Transformer Impedance Discussion

In summary, the conversation discusses finding the short circuit current rating of a 120 volt panel fed from a 7.5KVA transformer. The equation P=IV is used to calculate the current, which is then divided by the impedance of the transformer (.03) to get a short circuit rating of about 2,000 amps. The conversation also delves into the relationship between R and jX in impedance calculations, and the use of per-unit measurements in determining short circuit current.
  • #1
psparky
Gold Member
884
33
I was working on trying to find the short circuit current rating of a 120 volt panel fed from a 7.5KVA transformer.

Using P=IV you get 7.5KVA=120 * I

I = 62.5 Amps.

Then I believe you divide that current by the impedance of the transformer. .03 is the impedance in this case in the transformer specs. So I do the math and I get about 2,000 amp short circuit rating.

Great. My question is this. If impedance is R + JX, how does .03 relate to that?

Is it possible the R+jx add up to be .03? Or is that nonsense? I believe they even state the .03 as 3% as well.
 
Last edited:
Engineering news on Phys.org
  • #2
Ok, I am not an expert in electronics but if you have a circuit with impedances then its automatically an alternating current circuit. In this case I am only able to use complex way to calculate. (Z_complex * I_complex = V_complex)
You have apparent power and therefore effective/active power and reactive power.
There has to be a cos(phi) in your calculation of power. active power should be defined as P=V*I*cos(phi)
You can't easily divide P by U for the current.
U is the source voltage, but there is also R, and X (capacity or inductivity)
that means you have dropout voltages on R and X (Vr and Vx)
Also impedances generally have units, it's Ohm
 
  • #3
Sparky - I believe you are getting to the right answer.

I was taught a simpler method
Your 3% impedance is probably per-unit

so 1 per unit volts / 0.03 per unit impedance = 33.3 per unit amps
and your per-unit amperage is 62.5 .

62.5 amps X 33.3 = 2081 amps into a zero impedance fault, about what you got

(That's why your household 15 amp breakers say something preposterous on the back like 10,000 amps - don't [STRIKE]use[/STRIKE] attempt to use one downstream from a source capable of more fault current than that .)

i've not seen it broken down into R and X for small transformers.

Clearly the impedance of interconnecting wires and of the circuit breaker itself aid in limiting fault current.

old jim
 
  • #4
Interesting approach Jim.

I'm still looking for the relation of R+ jx to the transformer impedence (.03)

I will hit up my old electronics mentor from college. I have yet to stump him.
 
  • #5
120V, 7.5kVA; I = 62.5A
R load = V / I = 1.92 ohm

I believe the 3% is the maximum percentage of voltage drop to be lost in the transformer secondary and circuit under full load conditions.
3% of 1.92 ohm = 0.0576 ohm transformer secondary resistance.
Short circuit current will be V / R = 120 / 0.0576 = 2083.3A

If you know the current rating of the panel, you do not need to know the line voltage.
Short circuit current will be 63A * 100% / 3% = 2100.A
 
  • #6
If we’ll represent the current flowing through transformer in complex:
I=I*[cos(fi)-j*sin(fi)] and [neglecting the magnetic circuit of Xm and Rfe] the transformer impedance will be: Z=R1+R’2+j*(X1+X’2) where R1= primary winding resistance R’2=secondary winding resistance referred to primary and X1=leakage magnetic flux reactance of primary winding X’2=secondary winding leakage reactance referred to primary.
Then we may take R1+R’2=R and X1+X’2=X and Z=R+j*X.
abs(I*Z)[complex]=abs(I*[cos(fi)-j*sin(fi)]*(R+j*X)
I*Z=I*{[R*cos(fi)+X*sin(fi)]+j*[X*cos(fi)-R*sin(fi)]}
abs(I*Z)=I*SQRT{[R*cos(fi)+X*sin(fi)]^2+[X*cos(fi)-R*sin(fi)]^2}=I*SQRT(R^2+X^2)
abs(I*Z)[complex]=abs(I)*abs(Z)=V1-V’2 [Voltage dip-or voltage sag- through transformer.
This voltage dip -if the current will be Irated- it is the short-circuit voltage[vk] and it is represented in p.u.-vk%=vk/Vrated*100.
Z=vk%*Vrated/Irated for single-phase [or two-phase] system and Z=vk%*Vrated/sqrt(3)/Irated.
By multiplying [and dividing] by Vrated Z=vk%*Vrated^2/Srated where S=SQRT(3)*Vrated*Irated [the apparent rated power of the transformer].
 
  • #7
Correction:
Z=vk%/100*Vrated/Irated for single-phase [or two-phase] system and Z=vk%/100*Vrated/sqrt(3)/Irated for three-phase system.
By multiplying [and dividing] by Vrated Z=vk%/100*Vrated^2/Srated.
Ik1=Vrated/Z or Ik3=Vrated/Z/sqrt(3).By substituting Z=vk%/100*Vrated/Irated
Ik1=Irated*100/vk% or Ik3=Irated*100/vk% as Baluncore already said.
 
  • #8
I believe the 3% is the maximum percentage of voltage drop to be lost in the transformer secondary and circuit under full load conditions.
3% of 1.92 ohm = 0.0576 ohm transformer secondary resistance.
Short circuit current will be V / R = 120 / 0.0576 = 2083.3A

Secondary? or both windings, ie lumped ?

One per unit load gives voltage drop numerically equal to per unit Z, without having to worry about turns ratios .
Handy, eh? That's why there's 'per unit' .
 
  • #9
Of course, if you will consider a Zbase=Vrated^2/Srated then vk=Z/Zbase[p.u.] or vk%=Z/Zbase*100
 
  • #10
Babadag said:
If we’ll represent the current flowing through transformer in complex:
I=I*[cos(fi)-j*sin(fi)] and [neglecting the magnetic circuit of Xm and Rfe] the transformer impedance will be: Z=R1+R’2+j*(X1+X’2) where R1= primary winding resistance R’2=secondary winding resistance referred to primary and X1=leakage magnetic flux reactance of primary winding X’2=secondary winding leakage reactance referred to primary.
Then we may take R1+R’2=R and X1+X’2=X and Z=R+j*X.
abs(I*Z)[complex]=abs(I*[cos(fi)-j*sin(fi)]*(R+j*X)
I*Z=I*{[R*cos(fi)+X*sin(fi)]+j*[X*cos(fi)-R*sin(fi)]}
abs(I*Z)=I*SQRT{[R*cos(fi)+X*sin(fi)]^2+[X*cos(fi)-R*sin(fi)]^2}=I*SQRT(R^2+X^2)
abs(I*Z)[complex]=abs(I)*abs(Z)=V1-V’2 [Voltage dip-or voltage sag- through transformer.
This voltage dip -if the current will be Irated- it is the short-circuit voltage[vk] and it is represented in p.u.-vk%=vk/Vrated*100.
Z=vk%*Vrated/Irated for single-phase [or two-phase] system and Z=vk%*Vrated/sqrt(3)/Irated.
By multiplying [and dividing] by Vrated Z=vk%*Vrated^2/Srated where S=SQRT(3)*Vrated*Irated [the apparent rated power of the transformer].

Interesting stuff. Wish I had the brains to understand it.
 
  • #11
Baluncore said:
120V, 7.5kVA; I = 62.5A
R load = V / I = 1.92 ohm

I believe the 3% is the maximum percentage of voltage drop to be lost in the transformer secondary and circuit under full load conditions.
3% of 1.92 ohm = 0.0576 ohm transformer secondary resistance.
Short circuit current will be V / R = 120 / 0.0576 = 2083.3A

If you know the current rating of the panel, you do not need to know the line voltage.
Short circuit current will be 63A * 100% / 3% = 2100.A

Gotcha, thanks.
 

1. What is transformer impedance?

Transformer impedance refers to the resistance that a transformer presents to the flow of electrical current. It is a combination of the resistance, inductance, and capacitance of the transformer's windings and core.

2. How is transformer impedance calculated?

Transformer impedance can be calculated by dividing the voltage drop across the transformer by the current flowing through it. This is known as the voltage regulation method. Another method is to use the transformer's nameplate data, which specifies the percentage impedance or impedance voltage rating.

3. What is the significance of transformer impedance?

Transformer impedance is an important factor in determining the performance, efficiency, and voltage regulation of a transformer. A higher impedance can lead to greater voltage drops and reduced efficiency, while a lower impedance can cause higher currents and potential overheating.

4. How does transformer impedance affect power transfer?

The impedance of a transformer can have an impact on the amount of power that can be transferred through it. A higher impedance means a lower power transfer capability, while a lower impedance can handle higher power transfers. This is especially important in power transmission systems.

5. Can transformer impedance be changed?

Yes, transformer impedance can be changed by altering the winding configuration, using different materials in the transformer core, or adding external impedance devices. However, these changes must be carefully calculated and implemented to avoid damaging the transformer or affecting its performance.

Similar threads

  • Electrical Engineering
Replies
8
Views
1K
  • Electrical Engineering
Replies
8
Views
1K
Replies
21
Views
1K
  • Electrical Engineering
Replies
3
Views
2K
Replies
6
Views
2K
  • Electrical Engineering
Replies
15
Views
3K
  • Electrical Engineering
Replies
8
Views
2K
Replies
23
Views
3K
Replies
14
Views
2K
  • Electrical Engineering
Replies
5
Views
5K
Back
Top