Why Does the Phasor Rotate Anticlockwise?

  • Context: Undergrad 
  • Thread starter Thread starter Dadface
  • Start date Start date
  • Tags Tags
    Phasor Rotate
Click For Summary

Discussion Overview

The discussion revolves around the direction of phasor rotation, specifically why phasors are typically described as rotating anticlockwise. Participants explore whether this direction is a convention and if there are advantages to choosing anticlockwise over clockwise. The conversation touches on theoretical aspects, practical applications in electrical engineering, and the implications of phasor rotation in various contexts.

Discussion Character

  • Debate/contested
  • Technical explanation
  • Conceptual clarification

Main Points Raised

  • Some participants suggest that the anticlockwise rotation of phasors is likely a convention, similar to other conventions in mathematics and physics.
  • One participant notes that in 3-phase power systems, the positive sequence phasor rotates counterclockwise, while the negative sequence rotates clockwise, indicating that phasors can indeed rotate in both directions depending on the context.
  • Another viewpoint proposes that the choice of anticlockwise rotation may stem from the Cartesian coordinate system, where angles increase in that direction from the positive x-axis.
  • Some participants argue that the designation of positive or negative frequencies based on phasor rotation is somewhat arbitrary, while others contend that it is not entirely arbitrary, as it relates to the rate of change of phase relative to a reference frequency.
  • A participant elaborates on how higher frequency signals can appear to rotate in either direction depending on their linear combination and the context of a 3-phase system, providing examples of how harmonics can influence the resultant phasor direction.
  • There is a discussion about the implications of non-purely sinusoidal waves and how they can be decomposed into sinusoidal components, affecting the overall phasor representation.

Areas of Agreement / Disagreement

Participants express differing views on whether the anticlockwise direction is merely a convention or if it has deeper implications based on frequency and system behavior. The discussion remains unresolved, with multiple competing perspectives on the nature of phasor rotation.

Contextual Notes

Some claims about the relationship between frequency and phasor rotation depend on specific definitions and assumptions about the reference frame and the nature of the signals involved. The discussion also highlights the complexity of representing higher harmonics and their effects on phasor behavior.

Dadface
Messages
2,489
Reaction score
105
When phasors are used,for example to illustrate some of the properties of waves,all of the texts seem to emphasise that the phasor rotates anticlockwise.Why anticlockwise?I have always assumed that the direction is just a convention...or am I missing something?If it is a convention then does the choice of anticlockwise have any advantages over clockwise?Thanks to anyone who replies.
 
Last edited:
Physics news on Phys.org
It's probably a convention, like so many other things.

By the way, why do degrees start at 3 o'clock and increase counterclockwise? Maybe these degrees are the ones to blame!

In any case, there ARE phasors that rotate in the clockwise direction.

I am an electrical engineer and learned about phasors and symmetric components in the power systems class a couple of decades ago...this is what I remember.

Example, if you have a 3-phase power system, it can be handled and represented with a single phasor per quantity when things are nice and balanced; but when something happens (a short circuit, lightning, etc) and the system becomes unbalanced, it is difficult (impossible with phasors) to handle and so it is decomposed into its 3 symmetric components...these symmetric components can once again be handled with phasors as "things" are balanced within the corresponding frame of reference...the thing is that I said they are 3 symmetric components, they are referred to as the positive sequence, negative sequence and zero sequence components...the positive one rotates counterclockwise, the negative rotates clockwise and the zero does not rotate at all. The linear combination of these symmetric components models the original system.

A phasor represents a single pure sinusoidal quantity so that when there is a fault and things are momentarily not purely sinusoidal, an n-phase system can be decomposed into its n symmetric components that when combined can represent any state of the original system via these symmetric components which CAN be handle with phasors.

I hope this help and did not make it too confusing.
 
I think it's probably because we originally chose Right and Up for our +X and +Y cartesian axes and gradient is the angle 'upwards from the horizontal'. That gives you angles that increase from zero to 90 in an anticlockwise direction. The rest just follows.
 
Thanks gsal and sophiecentaur.
 
We can classify frequencies as being positive or negative depending on what way the phasor rotates; the direction we nominate as being positive is quite arbitrary.

Claude.
 
Not quite arbitrary. For a frequency higher than the reference frequency (at which the axes are 'frozen', a higher frequency will be represented by a phasor which is rotating anticlockwise and vice versa because of the rate of change of phase relative to the reference.
 
sophiecentaur said:
Not quite arbitrary. For a frequency higher than the reference frequency (at which the axes are 'frozen', a higher frequency will be represented by a phasor which is rotating anticlockwise and vice versa because of the rate of change of phase relative to the reference.

While the statement above is true for individual signals...

It is possible to make higher frequency signals show up rotating counterclockwise respect to the frame of reference...this can be accomplished via linear combination of spatially shifted higher frequency signals.

This is not as weird as it may seem...it is happening right now, somewhere in the world.

I am talking about a 3-phase electrical generator at some power plant that might not be working under perfect conditions and hence having non-purely sinusoidal waves through its winding...under these conditions, the waves can be decomposed (fourier) into purely sinusoidal ones starting with one at the fundamental frequency (f) and the rest at higher frequencies (2f, 3f, 4f, 5f, 6f, 7f...).

BUT, when we are talking about a 3-phase system, we have 3 sets of these signals that are (electrically) phase shifted 120 degrees (360/3) and being applied to windings ("mechanically", physically) located 120 degrees (for 2-pole generator) away from each other...when you add the signals vectorially, the resultant may rotate counterclockwise (CCW) or clockwise (CW) respect to the fundamental...

...for example, say the fundamental is rotating CCW at an angular velocity of 1f:
  • when you add the 5th harmonics from all 3 phases, the resultant will rotate CW with a velocity of 5f
  • when you add the 7th harmonics from all 3 phases, the resultant will rotate CCW with a velocity of 7f
 
gsal said:
While the statement above is true for individual signals...

It is possible to make higher frequency signals show up rotating counterclockwise respect to the frame of reference...this can be accomplished via linear combination of spatially shifted higher frequency signals.

This is not as weird as it may seem...it is happening right now, somewhere in the world.

I am talking about a 3-phase electrical generator at some power plant that might not be working under perfect conditions and hence having non-purely sinusoidal waves through its winding...under these conditions, the waves can be decomposed (fourier) into purely sinusoidal ones starting with one at the fundamental frequency (f) and the rest at higher frequencies (2f, 3f, 4f, 5f, 6f, 7f...).

BUT, when we are talking about a 3-phase system, we have 3 sets of these signals that are (electrically) phase shifted 120 degrees (360/3) and being applied to windings ("mechanically", physically) located 120 degrees (for 2-pole generator) away from each other...when you add the signals vectorially, the resultant may rotate counterclockwise (CCW) or clockwise (CW) respect to the fundamental...

...for example, say the fundamental is rotating CCW at an angular velocity of 1f:
  • when you add the 5th harmonics from all 3 phases, the resultant will rotate CW with a velocity of 5f
  • when you add the 7th harmonics from all 3 phases, the resultant will rotate CCW with a velocity of 7f

The way that a sinusoidal signal is generated is not relevant to its rate of change of phase. The 5th harmonic will have a frequency of 250 Hz (or 300 in the US) the phase of such a high frequency signal is advancing five times faster than the fundamental. ω is d∅/dt. It can't be drawn easily on a phasor diagram because the relative phase is increasing so fast but the direction that the phasor points must be anticlockwise and the rate would be at 4X the fundamental (i,e, at the difference frequency). If you have found a simulation that shows you otherwise then the reason is due to sub sampling problems and aliasing. The analysis is pretty clear, however, as shown above.
 
Last edited:

Similar threads

  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 11 ·
Replies
11
Views
3K
  • · Replies 39 ·
2
Replies
39
Views
6K
  • · Replies 37 ·
2
Replies
37
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 23 ·
Replies
23
Views
4K
  • · Replies 5 ·
Replies
5
Views
4K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K