Voltage Breakdown over two parallel rods

  • Thread starter Thread starter WalrusFuzz
  • Start date Start date
  • Tags Tags
    Parallel Voltage
Click For Summary

Discussion Overview

The discussion centers around the voltage breakdown between two parallel rods in the context of constructing a Jacob's Ladder. Participants explore the calculations and empirical measurements necessary to determine the optimal distance between the rods for effective arc generation, considering factors such as electrode shape and dielectric breakdown of air.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant suggests using Paschen's law to calculate the distance between the rods, noting that existing equations may not apply directly due to the shape of the electrodes.
  • Another participant provides a simplified formula for calculating electric field intensity and discusses the dielectric breakdown of air, stating it is approximately 3 MV/m.
  • A third participant corrects a previous claim about breakdown voltage, indicating that for a rod-rod gap, the breakdown voltage may be significantly less than for spherical electrodes and is influenced by the diameter of the rods.
  • This participant also mentions the effects of corona and space charge on the electric field and how these factors complicate the estimation of breakdown voltage, especially under AC conditions.
  • One participant inquires about the feasibility of placing rods 3 1/3 cm apart with a flyback transformer outputting ~20 kV, given the diameter of the rods.
  • Another participant suggests that a distance of 2 cm might be achievable and recommends making the ladder adjustable to optimize performance.

Areas of Agreement / Disagreement

Participants express differing views on the appropriate distance between the rods and the factors affecting breakdown voltage. There is no consensus on a definitive distance, and the discussion remains unresolved regarding the optimal setup for the Jacob's Ladder.

Contextual Notes

Participants highlight the complexity of calculating breakdown voltage due to dependencies on electrode shape, size, and the nature of the applied voltage (AC vs. DC). There are also mentions of empirical testing being necessary to refine the calculations.

WalrusFuzz
Messages
2
Reaction score
0
Hello everyone.

I'm building a Jacob's Ladder just for the hell of it, and am currently trying to figure out how far apart to place the two rods so that an arc will pass over them.

Paschen's law seems to vary depending on the shape of the electrodes; the equations that google brings up are probably for parallel plates, as I tried plugging in the numbers just for the hell of it, however not surprisingly, this didn't work because my resulting answer didn't make any sense.

Is there any way to calculate the distance between the two rods, or is the measurement entirely empirical? Wasting boards isn't exactly a preferred method.
 
Engineering news on Phys.org
It's not as complicated as you might think. Voltage is simply an electric field times a distance. Here's a simplified version that will work for the ladder. We can use this formula to calculate the field intensity E:

[tex]V = E \cdot x[/tex]

The not so simple version is this:

[tex]V = \oint{\vec(E) \cdot \vec{ds}}[/tex]

Don't worry about it though. For the ladder, we'll use the simple one (because the electric field is approximately constant between the rods).

Insulating materials have something called a dielectric breakdown. This is the point where the electric field E becomes so intense that the insulator starts to conduct. For air, it's 3MV/m. That's 3 million volts per meter.

So, here are two examples. Let's say you have a circuit that outputs a 30 kV pulse. You could find the necessary distance like this:

[tex]E = 3MV/m = 30kV / x[/tex]

Solve for x to get 10 cm.

Now, let's say you have a ladder with a gap of 1 cm. You need to know how much voltage you have to generate. Solve the following:

[tex]E = 3MV/m = v / 1cm[/tex]

The voltage required is 3kV.

The dielectric breakdown of air can vary. That's why the distance between is varied.
 
Last edited:
Hi,

You want to make sure that the gap at the bottom of the ladder will spark over so that the arc can start. Unfortunately, the above analysis has a math error that makes it off by a factor of 10. The DC breakdown voltage for a 1 cm sphere gap is actually closer to 30 kV (actually an electrical field of about 30 kV/cm) for spherical electrodes with a diameter that is much larger (>4X) than the gap length. The breakdown voltage for a rod-rod gap (the case you have) may be significantly less. If you are using smaller diameter electrodes, the peak electrical field at the electrode surface is intensified to V/r where V is the applied peak voltage (in volts versus ground) and r is the electrode radius (in cm). The air next to a 0.25 cm diameter electrode will begin to break down, forming corona at the surface of the electrodes, at a much lower applied voltage.

Once corona forms, free charges (called space charge) are injected into the gap, which then distorts the shape of the overall E-field within the gap. If these changes enhance the E-field within the gap, as it does especially with AC or RF voltages, the chances for a complete breakdown increase dramatically. A rod-rod gap will break over at a lower voltage when the applied voltage is 50/60 Hz AC, and at a considerably lower voltage for high frequency AC. However, estimating the actual breakdown voltage of the gap under these conditions can be quite difficult.

Since you'll be using relatively small diameter wires, the breakdown voltage at the bottom of your ladder will be lower than 30 kV since the electrical field will be enhanced by corona and space charges. And, since you'll probably be driving the ladder from a high voltage transformer powered from a sinusoidal AC source, the peak output voltage will be 1.414 times the RMS value. So, a 15,000 volt neon sign transformer (NST) will actually have a peak voltage of about 21,200 volts.

From a practical standpoint, a climbing arc setup (a "Jacob's Ladder") that has electrodes that are 1/4" in diameter or smaller can easily be powered from a 15 kV NST as long as it has an initial gap of 1 - 1.5 cm at the bottom.
 
So if I have a flyback that has ~20kV, is set in a circuit like "www.angelfire.com/80s/sixmhz/flyback.html"[/URL], and both rods are 1/8'', I should be able to place the rods about 3 1/3 cm apart?
 
Last edited by a moderator:
You might be able to do 2 cm. Make your ladder adjustable and lock it at the point where you get the best results. Because the circuit you referenced is low power, you may not be able to generate much heat in the arc, so you might not be able to separate the rods very much at the top...
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 10 ·
Replies
10
Views
3K
  • · Replies 1 ·
Replies
1
Views
1K
Replies
9
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 5 ·
Replies
5
Views
5K