.u.-vk%=vk/Vrated*100.
Z=vk%*Vrated/Irated for single-phase [or two-phase] system and Z=vk%*Vrated/sqrt(3)/Irated.
By multiplying [and dividing] by Vrated Z=vk%*Vrated^2/Srated where S=SQRT(3)*Vrated*Irated [the apparent rated power of the transformer].

Interesting stuff. Wish I had the brains to understand it.
 
  • #11
Baluncore said:
120V, 7.5kVA; I = 62.5A
R load = V / I = 1.92 ohm

I believe the 3% is the maximum percentage of voltage drop to be lost in the transformer secondary and circuit under full load conditions.
3% of 1.92 ohm = 0.0576 ohm transformer secondary resistance.
Short circuit current will be V / R = 120 / 0.0576 = 2083.3A

If you know the current rating of the panel, you do not need to know the line voltage.
Short circuit current will be 63A * 100% / 3% = 2100.A

Gotcha, thanks.
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 21 ·
Replies
21
Views
2K
  • · Replies 14 ·
Replies
14
Views
3K
Replies
6
Views
4K
  • · Replies 5 ·
Replies
5
Views
7K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 15 ·
Replies
15
Views
5K
  • · Replies 23 ·
Replies
23
Views
5K