Why aren't there more heat pumps in process plants?

Click For Summary

Discussion Overview

The discussion revolves around the reasons for the limited adoption of heat pumps in process plants, particularly in relation to heating applications that typically use steam and cooling water. Participants explore various factors influencing the feasibility and efficiency of heat pumps in industrial settings.

Discussion Character

  • Debate/contested
  • Technical explanation
  • Exploratory

Main Points Raised

  • Some participants suggest that the capital expenditure (capex) for heat pumps may be too high, or that compressors are inefficient for the required temperature rises.
  • Others propose that the cost and complexity of installing additional heat exchangers could deter the use of heat pumps, as current systems may already be using multiple heat exchangers.
  • One participant mentions that while an ideal heat pump could have a coefficient of performance (COP) of 6.5, actual COPs for HVAC applications are often lower, around 4.5, particularly when considering high temperature differentials.
  • Concerns are raised about the cost of electricity compared to natural gas, with some participants questioning whether the energy savings from heat pumps would justify their installation costs.
  • Another point made is that the required temperature rise for heat pumps in process plants may be too high, leading to excessive costs and minimal value, while the volume of available heat recovery fluid may be insufficient.
  • Participants discuss the importance of payback periods, noting that if energy costs do not cover the purchase and maintenance of heat pumps within a reasonable timeframe, plants are unlikely to invest in them.
  • Some participants express uncertainty about the realistic COP values for heat pumps operating at specific temperature ranges, suggesting that the source of heat (e.g., ambient air vs. hot process streams) significantly impacts efficiency.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the reasons for the limited use of heat pumps in process plants. Multiple competing views are presented regarding the efficiency, cost, and practicality of heat pumps in industrial applications.

Contextual Notes

Participants highlight various assumptions regarding the efficiency of heat pumps, the cost of energy sources, and the specific conditions in process plants that may affect the feasibility of heat pump implementation. The discussion reflects a range of perspectives on these factors without resolving the underlying uncertainties.

rollingstein
Messages
644
Reaction score
16
In process plants many heating applications will use steam at approx 120 C whereas the standard cooling utility is cooling water at approx. 30 C.

In the dozens of plants I've seen I cannot recall having seen even one Heat Pump. Why is this so? Is the capex too high? Or are compressors too inefficient?

An ideal heat pump raising heat from say 60 C to 120 C ought to have a COP of 6.5. Isn't that a lot of saving on steam & cooling tower costs both? What gives? Is coal / gas so much cheaper than electricity needed for the compressors?
 
Engineering news on Phys.org
rollingstein said:
Or are compressors too inefficient?
Or, are heat exchangers too expensive to insert two heat exchangers between heat pump and process streams where a single heat exchanger between two process streams is currently doing a less efficient job?
 
Bystander said:
Or, are heat exchangers too expensive to insert two heat exchangers between heat pump and process streams where a single heat exchanger between two process streams is currently doing a less efficient job?

Most often its not a single HEX even now. There's two. One having steam vs process fluid to heat. And another having CW & process fluid to cool.

The situations where you transfer heat directly from one process fluid to another are perfectly fine. Those are not what I'm targeting. Those don't add directly to boiler load nor cooling tower load.
 
rollingstein said:
An ideal heat pump raising heat from say 60 C to 120 C ought to have a COP of 6.5. Isn't that a lot of saving on steam & cooling tower costs both? What gives? Is coal / gas so much cheaper than electricity needed for the compressors?
You are overestimating the COP. For HVAC applications, with much lower DTs, they don't get much above 4.5. And per unit of energy, electricity costs a lot more than natural gas.
 
russ_watters said:
You are overestimating the COP. For HVAC applications, with much lower DTs, they don't get much above 4.5. And per unit of energy, electricity costs a lot more than natural gas.

I only meant it as the ideal i.e. Carnot efficiency. Actual will be lower I agree.

A rough estimate. Say 1 kg steam gives you 2260 kJ/kg heat. Assume a COP of 4.5. The energy needed to drive the compressor is 0.13 kWhr. At industrial power of say $ 0.07 per unit that would be 0.009 $/kg-steam-equivalent. i.e. A little less than a cent.

Does anyone know what the industrial costing of low pressure steam is? It might indeed be cheaper than a cent I suspect.
 
Last edited:
This may be of interest to you:
Industrial Heat Pumps for Steam and Fuel Savings
http://www.google.ca/url?sa=t&rct=j&q=&esrc=s&frm=1&source=web&cd=1&cad=rja&uact=8&ved=0CDkQFjAA&url=http://www1.eere.energy.gov/industry/bestpractices/pdfs/heatpump.pdf&ei=VzbZVPnWM8L2UIrhgIAI&usg=AFQjCNGV1W3JrVGuWbbZwbbW2A_4yDActg&sig2=EG_OoqOzk80GouBqfRwRYg&bvm=bv.85464276,d.d24


Typically it is either:
The temperature rise needed is too high, resulting in excessive costs and minimal value
The volume of available fluid from which to recover heat is too low

Principally, the payback period is too long. If the energy costs don't pay for the purchase, installation, and maintenance of the pump within a range of 1-5 years, a plant generally won't look at it. Most of the time it's about balancing available capital and projects with long payback periods will generally be passed up, even if they technically create more efficient process.
 
rollingstein said:
I only meant it as the ideal i.e. Carnot efficiency. Actual will be lower I agree.

A rough estimate. Say 1 kg steam gives you 2260 kJ/kg heat. Assume a COP of 4.5. The energy needed to drive the compressor is 0.13 kWhr. At industrial power of say $ 0.07 per unit that would be 0.009 $/kg-steam-equivalent. i.e. A little less than a cent.

Does anyone know what the industrial costing of low pressure steam is? It might indeed be cheaper than a cent I suspect.
About a cent and a half. But again, with that large of a delta-T, you won't even get anywhere close to 4.5 COP. Also, 7 cents a kWh is a little on the low side.
 
russ_watters said:
About a cent and a half. But again, with that large of a delta-T, you won't even get anywhere close to 4.5 COP. Also, 7 cents a kWh is a little on the low side.

I used EIA aggregate data for electric prices in USA in Nov. 2014. Industrial average is given at 6.67 cents per kWhr. For some states like Washington, Nevada, Iowa or Utah industrial consumers are paying less than 5 cents per kWhr. Is there a hidden factor I'm missing?

http://www.eia.gov/electricity/monthly/epm_table_grapher.cfm?t=epmt_5_6_a
 
russ_watters said:
But again, with that large of a delta-T, you won't even get anywhere close to 4.5 COP.

For a 60C-120C heat-pump I get Carnot Efficiency as 6.55. At 70% actual effeciency that's mean an effective COP of 4.5.

How bad is the actual difference from Carnot? Any estimates?

If not 4.5 what's a more realistic COP to use?
 
  • #10
Travis_King said:
ypically it is either:
The temperature rise needed is too high, resulting in excessive costs and minimal value
The volume of available fluid from which to recover heat is too low

Thanks for the link! The first point sure makes sense.

But not so sure about the second point: If you look at the cooling water needs of most chemical plants there's a huge amount of heat being extracted out ,say, in the 50 C to 110 C range. Lots of reactions etc. are run in that range & many being exothermic need cooling. Often products need cooling before they can be loaded into tank cars etc.

So I'm not sure why low volumes are a problem. Perhaps I misunderstand your explanation.

Travis_King said:
Principally, the payback period is too long. If the energy costs don't pay for the purchase, installation, and maintenance of the pump within a range of 1-5 years, a plant generally won't look at it. Most of the time it's about balancing available capital and projects with long payback periods will generally be passed up, even if they technically create more efficient process.

Agree that payback periods are crucial. Is there a good way to estimate the cost of (say) a kWhr of heat pump capacity. Anecdotally do you have any rough estimates?
 
  • #11
rollingstein said:
For a 60C-120C heat-pump I get Carnot Efficiency as 6.55. At 70% actual effeciency that's mean an effective COP of 4.5.

How bad is the actual difference from Carnot? Any estimates?

If not 4.5 what's a more realistic COP to use?
The wiki on heat pumps has several tables. They don't go as high a temperature as you are talking (because nobody makes them), but you can extrapolate from the difference between real and carnot efficiency for lower temperatures.

One thing that's also important here is you didn't say what the source of the heat would be. Ambient air? Groundwater? For example, a residential air source heat pump with a temperature difference between source and sink of 30 C has about a 4.5 COP. Given that you haven't said what the source is and the number you used was 60C, I'm not sure you are understanding the COP properly. The low temp is the temp of the heat source, which must be some sort of ambient heat, either from air or groundwater usually, but it also could be waste heat (room exhaust, at 20C). So the source is more likely to be 5C than 60C. That would give a Carnot COP of 3.4.
 
Last edited:
  • #12
russ_watters said:
One thing that's also important here is you didn't say what the source of the heat would be. Ambient air? Groundwater?

Oh sorry, I should have clarified. No neither ambient nor groundwater but a "richer" source in the form of hot process streams.

In most process plants there are streams that need cooling that are fairly hot (say 90 C) & are currently dumping all their heat to cooling towers.

Ergo a ready heat source at T much higher than ambient or groundwater is available. Besides heat transfer coefficients will be high relative to GW or air.
 
  • #13
rollingstein said:
Oh sorry, I should have clarified. No neither ambient nor groundwater but a "richer" source in the form of hot process streams.

In most process plants there are streams that need cooling that are fairly hot (say 90 C) & are currently dumping all their heat to cooling towers.
What kind of "process plants" are you referring to?

If they have waste streams that are that hot, there may be other ways of recovering the heat that are cheaper without the refrigerant circuit; using a glycol/water solution or even a direct heat exchanger. It would depend on the particulars of the processes.
 
  • #14
russ_watters said:
What kind of "process plants" are you referring to?

If they have waste streams that are that hot, there may be other ways of recovering the heat that are cheaper without the refrigerant circuit; using a glycol/water solution or even a direct heat exchanger. It would depend on the particulars of the processes.

The one's I had in mind were all pharma intermediates, fine chemicals, specialties etc. e.g. producing resins, detergents, or intermediates like pentaerythritol, BHT, BHA styrene oxide, etc. i.e. Much smaller than a refinery but not tiny. Reactions & distillation being the two very common unit operations.

Which other ways do you have in mind? If I have a large liquid stream at say 90 C that needs cooling to 60 C but OTOH I've no process needing heat at such low temperatures how can you use a direct HEX? Currently dumping the low quality heat to a cooling tower is the only viable option. And that's what most sites seem to do.
 
  • #15
russ_watters said:
Given that you haven't said what the source is and the number you used was 60C, I'm not sure you are understanding the COP properly. The low temp is the temp of the heat source, which must be some sort of ambient heat, either from air or groundwater usually, but it also could be waste heat (room exhaust, at 20C). So the source is more likely to be 5C than 60C.

Nope. I meant pumping heat up from a hot fluid at around 90 C that needs to be cooled down to a fluid at say 100 C that needs to be heated up. Hence the 60-to-120 duty accounting for deltaT across heat exchangers etc.
 

Similar threads

  • · Replies 15 ·
Replies
15
Views
2K
Replies
9
Views
2K
  • · Replies 80 ·
3
Replies
80
Views
12K
Replies
14
Views
10K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 152 ·
6
Replies
152
Views
11K
Replies
17
Views
7K
Replies
10
Views
13K
  • · Replies 89 ·
3
Replies
89
Views
38K