  • #1
artis
1,481
976
Friend gave me this task he had back in school to calculate the necessary amperage for a fuse that is put in series with one of the phases for a 3 phase induction motor.
I could calculate the working current of the motor from the rated kW and cos voltage/current angle, but I couldn't figure out how to calculate the starting current.

The parameters are as such , motor is put in a 3 phase delta (triangle) connection, supply voltage 380v, motor rated power 9.4Kw, power coefficient is 0,91cos.
From this I took 9.4kW and expressed that as 9400w which I divided by the power coefficient times voltage, I got 27.18 amps, the total current consumed, divide that by 3 as each phase uses one third of the current and I got 9.06 amps as the working current for a phase.
Obviously I could crudely take those 9 amps and multiply them by about 7 (times the nominal current for an induction motor at startup) but the task gives additional data, so my question then is using this additional data is it possible to determine the starting current and how?

additional data: mechanic efficiency = 0.98
Kp=Ip/In = 5 (really don't know what this means)
and lastly lower case alpha α = 2.0thanks.
 
Engineering news on Phys.org
  • #2
There are published guidelines for motor fusing , available at national electrical code and at fuse manufacturers sites

eg
https://m.littelfuse.com/~/media/electrical/application-notes/littelfuse-motor-protection-guide.pdf
http://www.cooperindustries.com/content/dam/public/bussmann/Electrical/Resources/solution-center/technical_library/BUS_Ele_Tech_Lib_Motor_Protection_Tables.pdf

As to starting current
someplace on the motor nameplate should be an entry called "NEMA KVA Code" or similar
it's a single letter code telling you what is the starting current
you look up the value corresponding to the one letter code in a table
it's expressed in kva per horsepowerhere's the top half of the table, rest of it is in the link
244337


https://www.electricalengineeringtoolbox.com/2015/12/nema-locked-rotor-kva-for-three-phase.html
old jim
 
  • Like
  • Informative
Likes dlgoff and anorlunda
  • #3
If we take R&M technical data resource for a 12.5 HP/9.3 kW induction motor at 380 V 50 Hz the rated current it is about 20 A[from other source the efficacy it is only 88% and power factor only 0.8]. However, in your case I=9400/SQRT(3)/0.98/0.91=16 A.
Ip/In could be the start current divided by rated then the start current it is about 80 A. In my opinion α it could be Tα/Tn the starting torque to rated torque ratio. Usually the start current it is between 6 to 8 times the rated. However, for 16 poles [750 rpm] this could be 5.
Still, in my opinion, some data are not entirely real. For instance efficacy of 98% is difficult to achieve.
244406
 
  • #4
Well this is a crude school task so I guess the numbers aren't meant to add up to real life performance.
@Babadag
so you are dividing the rated power in watts with the square root of (mechanical efficiency divided by cosine) ? Then why the you put (3) after sqrt, I don't understand this one?

I am trying to solve the equation you gave but I can't , I'm getting different numbers
 
Last edited:
  • #5
Irated[A]=P[kW]*1000/[√3*cosfi*eff*V]
[only 3 is under sqrt[√]
Irated=9400/[SQRT(3)*0.98*0.91*380]=16 A
 
  • Like
Likes artis
  • #6
@Babadag ok and if I had a single phase induction motor , would I then have to use sqrt of 2 or any sqrt or none at all?
 
  • #7
If "none at all" it means 1 then it is correct.
 

1. What is AC induction motor startup current?

AC induction motor startup current, also known as locked rotor current, is the initial current drawn by an AC induction motor when it is first turned on. It is typically higher than the motor's rated current and is necessary to overcome the inertia of the rotor and start the motor's rotation.

2. How is AC induction motor startup current calculated?

AC induction motor startup current can be calculated by multiplying the motor's rated current by its starting current factor. This factor is typically between 5 and 8 for most motors, but can vary depending on the motor's design and load characteristics.

3. Why is AC induction motor startup current important?

AC induction motor startup current is important because it determines the size and capacity of the motor's starting equipment, such as circuit breakers and motor starters. It also affects the power quality and stability of the electrical system, as high startup currents can cause voltage dips and fluctuations.

4. How can AC induction motor startup current be reduced?

AC induction motor startup current can be reduced by using soft starters or variable frequency drives (VFDs). These devices gradually ramp up the voltage and frequency supplied to the motor, reducing the initial current spike and providing a smoother startup. Proper motor sizing and selection can also help reduce startup current.

5. What are the potential risks of high AC induction motor startup current?

High AC induction motor startup current can cause mechanical stress and wear on the motor's components, leading to premature failure. It can also cause voltage sags and dips in the electrical system, affecting other equipment connected to the same power source. In extreme cases, it can even trip circuit breakers and disrupt power supply to the entire facility.

Similar threads

Replies
2
Views
629
Replies
4
Views
1K
  • Electrical Engineering
Replies
5
Views
973
  • Electrical Engineering
Replies
11
Views
2K
  • Electrical Engineering
Replies
8
Views
1K
  • Electrical Engineering
Replies
2
Views
2K
Replies
2
Views
411
  • Electrical Engineering
Replies
1
Views
664
  • Electrical Engineering
Replies
4
Views
719
Replies
4
Views
2K
Back
Top