A little help understanding 3 phase waveforms and summation

Click For Summary

Discussion Overview

The discussion revolves around understanding three-phase power systems, specifically the summation of voltages in a 208V three-phase service. Participants explore the relationship between individual phase voltages and the resultant voltage when connecting loads across two phases. The conversation includes technical aspects of waveform representation and calculations related to phase angles.

Discussion Character

  • Technical explanation
  • Conceptual clarification
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant asserts that two 120V phases do sum to a single 208V sinewave, but emphasizes that the phases are a differential voltage and are plotted referenced to neutral.
  • Another participant suggests that understanding Phasor Notation could simplify the analysis of how the phases combine, indicating a trigonometric approach to the problem.
  • A mathematical expression is provided to illustrate the relationship between the sinewaves, highlighting that the phase voltages should be subtracted rather than added.
  • One participant expresses confusion about why their Excel calculations show different results for summed amplitudes at different phase separations, questioning whether the issue lies in their charting method.
  • Another participant acknowledges the help received and notes that the correct approach was to subtract one phase from the other in their calculations.

Areas of Agreement / Disagreement

Participants generally agree that the two 120V phases relate to a 208V voltage, but there is some contention regarding the method of summation and the interpretation of phase relationships. The discussion remains unresolved regarding the specifics of the Excel calculations and their implications.

Contextual Notes

There are limitations in the discussion regarding the assumptions made about phase relationships and the definitions of voltage measurements. The mathematical steps in the Excel calculations are not fully resolved, leading to uncertainty in the conclusions drawn from them.

InquisitiveOne
Messages
38
Reaction score
4
Hello all,

I'm in the process of learning about 3 phase power and how to wire loads to a generator. I've searched high and low with as many sentence structures as I could think of in the google search bar and I can't seem to find the answers I'm looking for. I'm really hoping you guys can help.

I'll be referencing 208V single phase loads connected to 208V 3 phase service/generator.

I understand the individual phases measure 120V to ground, are separated by 120º, and connecting a load across two phases results in single phase 208V. I also understand the formula used to calculate the resultant combined voltage is one legs voltage to ground times the square root of 3. There are a ton of pictures on line and videos on YouTube that show the 2 (or 3) 120V phases as viewed on an oscilloscope, separated by 120º. But, there doesn't seem to be a single source that shows the combined 208V waveform. Looking at the separate waveforms makes me think the resultant waveform might have a couple bumps positive and a couple bumps negative, but I also recall learning somewhere that the two out of phase sinewaves sum to become a single sinewave.

Question 1) Do the two 120V phases sum to a single 208V pure sinewave?

I'm feeling 95% positive the answer is yes.

To help better understand the relationship and how the two phases combine, I set up and Excel sheet to help visualize everything. Except, I'm running into a confusing issue. Two sinewaves of identical frequency and 120V amplitude, separated by 120º are summing to a sinewave centered between the to being summed, but the combined amplitude is only 120V. If I change the separation angle to 60º, the summed sinewave peaks at 207.841, the same exact figure I get when completing the equation I put up above.

I've double and triple checked all my Excel formulas and have watched several YouTube videos that also verify two identical sinewaves separated by 120º sum to the originals amplitude.

Question 2) Do you have any idea why the spreadsheet indicates the right 208V voltage when separated by 60º, no increase in summed amplitude when separated by 120º, yet measuring across two legs of 3 phase service, separated by 120º does in fact sum to an increased voltage?

Is it my charting in Excel? Or, is there something about the way 208V single phase is created that makes it add up as though the phases were actually 60º apart?

I'm a little confused about that.

I have one other question that I'll save for later. The answers to these two may help me get there on my own.

Thank you guys, very much, for any help or guidance in better wrapping my mind around this concept.
 
Engineering news on Phys.org
InquisitiveOne said:
Question 1) Do the two 120V phases sum to a single 208V pure sinewave?
Yes, but the phases are a differential voltage, so they subtract and are plotted here referenced to "neutral", plotted as white. Frequency = 50 Hz.
Here on the left are the "lines" or "legs", R, B and Y; Red, Blue and Yellow.
The "phases" are R-B, B-Y and Y-R; magenta, orange and gray.
Notice the amplitude of 120 Vrms is 170 Vpeak.
The amplitude of the "phases" is then 208 Vrms, or 295 Vpeak.
Legs and Phases.png
 
  • Like
  • Informative
Likes   Reactions: Klystron, DaveE and berkeman
InquisitiveOne said:
Question 1) Do the two 120V phases sum to a single 208V pure sinewave?
Have you come across Phasor Notation in all your reading? It makes questions like this one very straightforward. By 'freezing' the constant phase rotation (e.g. 50 cycles per second), you get a simple bit of trigonometry to find how the Phasors (vectors) combine.
 
  • Like
Likes   Reactions: DaveE
##sin(\omega t) - sin(\omega t +\frac{2}{3} \pi) = ##
##sin(\omega t) - sin(\omega t)cos(\frac{2}{3} \pi) - cos(\omega t)sin(\frac{2}{3} \pi) = ##
##sin(\omega t) - sin(\omega t)(\frac{-1}{2}) - cos(\omega t)(\frac{\sqrt{3}}{2}) = ##
##sin(\omega t)(\frac{3}{2})-cos(\omega t)(\frac{\sqrt{3}}{2}) =##
##\sqrt{3}[sin(\omega t)(\frac{\sqrt{3}}{2})-cos(\omega t)(\frac{1}{2})] =##
##\sqrt{3}[sin(\omega t)cos(\frac{1}{6} \pi) - cos(\omega t)sin(\frac{1}{6} \pi)]=##
##\sqrt{3}[sin(\omega t - \frac{1}{6} \pi)]##

Note that you don't sum the phase voltages, you subtract them. Think of holding a voltmeter with + and - probes.
 
i.e. the Potential Difference. 😉👍🏼
 
I really appreciate all of you. You have all been a big help in both, wrapping my mind around how and why it is the way it is, as well as making the appropriate changes to my Excel graphs that indicate the relationship between phases correctly... which really was as simple as subtracting one phase from the other instead of adding them.

Thanks again. You guys (and gals) are awesome!
 
  • Like
Likes   Reactions: sophiecentaur, DaveE and Baluncore

Similar threads

  • · Replies 27 ·
Replies
27
Views
955
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 5 ·
Replies
5
Views
6K
  • · Replies 77 ·
3
Replies
77
Views
8K
  • · Replies 41 ·
2
Replies
41
Views
18K
Replies
21
Views
5K
  • · Replies 46 ·
2
Replies
46
Views
5K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 13 ·
Replies
13
Views
5K
  • · Replies 17 ·
Replies
17
Views
4K