Why Can We Experience An Electric Shock From Neutral

Click For Summary

Discussion Overview

The discussion centers around the phenomenon of experiencing an electric shock from a neutral conductor in electrical systems, particularly in residential settings. Participants explore the implications of alternating current (AC) versus direct current (DC), grounding practices, and the potential for misidentifying conductors based on color coding.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Conceptual clarification

Main Points Raised

  • Some participants assert that the neutral conductor is typically at 0V relative to ground, but this can vary based on the system and conditions, leading to potential shocks.
  • It is noted that voltage is relative, and the neutral can carry a voltage relative to the live conductor, which can lead to confusion about safety.
  • One participant suggests that shocks from the neutral may occur due to a fault in the electrical system, such as a break in the neutral conductor, which could elevate its voltage relative to ground.
  • Concerns are raised about identifying neutral wires by color, as some installations may use white wires for live connections, particularly in switch configurations.
  • Participants discuss the differences between AC and DC systems, with one arguing that the risk of shock depends more on voltage and skin resistance than the type of current.
  • There is mention of the variability in color codes for electrical wiring across different countries, which could lead to misunderstandings in international discussions.

Areas of Agreement / Disagreement

Participants express differing views on the safety of neutral conductors and the conditions under which shocks may occur. There is no consensus on the implications of AC versus DC systems, and the discussion remains unresolved regarding the specifics of electrical safety and identification of conductors.

Contextual Notes

Limitations include assumptions about specific electrical standards in different countries, the potential for misidentification of wires, and the variability in grounding practices that may affect the discussion.

Who May Find This Useful

This discussion may be of interest to individuals studying electrical engineering, electricians, or anyone involved in residential electrical work who seeks to understand the nuances of electrical safety and conductor identification.

Nowalcott
Messages
2
Reaction score
0
I have always been under the impression that the "Live" conductor was the most dangerous conductor.

The Live carries 120V (US) 240V (UK) and the Neutral carries 0V, but yet it is still possible to get an electric shock from a Neutral :confused:

Why is this possible?

Is it because it is Alternating Current and the direction of the current changes?

If so, would it be fair to say that in an DC circuit, it won't be possible to get shock from a Negative conductor?

Thanks in advance

Nathan
 
Engineering news on Phys.org
Voltage is always relative to something - not an absolute quantity.

The "Neutral is 0V" is only 0V relative to ground. Relative to the Hot, it's 120V/240V.

The reason the "to ground" matters is that you can shield the appliance or device by grounding it explicitly and then as a human resistor, anything you are likely to touch that is connected to the Neutral will result in zero current flowing through you. Then it's only a matter of worrying about the hot wire, and that current preferentially flow to any chassis grounded metal rather than through you.
 
You talking about static shock? It can happen because YOU are charged up!:smile:
 
jsgruszynski said:
Voltage is always relative to something - not an absolute quantity.

The "Neutral is 0V" is only 0V relative to ground. Relative to the Hot, it's 120V/240V.

The reason the "to ground" matters is that you can shield the appliance or device by grounding it explicitly and then as a human resistor, anything you are likely to touch that is connected to the Neutral will result in zero current flowing through you. Then it's only a matter of worrying about the hot wire, and that current preferentially flow to any chassis grounded metal rather than through you.

Thanks a lot
 
Nowalcott said:
I have always been under the impression that the "Live" conductor was the most dangerous conductor.

The Live carries 120V (US) 240V (UK) and the Neutral carries 0V, but yet it is still possible to get an electric shock from a Neutral :confused:

Why is this possible? ...
Assumptions:
1. US standard residential electrical system. Also true in Canada. I don't know about Brits.

2. By getting shocked from the neutral, you mean that you are touching the neutral conductor and some other grounded conductive surface (like bare feet on a concrete floor) and get somewhere between a sharp tingle and internal bright flashing lights, followed by "EEEEYWOOOOO"

3. You are not discussing swimming pools and voltage drop on the utility neutral from the subatation.

The Neutral is susposed to be bonded to the grounding conductor only in one place - at the first disconnect after the utility transformer. Generally this is at the main panel. The grounding conductor is susposed to have a medium decent connection to earth. The only difference of potential between the grounding conductor (also earth) and the neutral is the voltage drop along the neutral conductor of a loaded circuit. As most this would be about 3V. And it is really hard to feel 3 volts (but is is possible to get a bit of a tingle)

So, if you are getting shocked by the neutral then something in the electrical system is broken. And the broken part is likely in the neutral conductor - between the place you are touching and the main panel. With a break in the neutral, the neutral will rise to 120V with respect to earth.

Another possibility: How are you identifying the neutral? By it being colored white? If so, some parts of normal, correct, residential installations will have white wires that are energized.

Now that we got by that, may I gently suggest:
Don't be touching electrical wires until after you have verified (with a known good meter) the circuit is dead. Sweaty fingers, sweaty feet, damp shoes, concrete floor, indiscriminate touching of 120V residential electrical has a bit better than even money chance of not killing you. Although when you tie into an energized wire, you may feel that it is killing you.

ice
 
Nowalcott said:
I...If so, would it be fair to say that in an DC circuit, it won't be possible to get shock from a Negative conductor?

It really doesn't matter much AC or DC. It depends mostly on voltage and skin resistance. As for DC, grounded or ungrounded system?

An clean un-grounded DC system won't have a potential to earth. But all it takes a bit of dirt on one side of the source (battery) and the other side can get elevated above Earth to source potential.

I get leery of sticking my bare hands into ungrounded DC systems above 48V. 125DCV passing hand to hand hurts - even with dry hands.

ice
 
I completely agree with iceworm... especially if you are identifying the neutral wire by insulation colour.
In domestic lighting circuits especially you may find that the neutral colour wire is a live wire used to connect switches.
 
We must also remember that this is an international forum and that colour codes vary from country to country. Before commenting on specific colour codes to a given OP's question, we should make sure we know where they reside so as not to give misleading info :)

USA -- Black = hot; White = neutral; what do you use for Earth ?
UK -- I have no idea
NZ and Australia -- Brown = hot; Blue = neutral and green/yellow striped = earth

Dave
 

Similar threads

Replies
19
Views
3K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 26 ·
Replies
26
Views
5K
Replies
47
Views
11K
  • · Replies 78 ·
3
Replies
78
Views
18K
  • · Replies 4 ·
Replies
4
Views
16K
  • · Replies 5 ·
Replies
5
Views
11K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 16 ·
Replies
16
Views
5K