Understanding Reactive Power Measurement with Wattmeter Configuration

Click For Summary
SUMMARY

The discussion focuses on the measurement of reactive power using a wattmeter configuration in a three-phase system. The wattmeter responds to the current that is in phase with the voltage, with the reference voltage being Y-B. As the power factor decreases, the current vector rotates closer to the voltage vector, allowing the wattmeter to measure reactive power (VAr). The formula for calculating power in this context is P = K1. VYB . IR . COS ø, with adjustments for three-phase systems leading to P = 3. VR . IR . Sin ø for reactive power measurement.

PREREQUISITES
  • Understanding of three-phase electrical systems
  • Knowledge of wattmeter operation and configuration
  • Familiarity with power factor concepts
  • Basic grasp of electrical power formulas and calculations
NEXT STEPS
  • Research the principles of reactive power and its significance in electrical systems
  • Learn about the operation and configuration of wattmeters in three-phase systems
  • Study power factor correction techniques and their applications
  • Explore advanced electrical measurement tools and their functionalities
USEFUL FOR

Electrical engineers, power system analysts, and technicians involved in the measurement and management of reactive power in three-phase electrical systems.

mnada
Messages
21
Reaction score
0
Does anybody understand how this wattmeter configuration is measuring reactive power?

One%20Wattmeter.jpg


Thanks
 
Engineering news on Phys.org
The wattmeter responds to current that is in phase with the voltage.
In your picture, The reference voltage is Y-B. (picture this vector as horizontal, the base of the delta
triangle). The current is from phase R. Its vector would be vertical or at 90 deg to the voltage vector.
If the power factor is 1.00, then the vector representing current would remain at 90 deg in relation to the voltage vector. As the power factor decreases however, the current vector rotates right or left (inductive or capacitive) and comes closer to being in phase with the voltage vector. As it does, the meter begins to respond. It will measure and display VAr. This is common and has practical application in the electrical power industry.
 
Thank you very much, your explanation is crystal clear, and helped me so.
Again, thank you.
 
That varmeter regarding to special connection is a wattmeter inherently, and we can write:

P = K1. VYB . IR . COS ø (output of measurement device)

VYB = √3.VR< 90˚ (In three phase balance system)

P = K1. √3.VR . IR . COS (ø - п/2) = K2. VR . IR . Sin ø

If K2 = 3 we can write:

P = 3. VR . IR . Sin ø = Q3PH

--------------------------------
Creative thinking is breezy, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Another excellent Explanation. Thanks
 
you need to multiply \sqrt{3} to the wattmeter reading to get 3-phase reactive power...
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
Replies
11
Views
2K
Replies
4
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
21
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
Replies
2
Views
3K
  • · Replies 1 ·
Replies
1
Views
6K
  • · Replies 8 ·
Replies
8
Views
11K