Understanding Negative Reactive Power in Inductive and Resistive Power Systems

Click For Summary

Discussion Overview

The discussion revolves around the implications of observing negative reactive power in a power system composed of purely inductive and resistive elements, particularly when no load is connected. Participants explore the behavior of transmission lines under these conditions, including the effects of line length and the inherent properties of inductance and capacitance.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant questions the meaning of negative reactive power in a system with no load, specifically in the context of a transmission line with resistance and inductive reactance.
  • Another participant notes that transmission lines inherently contain resistance and suggests that their behavior can vary based on their length relative to the wavelength, implying that they cannot be purely inductive or resistive.
  • A different participant explains that inductive reactances consume negative vars while capacitors provide negative reactive power, proposing that the negative reactive power might originate from line charging susceptance.
  • Another contribution clarifies that while real power cannot be negative, reactive current can be, and describes how an open circuit transmission line may appear capacitive under certain conditions, particularly when its length is less than a quarter wavelength.
  • This participant also provides specific examples of how the length of the line affects its apparent capacitance, particularly at 60 Hz, suggesting that a lossless, one eighth wavelength open circuit stub behaves like a perfect capacitor.

Areas of Agreement / Disagreement

Participants express differing views on the nature of transmission lines and the conditions under which negative reactive power can be observed. There is no consensus on the implications of negative reactive power or the role of capacitance in this context.

Contextual Notes

The discussion includes assumptions about the behavior of transmission lines and the definitions of reactive power, which may not be universally agreed upon. The relationship between line length and its reactive properties is also a point of contention.

Physicist3
Messages
103
Reaction score
0
What would it mean if in a power system with purely inductive and resistive elements (No Capacitance) if you were seeing a negative value of reactive power when there was no load connected? E.g. If the load was disconnected but the transmission line contained both resistance and inductive reactance?
 
Engineering news on Phys.org
Strange question. Of course a transmission line in the real world always contains resistance. However, transmission lines are funny things. How a transmission line appears from one end depends on how many multiples of 1/4 wave that it is long when it is open at the other end. The definition of a capacitor is 2 conductors that are separated by an insulator. Does a length of transmission line not meet this criteria? So, we cannot have a transmission line that does not contain capacitance by nature. Nor can we have a transmission line that does not contain inductance. By manipulating the length we can make the transmission line look any way we want.
 
Inductive reactances consume negative vars while capacitors consume positive vars.
One way to think about this is that inductors consume reactive power while capacitors provide negative reactive power.
I suppose the negative reactive power could be from the line charging susceptance?
(as an aside, that first sentence is the nature of power factor correction. If inductors consume reactive power, and a capacitor can supply it, the source doesn't have to)
 
Strictly speaking real power cannot be negative, but a reactive current can. The unit of reactive power is the VAR (volts * amps_reactive), which is not real power, since the current is in quadrature with the applied voltage.

If a line has an open circuit load, and shows a negative VAR then it is appearing as a capacitor to the generator. An open circuit transmission line will appear to have capacitance if its length is below one quarter of a wavelength. At exactly one eighth of a wavelength it will appear most like a lumped capacitor.

At 60 Hz the wavelength would be 5000 km. One quarter wavelength will be 1250 km. So between 0 and 1250 km an open line will appear to be capacitive, and so have a negative reactive current. A lossless, one eighth wavelength, (625 km @ 60 Hz), open circuit stub, will appear to be a perfect capacitor. The apparent capacitance of a one eighth wavelength open line is a function of the line's characteristic impedance and frequency.
 
Last edited:

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 7 ·
Replies
7
Views
3K
Replies
11
Views
3K
Replies
15
Views
2K
Replies
2
Views
3K
Replies
4
Views
3K
Replies
9
Views
2K
  • · Replies 9 ·
Replies
9
Views
6K
  • · Replies 11 ·
Replies
11
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K