The discussion centers on the electrical design for apartment units, specifically regarding the distribution of 68A of 208V across two phases. The question raised is whether the 68A load will be shared between both phases or concentrated on one. It is clarified that if the load were a single device, such as a commercial water heater, all 68A would flow through one phase at any given moment. This indicates that the load does not split evenly across phases but can be concentrated. Understanding this concept is crucial for proper electrical design in the project.
herbeey
Messages
1
Reaction score
0
Hello,

I am an Electrical Engineering Technologist student and we have a design project that i am trying to understand. We are feeding apartment units with 82A of 120V and 68A of 208V. I am going to feed each with two phase lines and a neutral. What I am not sure about is if the 68A of 208V will be on both phases or not. Any clarification would be great!

Thank you.
 
Engineering news on Phys.org
Well - simplify your thinking

if all that 208 load were a single 68 amp device, say a commercial water heater,
at any instant would all 68 amps flow in one phase and out the other?

and you already knew the answer to that.

old jim
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...