Air Change Rate with Low Air Circulation

AI Thread Summary
In a 500-sq.ft laboratory with a 10 air changes per hour (AC/hr) rate, air circulation is significantly affected by the distance between the ceiling-mounted intake and exhaust, leading to lower air change rates near the floor. Calculating air change rates at different heights is complex due to variables like supply air temperature and diffuser shape, resulting in non-uniform airflow and dead spots. Solutions such as supplying air low and returning it high, or using directional grilles to promote circulation, can improve air distribution. Implementing these changes is cost-effective and can enhance air quality in the lab. Overall, addressing air circulation issues is crucial for maintaining a healthy laboratory environment.
Cusereef
Messages
1
Reaction score
0
I figured an example is the easiest way to explain my question. A 500-sq.ft laboratory with 9-ft ceiling includes an HVAC system delivering enough air volume for an air change (AC) rate of 10 AC/hr. However, both the air intake and exhaust are located in the ceiling, 18-ft apart. In this closed room with no additional air circulation air monitoring indicates that the air change rate is less closer to the floor (0-2 ft). Is there a way to calculate the air change rate at different room heights that includes air supply and exhaust located in the ceiling? Assume the laboratory is empty with standard temp, pressure, etc.
 
Engineering news on Phys.org
It isn't possible to calculate air change rate with height. There are just too many variables. Temperature of supply air, shape of the diffusers/registers - and the profile wouldn't be continuous throughout the room (there will always be dead spots). Even just walking around in the lab will stir-up the air. Plus, in the summer, the air coming out of the diffusers is cold and drops, while in the winter, air coming out may be warm and stay at the ceiling.

Supplying low, returning high is one potential solution. Fume hoods are another.
 
Assumeing you have a standard configered grille replace with a directional grille on the outlet pointed towards the closet wall, this should get the air to do a general loop about the room. It is the cheepest solution that should improve the situation. For a few hundred bucks or less is worth a try.
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...