Which Earth Fault Relay Setting Is Correct for a 20 KV Zig-Zag Transformer?

AI Thread Summary
The discussion centers on determining the correct primary current setting for an Earth fault relay in a 20 KV zig-zag transformer. The initial setting of 8.67 A is based on the transformer's continuous rating, but calculations suggest a higher setting of 12.5 A may be more appropriate due to the unique characteristics of zig-zag transformers. It is noted that zig-zag transformers operate with less voltage per leg, leading to a lower continuous rating of 5 A and a neutral current rating of 15 A. The consensus leans towards selecting 12.5 A for optimal performance during line-to-ground faults. Understanding the differences in transformer types is crucial for accurate fault relay settings.
m.s.j
Messages
212
Reaction score
1
A 20 KV switchgear have equipped with one zig-zag earthing transformer. As you know,
A grounding transformer must handle the unbalanced load on the circuit as well as the duty during line-to-ground faults. If the circuit has a lot of unbalance load, then we must concern the continuous rating of transformer in addition of its short time withstand currents. The continuous rating power of mentioned grounding transformer is 100 KVA.
The primary current setting of related Earth fault relay that installed in neutral point of E.T. is 8 Amp.
This set point current is chosen in base of E.T. continuous rating current and following calculations:

It =100/ (20x1.73) = 2.89 A

In= 3x It = 8.67 A

But the Earth fault current calculation and analyses dictate other primary current setting (12.5 A).

Which one current setting is correct? Which one do you choose?



--------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Engineering news on Phys.org
I would say 8.67 A since you are concerned with the phase to phase loading.
 
Unfortunately, nowadays with our world information transmission system (internet), we usually neglect the basic conceptions and deep thinking about new problems.
With more deep thinking, we can find that the mentioned evident equation (S = 1.73 VI) is not correct for zig-zag earthing transformers.
Indeed, each leg of a grounding transformer carries one-third of the neutral current and has line-to-neutral voltage. So in a grounded wye - delta transformer, the total power rating including all three phases is the neutral current times
The line-to-ground voltage:
S= 1.73 VI
But a zig-zag transformer is more efficient than a grounded wye - delta transformer.
In a zig-zag, each winding has less than the line-to-ground voltage,
by a factor of 1.73, so the bank may be rated lower:
S = 1.73/1.7.3 VI = VI
Therefore, the continuous rating current of E/T is 5 A and rating neutral current is 15A, and we can choose 12.5A as correct Earth fault primary current setting.


--------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...

Similar threads

Replies
3
Views
9K
Replies
1
Views
3K
Back
Top