hello,i am se electrical student. I want to know why in a transformer at start up the flux through the core is doubled?
Last edited:
Normally when a transformer (without load) is running steady state on a sinusoidally varying voltage, the voltage leads the current by 90 degrees (e.g., V = L dI/dt). So during steady state operation, when the voltage is zero, the current is at a negative maximum. But at startup, both the voltage and the current are initially simultaneously zero (i.e., not 90 degrees apart). When the voltage is switched on at a phase where applied voltage is maximum, there is a transient current surge that wants to double the maximum core flux. If the inductance L is a nonlinear function of current, the current surge is worse.djsourabh said:hello,i am se electrical student. I want to know why in a transformer at start up the flux through the core is doubled?
Bob S said:When the voltage is switched on at a phase where applied voltage is maximum, there is a transient current surge that wants to double the maximum core flux.
I thought I was careful to state that the "surge that wants to double the maximum core flux". In addition, if the core saturates (i.e., dL/dI is negative), the current surge is much larger. I have one transformer that will often create so much current surge that all the lights in the building flicker when I switch it on.m.s.j said:Excuse me my dear friend, I think vice versa the increasing of flux (saturation condition) is origin of inrush magnetizing current, also mentioned phenomenon is related to transformer magnetizing characteristics (core material) not angle difference between voltage and current.
Bob S said:I thought I was careful to state that the "surge that wants to double the maximum core flux".
Bob S