Backup Generator for 90 Apartments: Is My Understanding Right?

  • Thread starter Thread starter ariseawake
  • Start date Start date
  • Tags Tags
    Generator
AI Thread Summary
Connecting a backup generator to 90 apartments in parallel with the normal power supply is technically feasible but requires careful management of load and synchronization. The builder's concerns about neutral connections and potential overloads are valid, as a 160 kVA generator may struggle to support multiple high-demand appliances simultaneously. A droop setting on the generator's governor can help manage load distribution effectively, while a synchroscope is necessary for safe connection to the grid. The concept of a current limiter in this context may be misunderstood, as it typically refers to fault protection rather than controlling individual household power. Properly addressing these technical aspects is crucial for a successful implementation of the generator system.
ariseawake
Messages
2
Reaction score
0
Hi friends,
Iam from india(230v).Iam no good in Electrical distribution.We have a back up generator in our community of 160kva.We have 90 apartments. From the generator wiring is directly done to few lights points and fan points in the household which would make them function when the normal powersupply fails.But I wanted the supply to be given directly parallel to the normal supply with a current limiter so that we can choose the load as per requirement.
But the builder says it may not be possible now and he quotes reasons which i don't follow fully and agree...He says there would be problem with gene neutral and normal supply neutral which I cannot agree.I feel all that is required is a automatic changeover switch with a current limiter.
note :Generator is a 3 phase generator. But only single phase is given to individual apartment.(may be distributed)

My questions are,
1.Is my understanding right that it should be easily possible to connect the generator o/p to each apartments main parallelly with a changeover switch and current limiter.

2.What should be the current limiter rating for above specs.
3.Would you refer to any particular type auto change over switch.Any brand or make or part no.Because builder is washing off hands that he does not know any.

Please help me with your suggestion.
 
Engineering news on Phys.org
Forgot to mention input from normal power supply is 3 phase 230 v.
 
What you need is a droop setting on the governor of your engine. When you parallel to the grid, you'll need a synchroscope to make sure you're in phase with the grid before closing the breaker connecting the generator output to the grid. Most utilities will adjust the governor of the engine to make sure the engine is running a little higher than the grid (60.1 Hz for a 60 Hz grid in the US). This is done to ensure that the generator picks up load when it is paralleled. If the generator speed is below the grid frequency, you run the risk of motoring the generator.

I'm not sure what you're thinking with the change over switch and the current limiter. A droop setting on the engine governor will accomplish the current limiting behavior that you're after, as the governor will adjust engine speed to provide the power that you set on the droop control.

Google droop and diesel generators.
 
I think that the main problem that you will have is overloading the generator 160 KVA gives a little less then 2 KW per household if all the house holds have for instance electric water heaters, freezers etc they could well overload your generator, this is probably the reason that houses were originally supplied with only a few lights and sockets, in the first place.
I'm not sure what you mean by a current limiter in an industrial setting a current limiter is a device that reduces the spike of current in a fault condition it's not a "valve" that can limit the flow of current into an individual house or flat.
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...