The discussion revolves around the specifications and usage of relays labeled as "110V AC / 24V DC." Participants explore whether these relays can operate with both AC and DC voltages, the implications of using different voltage types on relay coils and contacts, and the potential risks involved in such applications.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Exploratory

Main Points Raised

  • Some participants question whether a relay designed for 110V AC and 24V DC can accept both types of voltage on the coil.
  • One participant suggests that relays designed for 24V AC should work for 24V DC, but notes that the ratings for AC and DC contacts differ significantly.
  • Concerns are raised about the stress on relay contacts when switching DC voltage compared to AC voltage, with some stating that DC switching is more demanding.
  • Several participants emphasize the importance of not mixing the ratings for the coil and contacts, warning that applying incorrect voltages could damage the relay.
  • There is a discussion about the inrush current characteristics of AC relay coils compared to DC relay coils, with some participants explaining that AC coils can draw significantly higher current initially.
  • One participant mentions that applying 24V DC to a 24V AC relay coil could lead to failure, while the reverse might not damage the coil but could prevent it from functioning properly.
  • Participants express uncertainty about the specific relay models and their specifications, with requests for links to product information and datasheets.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the interchangeability of AC and DC voltages for the relay coils. There are competing views on the implications of using different voltage types, and the discussion remains unresolved regarding the safety and functionality of such applications.

Contextual Notes

Limitations include the lack of specific relay model details and the need for further clarification on voltage ratings and operational characteristics. Some assumptions about relay behavior under different voltage conditions remain unverified.

Who May Find This Useful

Individuals interested in relay specifications, electrical engineering, and those working on projects involving relay circuits may find this discussion relevant.

Nikhil N
Messages
80
Reaction score
2
I have seen some relays mentioned as 110V AC/ 24V DC relay. Is this means, can I use both 24DC and 110V AC to the coil of relay?
 
Engineering news on Phys.org
Could you please give us a link for one such relay?

Regarding the coil, the AC and DC requirements are usually the same. So a relay designed for 24V AC should be OK for 24V DC.

However: regarding the poles the AC and DC ratings are different. It's less stressing to switch AC voltage, so the limit for AC is always higher.
To switch off DC voltage is the most stressing. I think that 110V AC/ 24V DC will be about this, but without further input I cannot be sure.
 
  • Like
Likes   Reactions: davenn
Rive said:
To switch off DC voltage is the most stressing. I think that 110V AC/ 24V DC will be about this, but without further input I cannot be sure.

and to expand of Rive's good response, there will usually be a current rating in amps along with the voltage for the relay contacts
 
Rive said:
Could you please give us a link for one such relay?
Capture.PNG

rl.PNG
 
That's not for a single relay, but for a family. Within the family the contact rating is '10 Amps contact rating at 24V DC or 230V AC', and the coil ratings are 'from 6volts to 110V DC and upto 230V AC with phenolic cover'.

This family consists of 10-20 different relays with various coil ratings, contact arrangement and chasing options.

Ps.: and yes, on the contacts for 10A these relays will bear 24V DC or 230V AC. The limit for DC is far lower than for AC.
 
Rive said:
That's not for a single relay, but for a family. Within the family the contact rating is '10 Amps contact rating at 24V DC or 230V AC', and the coil ratings are 'from 6volts to 110V DC and upto 230V AC with phenolic cover'.

This family consists of 10-20 different relays with various coil ratings, contact arrangement and chasing options.

Ps.: and yes, on the contacts for 10A these relays will bear 24V DC or 230V AC. The limit for DC is far lower than for AC.
I have to make chattering relay with above spec. I was using the below circuit for relay chattering. Now with the above relay if I connect 110V AC instead of 12V DC, it will work as same right?
relay.png
 
Nikhil N said:
I have to make chattering relay with above spec. I was using the below circuit for relay chattering. Now with the above relay if I connect 110V AC instead of 12V DC, it will work as same right?
Not likely. If that relay coil works at 12V then 110V AC will most likely break/burn it within seconds.

The contacts might survive, if that's any help :angel:
 
Rive said:
Not likely. If that relay coil works at 12V then 110V AC will most likely break/burn it within seconds.

The contacts might survive, if that's any help :angel:
Let me take the first relay spec, they have given the relay work either in 24V DC or 240V AC, so in the above circuit, if I am connecting 240V AC with the first relay, the chattering circuit should work right?
 
In a relay you have the coil and you have the contacts. These are different things.
For that relay the rating for the coil is 12V (or something in this caliber, since it works at this voltage).
For the contacts, the rating is 24V DC//240V AC (for 10A at most).

Don't mix the different ratings. If you try to apply 240V AC for the coil, then it'll be far out of it's rating.
 
  • Like
Likes   Reactions: davenn and jim hardy
  • #10
Rive said:
In a relay you have the coil and you have the contacts. These are different things.
For that relay the rating for the coil is 12V (or something in this caliber, since it works at this voltage).
For the contacts, the rating is 24V DC//240V AC (for 10A at most).

Don't mix the different ratings. If you try to apply 240V AC for the coil, then it'll be far out of it's rating.
Just see this product info. It has mentioed the coil DC volage range and AC voltage ranges. For this relay, will it work in both AC and DC volages?
http://oenindia.com/uploads/products/58_20160601032651.pdf
 
Last edited by a moderator:
  • #11
That product info sheet is also about a whole family.
The 24V AC version will ~ work as the 12V DC version, but for this family this kind of operation is out of spec. I do not recommend it. Buy the right tool for the job.
 
  • #12
Rive said:
Regarding the coil, the AC and DC requirements are usually the same. So a relay designed for 24V AC should be OK for 24V DC.

Not so at all.

A DC relay coil has enough resistance to limit the current through it to whatever the designer wanted it to be.

An AC relay coil has far less resistance, instead depends on its inductive reactance to limit coil current.
When first energized it draws several times its rated current and does so until the armature plunger moves into position reducing the air gap which raises inductance, pushing coil current back down to design value. Inrush might be 10X steady state current.
AC relays also have ,magnetic shading on the pole to prevent buzzing when closed , DC poles don't need it because there are no zero crossings.

Panasonic says about relay coils:
https://www3.panasonic.biz/ac/ae/control/relay/cautions_use/
For the AC type, there is an inrush current during the operation time (for the separated condition of the armature, the impedance is low and a current greater than rated current flows; for the adhered condition of the armature, the impedance is high and the rated value of current flows), and because of this, for the case of several relays being used in parallel connection, it is necessary to give consideration to power consumption.
Apply 24 volts DC to a 24 volt AC relay coil and you'll probably let the smoke out of it in just minutes.
Here's a snip from the datasheet of that relay
http://oenindia.com/uploads/products/58_20160601032651.pdf
relaycoildeltaR.jpg


Calculate the power in each with 24 volts DC applied , E2/R , to convince yourself .
 
Last edited by a moderator:
  • Like
Likes   Reactions: BvU
  • #13
jim hardy said:
Not so at all.

A DC relay coil has enough resistance to limit the current through it to whatever the designer wanted it to be.

An AC relay coil has far less resistance, instead depends on its inductive reactance to limit coil current.
When first energized it draws several times its rated current and does so until the armature plunger moves into position reducing the air gap which raises inductance, pushing coil current back down to design value. Inrush might be 10X steady state current.
AC relays also have ,magnetic shading on the pole to prevent buzzing when closed , DC poles don't need it because there are no zero crossings.

Panasonic says about relay coils:
https://www3.panasonic.biz/ac/ae/control/relay/cautions_use/

Apply 24 volts DC to a 24 volt AC relay coil and you'll probably let the smoke out of it in just minutes.
Here's a snip from the datasheet of that relay
http://oenindia.com/uploads/products/58_20160601032651.pdf
View attachment 114939
I have this relay with me. My doubt is whether can I use AC across coil and make a chattering circuit>?
IMG_20170323_153341.jpg
 
Last edited by a moderator:
  • #14
Nikhil N said:
My doubt is whether can I use AC across coil and make a chattering circuit>?

What is rated voltage and frequency of is coil?
A 24 VAC coil will be ruint by application of 24 VDC.
A 24 VDC coil will not be harmed by application of 24 VAC . But it might not pull in its armature to close the contacts, either. One experiment is worth a thousand expert opinions.
 
  • #15
jim hardy said:
Not so at all. .
Yep. It seems I messed up that part.

Nikhil N said:
I have this relay with me. My doubt is whether can I use AC across coil and make a chattering circuit>?
I won't try it above 24V AC without measuring the actual current through the coil.
And I won't try it above 30V AC at all.
 
  • #16
By this specification what it means? I have a Eagleman relay, their website showing these details only.
capture-png.114936.png

img_20170323_153341-jpg.114940.jpg
 
  • #17
Nikhil N said:
I have this relay with me. My doubt is whether can I use AC across coil and make a chattering circuit>?

not mains AC

Nikhil N said:
By this specification what it means? I have a Eagleman relay, their website showing these details only.

the pic of the one you have shown is a 12V coil

As Rive said many posts ago .....

Rive said:
That product info sheet is also about a whole family.
The 24V AC version will ~ work as the 12V DC version, but for this family this kind of operation is out of spec. I do not recommend it. Buy the right tool for the job.

so if you put anything significantly higher than 12V across it, it will failDave
 
  • #18
you have to work with what information you have, or find a better spec sheet.

I see no direct statement whether that coil is for AC or DC voltage.

If coil power is as they stated 1.5 to 1.2 VA , at 12 volts (as written on the side of the relay ) that would mean 0.125 to 0.100 amps

which at 12 volts would be 96 to 120 ohms of impedance. Is that impedance all resistance or is it the sum of resistance and reactance?
What does your ohm meter show for resistance of the coil ?
If it's much less than 96 ohms you'd better not apply very much DC to it.
 
  • #19
No it means the relay is operated by a 24V DC voltage to control a 110AC source.
 

Similar threads

Replies
8
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 10 ·
Replies
10
Views
3K
  • · Replies 7 ·
Replies
7
Views
2K
Replies
21
Views
3K
  • · Replies 48 ·
2
Replies
48
Views
9K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 9 ·
Replies
9
Views
9K
  • · Replies 4 ·
Replies
4
Views
5K