The discussion revolves around the importance of correct polarity in alternating current (AC) connections, particularly in wall outlets. Participants explore the implications of connecting live and neutral wires correctly, the differences in plug designs between regions, and the potential safety concerns associated with incorrect polarity.

Discussion Character

  • Exploratory
  • Debate/contested
  • Technical explanation

Main Points Raised

  • Some participants question why correct polarity matters in AC systems since the current changes direction frequently (50 times per second).
  • Others note that certain appliances may behave differently depending on how they are plugged in, citing examples of devices that can cause electric shocks if connected with the wrong polarity.
  • A participant mentions that in the US, the neutral wire is connected to ground, suggesting this may have implications for why polarity is important.
  • There is a discussion about the design of AC to DC converters and whether the designation of live and neutral sides is merely conventional or has practical implications.
  • Concerns are raised about the inability to guarantee which side is hot in non-polarized systems, particularly in Europe, where plugs can be inserted in either orientation.
  • One participant suggests that the placement of fuses in circuits should prioritize safety, but questions how this can be ensured in AC systems.
  • Another participant discusses the heat generated in fuses and how it relates to AC current, emphasizing that current flow is a critical factor regardless of polarity.

Areas of Agreement / Disagreement

Participants express a range of views on the importance of polarity in AC systems, with some emphasizing safety concerns and others questioning the necessity of strict adherence to polarity given the nature of AC. There is no consensus on whether the correct polarity is essential in all cases, and the discussion remains unresolved.

Contextual Notes

Participants reference various wiring conventions and safety practices that differ across regions, highlighting the complexity of the topic. The discussion includes assumptions about user behavior and appliance design that may not be universally applicable.

  • #61
russ_watters said:
I learned this while changing a lightbulb my dad wired in my parents' basement...

@HomeExperiement something perhaps less evident is consistency in the circuit itself - not just the devices plugged into it - is part of the safety equation. If you aren't paying attention to polarity, you may wire a circuit that works fine, but due to the switch being on the neutral side, it's always live even when switched off.
I found an even worse wiring situation in an old pub in South East London, UK, where my friend, the landlady, had accidentally hit a light with a brush and broken the lamp socket. A fuse blew and I at first assumed the power was off. Being an electronics technician, I had learned to test things rather than assume and this may have saved my life, or at least a severe shock. Finding the lamp socket still live, I rechecked the fuses in the pub's cellar and found a blown fuse in a neutral line on a separate switchboard to the live fuses, which of course left the circuit live and unsafe to work on without extra safety measures. Removing both fuses, I replaced the lamp socket and then rewired and replaced the fuses.

The ancient switchgear in the pub cellar reminded me that electrical practices in the the pre-WW2 era were different to the more modern (early 1980s) times and reinforced the concept of testing before attempting any sort of electrical work.

In the same pub, the landlord had replaced a broken plug on a pie warmer, but it wasn't warming so he asked me to check it. A slight tingling shock (I was insulated from ground) suggested that I should check the plug wiring. Sure enough, the landlord was red/green colour blind and had interchanged the live and Earth wires (the old colour scheme, red-live, black-neutral, green-earth).
 
  • Like
  • Wow
Likes   Reactions: Asymptotic, berkeman, anorlunda and 2 others
Engineering news on Phys.org
  • #62
darth boozer said:
I found an even worse wiring situation in an old pub in South East London, UK, where my friend, the landlady, had accidentally hit a light with a brush and broken the lamp socket. A fuse blew and I at first assumed the power was off. Being an electronics technician, I had learned to test things rather than assume and this may have saved my life, or at least a severe shock. Finding the lamp socket still live, I rechecked the fuses in the pub's cellar and found a blown fuse in a neutral line on a separate switchboard to the live fuses, which of course left the circuit live and unsafe to work on without extra safety measures. Removing both fuses, I replaced the lamp socket and then rewired and replaced the fuses.

The ancient switchgear in the pub cellar reminded me that electrical practices in the the pre-WW2 era were different to the more modern (early 1980s) times and reinforced the concept of testing before attempting any sort of electrical work.

In the same pub, the landlord had replaced a broken plug on a pie warmer, but it wasn't warming so he asked me to check it. A slight tingling shock (I was insulated from ground) suggested that I should check the plug wiring. Sure enough, the landlord was red/green colour blind and had interchanged the live and Earth wires (the old colour scheme, red-live, black-neutral, green-earth).
Both of these stories illustrate why, at least in the UK, electricians are taught a standard ‘proving dead’ procedure. This involves a dedicated voltage indicator, which has no off button or requirement for batteries, and a test unit for the proving unit. They also must test all combinations of L, N and E as there is no guarantee that polarity is correct.

I’m surprised at your landlord/pie warmer story - even without the colours, L and E should be very different lengths, unless he chopped off and started again.
 
  • #63
darth boozer said:
Sure enough, the landlord was red/green colour blind and had interchanged the live and Earth wires (the old colour scheme, red-live, black-neutral, green-earth).
Oh yikes!
 
  • #64
In Norway, both wires are "live". They may or may not have any close relation to protective ground.
 
  • #65
Svein said:
In Norway, both wires are "live". They may or may not have any close relation to protective ground.
I find that very hard to believe. In the USA it is common knowledge amongst those who have an interest in electricity that the neutral it grounded. However, those with an ounce of sense still respect the neutral wire as much as the hot. Sometimes it seems the neutral wire gets more people into trouble than the hot.
 
  • #66
Averagesupernova said:
I find that very hard to believe. In the USA it is common knowledge amongst those who have an interest in electricity that the neutral it grounded. However, those with an ounce of sense still respect the neutral wire as much as the hot. Sometimes it seems the neutral wire gets more people into trouble than the hot.
It’s an IT system in Norway, I believe. Isole-Terre.

It’s pointless attempting an Earth return path through the rocky terrain, so the supply transformer is not earthed at all, or only through high impedance. The installation has a local earth.
 
  • Like
Likes   Reactions: Asymptotic
  • #67
I am not sure why would the Norway system differ from others here in Europe? Maybe @Svein can elaborate , as far as I know , in the link below
https://energifaktanorge.no/en/norsk-energiforsyning/kraftnett/

it is said that they have 400v and 230v supply, which is the same as I have here below Scandinavia, 400v would be for the 3 phase system and 230v single phase. Here also neutral exists only in the lowest distribution part from the local step down 20kv/0.4kV traffo to the user, before that there are only 3 wires for each phase.
As for the US split phase system I understand that they ground the center tap because that is normally always used as one of the two pins for a 120v outlet, what confuses me a bit is why in most of the diagrams they show the US split phase 240v as two sines 180 degrees out of phase because as I understand the 240v is the real full secondary of the transformer and being single phase I would expect to see a normal typical sine with a 240v amplitude if I probed it with a scope should I not?
 
  • #68
artis said:
I am not sure why would the Norway system differ from others here in Europe?
The rocky terrain, as I said.

artis said:
As for the US split phase system I understand that they ground the center tap because that is normally always used as one of the two pins for a 120v outlet, what confuses me a bit is why in most of the diagrams they show the US split phase 240v as two sines 180 degrees out of phase because as I understand the 240v is the real full secondary of the transformer and being single phase I would expect to see a normal typical sine with a 240v amplitude if I probed it with a scope should I not?
If you probed the outer taps, you would see a 240V rms sine. The diagrams you have seen are two simultaneous waveforms, commoned to the centre tap and connected to each outer.
 
  • Like
Likes   Reactions: Asymptotic
  • #69
Sure but they only look like that on drawings because in real life when one uses the 240v outlet the center tap is not used by that device/outlet.

Well here also we don't use ground for neutral (only for lighting rods and ground fault current protection) the neutral runs as a separate (4th ) wire from the nearest step down to load, this is so for every transformer.
I think that almost nowhere neutral runs back through ground as in most cases that would be a very inefficient/dangerous solution.
 
  • #70
artis said:
Sure but they only look like that on drawings because in real life when one uses the 240v outlet the center tap is not used by that device/outlet.
Phase is relative. Relative to the center tap, the outside ends of the secondary are 180 degrees out of phase. Been there, done that.
 
  • #71
artis said:
Sure but they only look like that on drawings because in real life when one uses the 240v outlet the center tap is not used by that device/outlet
I’m not sure how that relates to my answer, so I guess I’ll try again.

1. Scope between outer taps - one 240v rms sine. Centre not involved.

2. Using a two-channel scope, connect one probe common to centre, and its tip to one outer tap. Connect the other probe tip to the other outer tap. Displaying both channels simultaneously, you will see two sines, 120V rms 180deg apart.

^^^ This is a thought experiment. There are safety issues to consider when probing mains voltages.
 
  • Like
Likes   Reactions: Asymptotic, artis and Averagesupernova
  • #72
@Guineafowl thanks, I already understood that by the fact that @Averagesupernova said about the measurement being relative to center tap but you beat me to it
 
  • #73
Guineafowl said:
It’s an IT system in Norway, I believe. Isole-Terre.

It’s pointless attempting an Earth return path through the rocky terrain, so the supply transformer is not earthed at all, or only through high impedance. The installation has a local earth.
Spot on!
 
  • Like
Likes   Reactions: Asymptotic
  • #74
Hello just stumbled upon this.. trying to understand how diode bridge works. Is it an assortment of 4 different diodes , are they configured a specific way ? I am a bit confused on the construction. Any help would be great. Also why would this be necessary in a situation like this ?
 
  • #75
chipresistor122 said:
Hello just stumbled upon this.. trying to understand how diode bridge works. Is it an assortment of 4 different diodes , are they configured a specific way ? I am a bit confused on the construction. Any help would be great. Also why would this be necessary in a situation like this ?
This wikipedia article is pretty good : https://en.wikipedia.org/wiki/Diode_bridge

1606880037433.png


There is a non-planar crossover (the little half circle) in this bridge circuit ##-## that crosser can be replaced with 3 XOR gates to make it planar, arranged as shown here:

1606879120468.png

. . . and each those can be relaced by 4 NAND gates arranged as follows:

1606878936344.png


That can matter in micro-circuits, but generally doesn't matter on a breadboard circuit.
 

Attachments

  • 1606879861049.png
    1606879861049.png
    2.9 KB · Views: 176
Last edited:
  • #76
sysprog said:
This wikipedia article is pretty good : https://en.wikipedia.org/wiki/Diode_bridge

View attachment 273546

There is a non-planar crossover (the little half circle) in this bridge circuit ##-## that crosser can be replaced with 4 XOR gates to make it planar, arranged as shown here:

View attachment 273544
. . . and each those can be relaced by 4 NAND gates arranged as follows:

View attachment 273543

That can matter in micro-circuits, but generally doesn't matter on a breadboard circuit.
"... that crosser can be replaced with 4 XOR gates to make it planar, arranged as shown here:"
There are only three XOR gates shown.

I don't see why a diode bridge was suggested in the context of the OP, anyway. It certainly wouldn't work for an appliance requiring an AC supply, and neither would using logic gates as part of a diode bridge in a power circuit.
 
  • Like
Likes   Reactions: sysprog and sophiecentaur
  • #77
darth boozer said:
"... that crosser can be replaced with 4 XOR gates to make it planar, arranged as shown here:"
There are only three XOR gates shown.

I don't see why a diode bridge was suggested in the context of the OP, anyway. It certainly wouldn't work for an appliance requiring an AC supply, and neither would using logic gates as part of a diode bridge in a power circuit.
You right ##-## it's 3 XORs, 4 NANDs each to replace them, and 4 diodes in the bridge ##-## thanks for the correction ##-## I'll edit the post ##-## as for appliances that use bridge rectifiers to convert AC to full-wave-rectified DC, there are many such devices.

Regarding using logic gates as part of the bridge circuit, they could be used in the DC part of the circuit to allow a planar crossover, like this:

1606893624932.png

The 3 XOR gates could go where the left-tilted X with the adjacent - + and + - labels is in the circuit illustration.
 

Attachments

  • 1606892305321.png
    1606892305321.png
    3.3 KB · Views: 175
Last edited:
  • #78
Sysprog , thank you for the thoughtful response. It is much appreciated I needed a refresher on how Bridge Rectifiers work.
 
  • #79
Yup that is a good explanation. Overall a bridge rectifier is just an assortment of 4 or more diodes. It comes in a pre-assembled module. They convert AC current to DC current and are generally used in power supplies or battery chargers. The assortment of diodes are used to allow current to flow in one direction only and not flow backwards. It is a really common component in our daily lives. I found another article for you to reference that should help refresh you. Talks about how it works, different applications and also has a video to go along with it Bridge Rectifier Explanation . Hope that helps ... let me know if you have any other questions. I am happy to help.

best,
 
  • Like
Likes   Reactions: sysprog

Similar threads

Replies
13
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 11 ·
Replies
11
Views
3K
Replies
4
Views
3K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 18 ·
Replies
18
Views
8K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 32 ·
2
Replies
32
Views
4K
Replies
14
Views
3K
  • · Replies 83 ·
3
Replies
83
Views
8K