Polarity of 3p core transformer

AI Thread Summary
A 380V, 3-phase core type transformer is utilized as an AC line choke in a VFD setup, focusing on its inductance properties. It is confirmed that the R phase can connect to any winding, provided the phase sequence is maintained. Ensuring consistency among the three windings is crucial, with no end-to-end swaps. For balanced phase currents, the shared core must exhibit a sum zero magnetic field. Proper connections will optimize the transformer's performance in this application.
Amith Menon
Messages
1
Reaction score
0
I have a 380V,3 phase core type transformer which is being used as AC line choke in the incomer of a VFD.As we are using only the inductance property of the transformer,I was just wondering whether we could connect R phase of the supply to any winding and then follow the phase sequence accordingly.
Thanks in advance
 
Engineering news on Phys.org
Welcome to the PF.
Yes. The only important thing is to make sure that the three windings are consistent and that one is not swapped end for end. For balanced phase currents, the shared core should have a sum zero field.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
Back
Top