Transformers and Drives - sizing and harmonics

AI Thread Summary
When using transformers with three-phase drives for induction motors, it is often suggested that transformers should be sized 40% larger than the drives to mitigate harmonics and other issues. However, this sizing can vary significantly based on the quality of the variable frequency drives (VFDs) and the filtering applied. The discussion highlights that there is no universally accepted standard or reliable recommendation for transformer sizing relative to drives, as each installation is unique. The 40% guideline may serve as a precautionary measure rather than a strict requirement. Ultimately, careful consideration of specific application needs and engineering analysis is essential for optimal transformer sizing.
elcraft
Messages
8
Reaction score
0
Hello,

Is it true that when using transformers and three-phase drives/VFDs for induction motors, the transformer's power needs to be much higher (e.g. +40%) than the drive's in order to avoid increased harmonics (or even other problems)?

If you know any official standard, paper or recommendation regarding the matter of sizing transformers vs drives, please share.

Thank you.
 
Engineering news on Phys.org
It is a very generalized question - there is a pretty big range in quality of VFD and the types / amount of filtering that can be applied. -- So the "needs" question could be "may need" - However, every installation or application is different.
Regardless 40% seems like a lot, but depending on who you got your info from - they may have learned that spec'ing a 40% larger transformer is insurance against problems, and has worked in the past without looking at the causes or doing real engineering.
 
So there is no paradigm with reliable recommendations or relevant discoveries?
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...