Added resistance due to coiled wire

  • Thread starter Thread starter Patrick791
  • Start date Start date
  • Tags Tags
    Resistance Wire
Click For Summary

Discussion Overview

The discussion revolves around the calculation of added resistance in a coiled cable configuration compared to a flat layout, specifically focusing on the effects of magnetoresistance and temperature changes due to the coiling. Participants explore the implications of using AC versus DC current and the associated phenomena such as skin effect and proximity effect.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • Patrick inquires about calculating added resistance due to coiling a cable and mentions running 250A through it.
  • Some participants suggest that the term "impedance" may be more appropriate than "resistance" in this context.
  • One participant notes an observed increase in resistance during testing of coiled versus uncoiled wires, questioning whether this is due to magnetoresistance or increased heat from proximity.
  • Another participant argues that magnetoresistance is unlikely to be significant with the given parameters, suggesting that increased resistivity due to temperature is a more plausible explanation.
  • Participants discuss the effects of AC versus DC current, with some stating that AC may lead to increased effective resistance due to skin and proximity effects.
  • There is a debate about the significance of skin effect at 60Hz, with some asserting it is negligible while others provide calculations indicating detectable losses.
  • Patrick expresses curiosity about the cause of resistance increase and questions the accuracy of measurement instruments used.
  • One participant suggests measuring the temperature in the coil, noting that a temperature rise could account for a measurable increase in resistance.
  • Patrick reports a 14% temperature increase between coiled and uncoiled configurations and attributes this primarily to the proximity of the cable to itself and inadequate ventilation.
  • Another participant challenges the interpretation of the temperature increase, suggesting that it should be expressed in degrees Celsius rather than percentage and provides a calculation for expected resistance increase based on temperature rise.
  • Discussion includes references to inductance calculations for the coiled configuration, with suggestions to use online calculators for estimates.

Areas of Agreement / Disagreement

Participants express differing views on the significance of magnetoresistance, the effects of AC versus DC current, and the relevance of skin effect at 60Hz. The discussion remains unresolved regarding the primary cause of the observed increase in resistance.

Contextual Notes

Participants note limitations in measurement accuracy and the dependence on definitions related to resistance and impedance. There are unresolved mathematical steps regarding the calculation of inductance and resistance values.

Patrick791
Messages
4
Reaction score
0
Hello everyone,

I was wondering how to calculate the added resistance experienced when a cable is coiled rather than layed flat due to the magnetoresistance of the magnetic field created by the solenoid configuration.

I will be running 250A though a cable which will be coiled like a solenoid that has 5 turns and a radius of 40 inches, (although I have not calculated this yet) I can determine the DC and AC resistance of the cable layed flat as well as the length of cable used.

Thanks,
Patrick
 
Engineering news on Phys.org
It's not "resistance" it's "impedance". I can't help you with the formula but I suggest that you look up "coil impedance calculator".
 
Well the problem we ran into during testing was that the resistance increased when we measured coiled vs uncoiled. We are trying to determine whether or not this was a factor or the fact that the coiled wires are closer together (therefore increasing the heat of the wires) which in turn increases the resistance. As seen in equation R(T) = Ro[1 + a[T-To]].

Thanks for the input. I was able to calculate the impedence given my parameters.
 
You won't have any magnetoresistance with such figures. But hotter metal possibly, and this increases the resistivity.
 
Is that 250 amp AC or 250 amp DC.
If it's DC there should not be any increase in resistance except for temperature increase.
If it's AC there will probably be an increase in effective resistance (watt loss) at 250 amp and 60 Hertz.
You might Google skin effct and proximity loss.
 
Carl Pugh said:
Is that 250 amp AC or 250 amp DC.
If it's DC there should not be any increase in resistance except for temperature increase.
If it's AC there will probably be an increase in effective resistance (watt loss) at 250 amp and 60 Hertz.
You might Google skin effct and proximity loss.

Skin effect at 60Hz? Really?
 
Yes AC current is being passed through the cable, and skin effect + proximity effect should be taken into consideration since we are using a medium voltage (35kV rated) cable with an aluminum core.
 
Patrick791 said:
Yes AC current is being passed through the cable, and skin effect + proximity effect should be taken into consideration since we are using a medium voltage (35kV rated) cable with an aluminum core.

My understanding is that skin effect is a function of frequency and at 60Hz the effect is probably not even measurable, much less significant.
 
Skin depth in copper at 60 hertz is 0.33 inch. So any copper conductor over say 3/8 inch diameter will have detectable loss due to skin effect. (Yes I know that 3/8 inch diameter could be 1/8 inch or 3/4 inch or anything in-between)

Patrick;
Just curious, but why do you believe that the increase in resistance was caused by magnetoresistance of the magnetic field?
How large was the increase in resistance?
What was the accuracy of the instruments that were used to make these measurements?

I would be inclined to believe that the measured increase in resistance was due to measurement errors.
 
  • #10
Carl Pugh said:
Skin depth in copper at 60 hertz is 0.33 inch. So any copper conductor over say 3/8 inch diameter will have detectable loss due to skin effect. (Yes I know that 3/8 inch diameter could be 1/8 inch or 3/4 inch or anything in-between)

Having now done some research, I now see that my "knowledge" of skin effect was completely wrong, colored as it was by recollections of calculations regarding very high frequency wave guides some 40+ years ago. Thank's for the correction.
 
  • #11
Could you, perhaps, measure the temperature in the coil? The thermal coefficient for Aluminium is about 0.4% per degree C so a 10 degree rise could account for a 4% increase in R. See here
Does that square with what you have been getting?
 
  • #12
Well we were only testing this to measure the temperature differential between the coiled and uncoiled wire. We were told that the magnetic field induced by the coiled wire would increase the temperature of the conductor therefore increasing the resistance. Before testing, we wanted to get a ballpark estimate for this increase in resistance.

We measured a 14% temperature increase between the coiled and uncoiled configuration using the same cable and meter to measure the DC resistance (we do not have a meter to measure the AC resistance).

I'm sure most of the temperature increase is due to the proximity of the cable to itself in its wound formation and the fact that its in an enclosure with insufficient ventilation.
 
  • #13
I think you probably don't mean 14 "percent" because the only way that would mean anything would be if you use the absolute (Kelvin) scale?
So 14oC of temperature increase would be expected to increase the resistance by about 5.6% due to the positive temperature coefficient of resistivity of Aluminium. Afaik, any other effects are at a much lower level and 'only just detectable'.
The Inductance is an entirely different thing but it is easy to estimate this using the formula for inductance of a coil. There are 'calculators' for this, which you can easily find with a Google search - you put the dimensions in and you get the value of L. The inductance would not be much for the coil size you quoted unless you added an iron core.

I can't find any mention of the actual resistance values you got (hot and cold)?? If they differ by about 5%, then we've explained it.
 

Similar threads

  • · Replies 11 ·
Replies
11
Views
4K
Replies
22
Views
5K
  • · Replies 26 ·
Replies
26
Views
3K
  • · Replies 3 ·
Replies
3
Views
5K
Replies
0
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
Replies
12
Views
3K
  • · Replies 6 ·
Replies
6
Views
2K
Replies
64
Views
8K