Use Norton’s Theorem to find the current in RL
  • Thread starter Thread starter agata78
    Current Theorem
Norton’s Theorem is applied to find the current in the load resistor (RL) using the equation for Norton resistance (RN). The calculations involve complex numbers, where the load resistor should not be included in the Norton equivalent circuit to accurately determine the current through it. The discussion highlights the importance of correctly simplifying complex expressions and using the complex conjugate to eliminate imaginary components from the denominator. Participants emphasize the need for careful arithmetic and suggest using online calculators for verification. Ultimately, the correct approach involves calculating the open circuit voltage at terminals AB and dividing it by the Norton resistance to find the current.
agata78
Use Norton’s Theorem to find the current in RL for the figure attached to this post?
Norton's Resistance Equation (The first part of Norton's Theorem)
RN = RL + ((R1 x R3) / (R2 + R3))
RN = 50 + (20+j5) x (40-j10) / (5+j10) + (40-j10)
RN = 50 + (800 - 200J + 200J -J250) / (5+j10 + 40-j10)
RN = 50 + (800 - j250 / 45)
RN = (50 x 45 + 800 - j250) / 45
RN = (2250 + 800 - j250) / 45
RN = 3050 - j250 / 45
RN = 5 (610 - 10j2) / 5 x 9
RN = 610 - 10j2 / 9
Am I correct so far? If I was given simple figures for the R1, R2 & R3 then this exercise would be very straight forward. But because of the complex figures for each Resistor, I need guidance so I know I am answering the question correctly. Many thanks!
We'd be able to help better if there actually were a figure attached.
Can you elaborate on the above? How did you arrive at that expression for the Norton Resistance?
What are you intending to include in the Norton equivalent circuit? It looks as though you're bundling the load resistance RL into the model. Isn't that the resistor for which you want to find the current? Once a component is absorbed into the equivalent circuit it "disappears" from view, and you can no longer say or determine anything about it...
Since RL is your load (attached at indicated points a and b), you don't want to include it in the Norton equivalent. You want to keep it separate so that later you can determine the current though it.
RN = R2 + ((R1 x R3) / (R1 + R3))
3. The Attempt at a Solution
RN = 5+J10 + (20+j5) x (40-j10) / (20+j5) + (40-j10)
RN = 5+J10 + (800 - 200J + 200J -(j250)/ (5+j10 + 40-j10)
RN = 5+J10 + (800 - j250) / 45)
Am i on the correct path? I am a bit confussed, it seems to be not difficult one but gives me a headache!
Yes, I was incorrect previously. Once the RL is removed, it can no longer be worked on in further calculations.
Yes, that looks better.
You've got the right starting formula, so that's a plus :smile: but your calculations seem to be getting mucked up. Yes, doing complex number arithmetic by hand can be tedious. But there's no thing for it but practice. All I can say is, work carefully and perhaps check each step using an online complex calculator as you practice :wink:
Right. Later you'll tack it back onto the Norton source and determine the current through it.
RN = 5+J10 + (((20+j5) x (40-j10)) / ( (20+j5) + (40-j10)))
Then this would be correct yes??!
Yes.
STEP 1: Calculate Norton Resistance (RN)
RN = 5+J10 + ((20+j5) x (40-j10)) / ((20+j5) + (40-j10))
RN = 5+J10 + ((800 - 200J + 200J -(j250)) / (20+j5 + 40 - j10)
RN = 5+J10 + ((800 - j250)) / (60 - j5)
RN = ((5 + j10) (60 - j5) + 800 - j250)) / (60 - j5)
RN = (300 - 25j + j600 - j250 + 800 - j250) / (60 - j5)
RN = (1100 + 575j - 100j2) / (60 - 5j)
STEP 2: Calculate Total Current (IT)
IT = Battery Voltage / Norton's Resistance
IT = 50 / ((1100 + 575j - 100j2) / (60 - 5j))
IT = 50 x ((60 - 5j) / (1100 + 575j - 100j2))
IT = (3000 - 250j) / (1100 + 575j - 100j2)
STEP 3: Calculate Norton Current (IN)
IN = IT x R3 / R2 + R3
Thanks Neil. Yeah, once again I can see where I went wrong. Hopefully, I am heading in the right direction now. Agata
Can someone please help me out? Was my last post correct? Much appreciated!
Your Rn is on the right track, but you didn't complete the simplification. The final result should be a single complex value of the form a + bj. That is, the result should be clear of complex values in the denominator.
The same can be said for the other steps, they seem to have been left incomplete.
Remember that in complex numbers, j2 = -1.
Thank you.
Why j2 = -1
I actually missed that. It makes it much easier to calculate.
ok, i tried to go with your advice and calculate the rest.
Rn = (240+115j) / ( 12-j )
It= (120-10j ) / ( 48+23j )
In= ( 960 -340j ) / (432 - 207 j )
the final figures looks better but still it doesn't give me ( a+bj ) answer.
Im worried that i made a mistake in calculations. Could you have a look i can write all the calculations if necessery.
thank you
Your Rn is okay so far, but you still need to clear the complex value from the denominator. It's a basic operation for complex numbers that you'll need to know how to do. It involves multiplying the numerator and denominator by the complex conjugate of the denominator (effectively multiplying the whole thing by one). The complex conjugate of a complex value is obtained by changing the sign of the imaginary part. So for a complex value a + bj, the complex conjugate is a - bj. Note that multiplying out (a + bj)(a - bj) results in ##a^2 + b^2##, a purely real value.
There is something amiss with your calculation of It. You assumed that It = supply voltage/Norton resistance, but that's not true. The Norton impedance (I call it an impedance rather than a resistance because it's a complex value not a pure real resistance) is obtained "looking into" the open terminals a-b. The power supply is "looking into" the other end of the network with a-b shorted. So you'd need to calculate that impedance that the voltage source "sees" first. After that you can obtain In by the method you've shown.
Ok.
Rn= ((240 + 115j) / (12-j)) x ( (12+j) / ( 12+j)) =( 2765 + 1620j ) / 145
Is my final answer for Rn is correct?
agata78 said:
Ok.
Yes, that's better. There are still some common factors to the numbers, so a tad more reduction is possible. You could write it as separate terms:
##\frac{553}{29} + \frac{324}{29}j## [Ohms]
Yes i can see what you ve done, you diveded everything by 5. Yes it looks better.
Thank you. Just need to sit down now and try to find the It.
The value (I) for the current used in Norton's Theorem is found by determining the open circuit voltage at the terminals AB and dividing it by the Norton resistance RN.
VAB = V1 x R2 / R1 + R2
I = VAB / RN
Am I heading in the correct direction?
Is my final answer for Rn is correct? Anybody?
Next part:
I = VAB / RN
Am i right? Would like move further but I am stuck with this one. Please help me!
The Norton resistance does not include the load resistor. You remove the load and "look into" the circuit from where the load was connected.
I decide to move further myself.
Vab= (116- 248j) / 29
i= 144500- 99560j
I need to use Thevenin theorem as well but it seems like all figures are the same as for Norton theorem.
Would be nice to know if its correct?
i= 144500- 99560j
Doesn't look right. Show a bit more of your work; What expression did you start with for Vab?
The value i for the current used in Norton's Theorem is found by determining the open circuit voltage at the terminals AB and dividing it by the Norton resistance r.
VAB =( V1 x R2) /( R1 + R2)
Vab= (50 x ( 40 -j10 )) / ( 20 + j5) + ( 40 - j10)
Vab= (200- j500) / (60-j5)
Vab= (( 200- j500 ) ( 60 +j5 )) / (60 -j5 ) ( 60 +j5)
Vab= (12000- 1000j - 30000j- j Xj x 2500 ) / ( 3600 + 300j -300j + 25 )
Vab= (12000-31000j + 2500 ) / 3625
Vab= (14500-31000j ) / 3625 everything divide per 125
Vab= (116 - 248j) / 29
Your expression for Vab is not correct. There's a voltage divider, but it involves resistors R1 and R3.
R2 is open-circuited at terminal a, so it passes no current and so produces no potential drop from the junction of R1 and R3.
I made mistake with my previous post:
Vab= V1 x R3 / R1 + R3
How can i deivide voltage?
Much better.
? Divide voltage ?
Is this correct?
And then
agata78 said:
And then
Vab= (200- j500) / (60-j5) <------- 50 x 40 is not 200
Vab= (12000- 1000j - 30000j- j Xj x 2500 ) / ( 3600 + 300j -300j + 25 ) Sign is incorrect
Check the sign on that term.
EDIT: Just noticed the "200" instead of "2000" above!
Yes i can see where i made mistake, it should be +1000j.
After changing it i have:
Vab=(14500-29000j+2500 ) / 3600+25
Vab= (14500-29000j ) / 3625
Vab= (116-232j) / 29
Vab= 4-8j= 4(1-2j)
and then
i= Vab/ r
i = ((4-8j )) / ( 553+232j/29)
i= (4-8j ) x (29/ (553+324j ))
i= ((4-8j ) x 29 ) (553 +324j )
i= (116-232j) / (553+324j)Do you agree with my later calculations?
Sorry, a just noticed a previous error in the calculation. My apologies. Please go back to my post #28 and see the edit (in green).
You really should look into finding an online complex number calculator that you can use to confirm your operations.
  • · Replies 28 ·
  • · Replies 20 ·
12K