Assumed violation of physics - Heat vs. Work

  1. Jan 26, 2013 #1

    Low-Q

    User Avatar
    Gold Member

    I have had a discussion with some friends who is interesting in all sort of things of physics and experiments. We are interesting in energy research particulary, and looks for alternative energy sources that is "free of use", or at some degree an independent energy source.

    We have been discussing heat pumps, and heat engines. And I know it has been discussed here as well. My friends and I do know that energy MUST be conserved. There is NO such thing as over unity. But still we do discuss the potential in a heat engine that is assisted by a heat pump.
    What I have been told at physicsforums.com is that a heat pump with high COP, does work very bad as a heat engine - I'm told here that there is a reversed relationship between the COP number as a heat pump, and efficiency as a heat engine. So we can agree that using two identical heat pumps, where one of them is used as a heat engine, powered by the other heat pump, is not going to work - not even without loss.

    However, we have been discussing back and forth wether it is possible to use an efficient heat engine to power the pump of a high COP heat pump.
    I have compared this particular experiment with a water turbine that is harvesting the potential of the hight of a dam. The dam is continiously supplied with water from the river. The river itself is inefficient as power supply, so the dam is made to increase the level of water.
    I think that the heat pump is doing something similar with the heat in the air. The pump has a cold and warm side when it is running, that is compared with the hight of a dam - one high and one low level which contains the potential energy in the water.

    If now the heat engine is compared with the turbine in the hydro power plant, it harvest the potential difference, NOT between the cold and hot side of the heat pump, but between the hot OR cold side, and the surrounding air. The heat pump either supply the heat engine with high temperature which is doing work as it cools down to surrounding temperature, OR the heat pump takes away heat from the heat engine, and do work as the temperature rise up to surrounding temperature.

    I would like to quote one of the people I'm discussing this with. He had (to me) a good point:

    "Why wouldn't this work?

    A heat engine converts heat into work, Right?

    If, just for the sake of argument, or a place to start as an example, you have a very efficient heat engine that can convert 70% of the heat delivered to it into useful work output with 30% waste heat and a Heat Pump with a COP of 3 or higher.

    The heat pump can remove 3 times more waste heat from the engine than the energy required to run the heat pump. (It can remove the 30% waste heat with just 10% of the heat engines 70% work output).

    That leaves 60% work output from the heat engine to be used for other purposes such as generating electricity.

    If the heat engine is running directly from ambient heat, then the heat pump is not needed as a source of heat/energy to run the engine. All it has to do is remove the waste heat not converted into work by the engine.

    If you had an engine only 40% efficient leaving 60% waste heat to be removed, you would still only need 20% of the work output to remove the waste heat and have 20% left over for the production of electricity.

    Heat pumps can have a COP of much grater than 3. Some are as high as 10.

    And please say something other than it violates the second law of thermodynamics."

    Do the sceptics to free energy ASSUME this particular setup will not work, because it fights all common sense of what is understood as violation of physics?

    Vidar
     
  2. jcsd
  3. Jan 26, 2013 #2

    mfb

    User Avatar
    2016 Award

    Staff: Mentor

    An efficient heat engine needs a large temperature difference. An efficient heat pump needs a small temperature difference. The actual pump design does not matter, the efficiency is limited by those temperature differences. You can extract work if you have both at the same time (with at least 3 reservoirs), but this will just give a heat engine, cooling a very hot reservoir and/or heating a very cold one.

    Apart from an analysis of your specific setup (see above how this can be done), you can prove (using very basic assumptions about physics) that no setup of heat engines / pumps can ever do what you want: It would reduce entropy, and that cannot be reduced in closed systems.
     
  4. Jan 26, 2013 #3

    sophiecentaur

    User Avatar
    Science Advisor
    Gold Member

    You must be adding the wrong quantities together in order to arrive at your conclusion.
    You seem to want to improve the efficiency of a heat engine by increasing the temperature difference over which it operates. You want to achieve this by pumping heat to a higher temperature heat reservoir. But the mechanical energy work needed to do this heat pumping could be no less than the extra mechanical work got out of your 'more efficient' heat engine - operating over a bigger temperature difference.

    Maximum thermodynamic efficiency (work out for a given amount of thermal energy transferred) all depends upon temperature difference. And the temperature difference from a heat pump imposes a minimum amount of work in. You can't just pick arbitrary percentage figures for efficiencies out of the air and then put those figures into a sum to prove anything at all.
     
  5. Jan 26, 2013 #4
    Let us start by replacing your dream figures with some realistic ones.

    All heat engines work by taking in heat at a high temperature T1 and rejecting some of it at a lower temperature T2

    The maximum possible efficiency is (T1-T2)/T1 x100 in %
    Where temperature, T is measured in degrees Kelvin.
    You would be very lucky to find a real engine that can achieve half this.

    So let us say your river water is at 15°C and you heat pump manages to raise some of it to 60°C, the standard temperature in a domestic hot water cylinder. Then you use this to run a heat engine.


    Max Efficiency of heat engine = (333-288)/333 x100 = 13.5%

    So a real heat engine might manage half this or nearly 7% efficiency.

    What effect do these figures have on your ideas?
     
    Last edited: Jan 26, 2013
  6. Jan 26, 2013 #5

    Dale

    Staff: Mentor

    The maximum efficiency of a heat engine and the maximum COP of a heat pump are strongly dependent on the temperature of the cold and hot reservoirs. Assuming that the cold reservoir is a typical 300 K temperature, then for 70% efficiency the minimum hot reservoir temperature would be 1000 K. An ideal heat pump with a COP of 3 could only raise the temperature from 300 K to 450 K. The maximum COP for a cold reservoir of 300 K and a hot reservoir of 100 K is 1.43 which, not surprisingly, is 100%/70%.
     
  7. Jan 27, 2013 #6

    Low-Q

    User Avatar
    Gold Member

    How do these figures change with a COP 10 heat pump?

    Or does the COP strongly depend on the load - this case the heat engine? Edit I think you answered this in your previous post...

    Is it any theoretical posibility to make this work if we have no real limits in COP? The Carnot efficiency is approx 70%. Using this efficiency, and use a neccesary high COP of the heat pump.

    PS! Either the hot or cold reservoir of the heat pump is independent as it is not in direct contact with the heat engine. If the hot reservoir is in contact with the heat engine, the cold reservoir is independent and only in contact with surrounding air.
    MVR heat pumps can achieve COP up to 80 with outputs up tp 100MW...ofcourse this is industrial heat pumps where several compressors are connecten in series. These can get heat from temperatures below -40 degrees C using vacuum in the low pressure reservoir.

    Vidar
     
    Last edited: Jan 27, 2013
  8. Jan 27, 2013 #7
    Thank you for wasting my time.

    Having discussed real world heat engines I was going on to discuss real world heat pumps next.
     
  9. Jan 27, 2013 #8

    Dale

    Staff: Mentor

    An ideal COP 10 heat pump with a cold reservoir at 300 K could only raise heat to a hot reservoir of 333 K. An ideal heat engine with those same reservoirs could have a maximum effeciency of 10%.

    The point is that there are 4 quantites of interest: the heat pump COP, the heat engine efficiency, the hot reservoir temperature, the cold reservoir temperature. Once you set any two of those then the other two are fixed. They are fixed in such a way that, all things being ideal, you can raise the same amount of heat you lowered.

    Not sure what you mean here. All heat engines and all heat pumps have a hot reservoir and a cold reservoir, that is part of the definition of heat engines and pumps. If you are not connecting the engine and the pump to the same pair of reservoirs then I am not sure what you are doing and why.
     
  10. Jan 27, 2013 #9

    Dale

    Staff: Mentor

    Upon re reading your question I think I understand the arrangement better now. Let's say that we have a hot reservoir at 1000 K and a cold reservoir at 300 K. Instead of connecting both the heat pump and the heat engine to both reservoirs you want to connect the heat engine to the hot, the heat pump to the cold, and both to an artificial shared reservoir which would be colder than the cold reservoir. Could the gain in efficiency for the heat engine compensate the work required for the pump.

    Is that the arrangement?
     
  11. Jan 27, 2013 #10

    sophiecentaur

    User Avatar
    Science Advisor
    Gold Member

    Send him the bill - @ £200 per hour, as a consutant. :wink:
     
  12. Jan 27, 2013 #11

    Low-Q

    User Avatar
    Gold Member

    I will make a drawing of this. I will post it later. However you are (about) on the right track but not fully there yet I guess.

    Vidar.
     
  13. Jan 27, 2013 #12

    Low-Q

    User Avatar
    Gold Member

    Sorry for wasting your time. Your earlier input is welcome. Send me a bill if I ruined your day:-D

    Vidar
     
  14. Jan 27, 2013 #13
    If our teachers at school would send us bills for wasting their days back then I think we would be out of money by now. :D
     
  15. Jan 27, 2013 #14

    Dale

    Staff: Mentor

    Low-Q, I know you said this wasn't quite the arrangement you had in mind, but I had some time now and may not later (depending on weather). So I went ahead and analyzed this scenario. In the below W is work, Q is heat, T is temperature, a subscript E is for the heat engine, a subscript P is for the heat pump, a subscript C is for the cold reservoir, and a subscript H is for the hot reservoir.

    The efficiency of an ideal heat engine is:
    [tex]\frac{W_E}{Q_{HE}}=1-\frac{T_{CE}}{T_{HE}}[/tex]

    The COP of an ideal (refrigeration) heat pump is:
    [tex]\frac{Q_{CP}}{W_P}=\frac{T_{CP}}{T_{HP}-T_{CP}}[/tex]

    Since the shared reservoir is the cold reservoir for both the pump and the engine we have [itex]T_{CE}=T_{CP}[/itex]. In order to keep the shared reservoir cold we have [itex]Q_{CP}=Q_{HE}-W_E[/itex]. Plugging all these in and simplifying we have that the overall efficiency is:
    [tex]\frac{W_E-W_P}{Q_{HE}}=1-\frac{T_{HP}}{T_{HE}}[/tex]

    In other words, the overall ideal efficiency is the same as if you just skip the shared reservoir and the ideal heat pump and directly connect the ideal heat engine between the two non-shared reservoirs.

    You can show me your envisioned arrangement and I can re-do my analysis accordingly, but I expect that the result will remain the same.
     
  16. Jan 27, 2013 #15

    Low-Q

    User Avatar
    Gold Member

    Well, I was allowed to borrow an illustration from one of the members in another forum I am in.
    Here is the illustration.:
    image.jpg

    For the record, we are NOT discussing over unity. Just very curious hobbyists.

    BTW, your equation for heat engine equation seems to allow 100% efficiency. I believed the absolute maximum theoretical efficiency was about 70%....

    Vidar
     
    Last edited: Jan 27, 2013
  17. Jan 27, 2013 #16

    Dale

    Staff: Mentor

    In that image the heat pump and the heat engine share both the same hot reservoir and the same cold reservoir. Everything in my posts 5 and 8 applies, specifically the maximum possible COP is 1/0.7=1.43 so you would have to use all of the work from the ideal heat engine to power the ideal heat pump.

    How do you figure that?
     
  18. Jan 27, 2013 #17

    Low-Q

    User Avatar
    Gold Member

    With independent I ment that the hot side of the pump and engine is both in free air. Their physical surfaces/heat sinks do not neccessarily have the same temperature even if the air around them have constant temperature. Only the cold sides have the same temperature.


    Regarding the equation: If TCE is 0 K you have 1 and remove zero - 100% efficiency. If TCE is 20K and THE is 273K, the efficiency is 93%.

    Vidar
     
  19. Jan 27, 2013 #18

    mfb

    User Avatar
    2016 Award

    Staff: Mentor

    The heat pump will have at least the same temperature difference then, and therefore it cannot be "better" than the heat engine - for ideal engines and the same air temperature, they just cancel.


    That is correct, a cold reservoir at absolute zero would allow 100% efficiency - as upper limit on the efficiency of real machines. An upper limit of 100% is trivial, but not problematic.
     
  20. Jan 27, 2013 #19

    Dale

    Staff: Mentor

    Yes, so free air is the hot reservoir for both. All of my comments in 5 and 8 apply. You have to use all of the work from the ideal heat engine to run the ideal heat pump.
     
  21. Jan 27, 2013 #20

    Low-Q

    User Avatar
    Gold Member

    I thought that COP was describing the relationship between input work and output heat of a heat pump. Say you have a heat pump with COP of 10, is it so that this heat pump suddenly drop its COP to 1.43 as soon as it is connected to a heat engine with 70% efficiency? And, does it increase COP to 20 as soon as it is connected to a heat engine with 5% efficiency?

    Vidar
     