The discussion centers on addressing a momentary air pressure drop from 90psi to 80psi when activating an air turbine motor, which disrupts other system components. Key solutions include adding an accumulator to manage sudden air demand and installing a separate regulator to stabilize pressure. The phenomenon known as "droop" occurs due to increased flow demand on the regulator, affecting the spring load and diaphragm pressure. A practical resolution is to implement a time delay on pressure sensors to accommodate brief fluctuations.

PREREQUISITES
  • Understanding of pneumatic systems and air pressure dynamics
  • Familiarity with air regulators and their operational principles
  • Knowledge of pressure sensors and PLC (Programmable Logic Controller) integration
  • Experience with flow control devices such as accumulators and control valves
NEXT STEPS
  • Research the installation and benefits of pneumatic accumulators
  • Learn about different types of air regulators, including dome loaded and sensitive spring loaded regulators
  • Explore methods for optimizing PLC response to pressure fluctuations
  • Investigate flow control techniques, such as using orifices or circuit setters
USEFUL FOR

Pneumatic engineers, maintenance technicians, and anyone involved in optimizing air pressure systems in industrial applications.

JimatDAC
Messages
3
Reaction score
0
I am having a problem with an air pressure drop. I have a supply of 100psi of around 4scfm. I have it regulated down to 90psi, but when I turn on an air turbine motor my regulated pressure drops momentarily (1-2sec) down to 80psi. This drop in pressure is unacceptable to other components in my system. Do I need to to run a separate regulator, or can I put an accumulator into the line to take up this sudden demand on available air?
 
Physics news on Phys.org
Welcome to PF.

How does the air turbine motor get turned on? Is there a valve too far from it that some tubing has to fill with air before it starts the turbine motor? Can you make the valve open slower? An accumulator should definitely help, as should a regulator. Or even an orifice or other flow restriction like a circuit setter, calibrated to only let the required flow for the turbine motor through.
 
Thanks Russ. The turbine gets started via a solenoid through 4' of 1/2" air line. I used to use smaller diameter air line (which worked like a restrictor), but changed to larger air line when having intermittent problems with turbine not starting. Now, I have the turbine starting everytime, but other components in the system can't tolerate the drop in pressure.
 
The drop in pressure caused by the increase in flow through the regulator is called droop, falloff and probably a few other things. It's caused by the fact that as more flow demand is put on the regulator, the valve poppet must open further to maintain pressure and increase flow. But the reg is most likely spring loaded and the spring load is a function of how far the spring has to extend. Even for fairly small movements of the poppet, the spring load (F = k dx) can change significantly, and as it does, the pressure opposing the spring (pressure on the diaphragm) has to change with it. So the pressure drops as the spring load falls off and the poppet opens.

Yes, the easiest thing to do is simply add another regulator to either the turbine or the rest of your system that can't tolerate the pressure drop.

There are other solutions such as
  1. increasing upstream pressure on the regulator
  2. install a more sensitive spring loaded regulator
  3. install a dome loaded regulator
  4. install a control valve
but I suspect those aren't as practical as simply adding another reg.
 
Problem solved

Thanks Goest for your explanation. You hit the nail on the head with what is going on. The momentary drop in air pressure caused a pressure sensor to send a signal to the PLC telling everything else to stop due to the pressure loss. I installed a sensor with a time delay or 2 seconds, and since the droop is less then that, I am good to go. Thanks again.
 

Similar threads

  • · Replies 11 ·
Replies
11
Views
3K
  • · Replies 27 ·
Replies
27
Views
5K
  • · Replies 67 ·
3
Replies
67
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 12 ·
Replies
12
Views
3K
  • · Replies 50 ·
2
Replies
50
Views
5K
  • · Replies 9 ·
Replies
9
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 32 ·
2
Replies
32
Views
10K
  • · Replies 13 ·
Replies
13
Views
21K