Starting large motors causes voltage sag due to their high inrush current, which exceeds normal operational levels. This high current draw leads to increased resistance in the power source and wiring, resulting in a voltage drop at the motor terminals. When the motor stalls, all input power converts to heat instead of mechanical energy, risking overheating. The reactive components of the motor's inductive load complicate the relationship between voltage and current, as the effective resistance varies during startup. Understanding these dynamics is crucial for managing power quality in motor applications.
nafas
Messages
2
Reaction score
0
Hello,

In Power Quality, how does starting of large motor will cause voltage sag? How does voltage sag cause the motor to stall and overheat?

A friend mentioned that it has something to do with sustaining the source power, but I simply don't get it.

Thank you in advance.
 
Engineering news on Phys.org
Motors draw more current during start up (or if you stall it) than when rotating.
In normal operation, most of the input power gets converted to mechanical energy.
In the stopped/stalled condition all the input power gets converted to heat.

All real world power sources and connecting wiring have impedance (or resistance).
If you had a power connection with a zero impedance then there would be no voltage sag.
 
Hi,

If starting a motor consumed high current, then why doesn't the voltage increase too; since V=IR?

Thanks.
 
Motor is an inductive load, so it draws high initial current.
voltage or the potential is not absorbed, rather electrons are ( current).
you just need to supply more electrons to take your motor coil to operating level with the same potential.
the R in ohms law corresponds to resistive real value where as an inductive element possesses reactive component as well.
Hope this helps.
 
nafas said:
Hi,

If starting a motor consumed high current, then why doesn't the voltage increase too; since V=IR?

Thanks.

Due to the Conservation of Energy.

CS
 
nafas said:
Hi,

If starting a motor consumed high current, then why doesn't the voltage increase too; since V=IR?

Thanks.
It depends on you're viewpoint or which components of V=IR you are looking at.
The effective "R" of the motor is variable and very low at startup.
V is a constant defined by the construction of the source.

However, the wires connecting the voltage source (and the voltage source) have a value of R associated with them, separate from the motor.
The voltage drop due to R_source and R_wire does increase with current and must be subtracted from V_source.
This is seen as a "voltage sag" at the terminals of the motor.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...