ASTM A500 Grade B Square Tubing: Safely Supporting 180 lbs. Over 12 ft.

  • Thread starter Thread starter Jaman
  • Start date Start date
  • Tags Tags
    Square
AI Thread Summary
The discussion centers on the ability of 3" OD x .250" wall ASTM A500 Grade B square tubing to safely support a 180 lbs load over a 12 ft span, specifically for suspending a speaker system in a gym. It is confirmed that the tubing can handle the load, provided it is properly connected at both ends to the roof trusses. A safety factor of 5:1 is preferred for suspended speakers, and calculations indicate a bending stress of less than 5 ksi and a deflection of less than 1/4". Proper end connections near truss joints are emphasized for safety. Overall, the setup appears structurally sound for the intended application.
Jaman
Messages
2
Reaction score
0
Will 3"od X .250" wall ASTM A500 Grade B square tubing safely carry a single point load of 180lbs. over a 12ft span.

Thanks
 
Engineering news on Phys.org
It should, depending on proper end connection(s) design, but what's
the application? Cantilever or supported at both ends? What safety factor do you need? Deflection limitations? PLEASE ELABORATE.
 
We are suspending a speaker system in a gym. The tubing will span across 2 roof trusses and be bolted in place at each end. The speakers will be suspended using a "fly bar" that attaches to the speakers which is load rated by the speaker manufacture. The roof trusses should be more than enough to carry the load. I believe they are 5ft trusses. We like to have a 5:1 safety factor for suspended speakers. We always use load rated chain and shackles for hardware. Not sure how much deflection would be allowed, I guess that's what my question really is.

Thanks
 
Yes, that will work. A quick calc with the speaker suspended at the middle of the span indicates a bending stress of less than 5 ksi which has a safety factor about 9 against yield and a deflection at mid span of less than 1/4". Be sure to connect the ends close to a joint on the trusses.
Disclaimer: This author claims no responsibility for the proper design of the beam and its connections.
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...

Similar threads

Back
Top