Calculating air flow through a tube

Click For Summary

Discussion Overview

The discussion revolves around calculating air flow through a tube for a campervan project, specifically focusing on mixing outside cold air with return air from a diesel heater to maintain proper CO2 levels. Participants explore various factors affecting air flow, including fan specifications, pressure measurements, and duct characteristics.

Discussion Character

  • Exploratory, Technical explanation, Debate/contested, Mathematical reasoning

Main Points Raised

  • One participant outlines the need for a specific minimal CFM to maintain CO2 levels and mentions the use of a 30 CFM axial fan with a 1.5" inner diameter tube.
  • Another participant suggests using a web-based fluid flow simulator, SimScale, to model the system.
  • Some participants emphasize the importance of measuring inside pressure, noting that blowing cold air could increase pressure while hot gases could decrease it.
  • There are suggestions to obtain a performance curve for the fan to understand the pressure available for pushing air through the ductwork.
  • Concerns are raised about the capability of a 30 CFM axial fan to generate sufficient static pressure, with comparisons to computer case fans.
  • Participants discuss the expected airflow needs based on the number of occupants and the CO2 generation rate.
  • Clarifications are made regarding the source of CO2, confirming it comes from breathing rather than exhaust gases.
  • One participant proposes using a centrifugal fan to achieve the necessary pressure and mentions plans to install a barometric pressure sensor to measure flow rate.
  • Calculations regarding pressure loss in the tube and the total fan static pressure required to achieve desired airflow are shared.

Areas of Agreement / Disagreement

Participants express various viewpoints on the adequacy of the axial fan for the intended application, with some questioning its ability to generate necessary pressure while others suggest alternative fan types. The discussion remains unresolved regarding the optimal fan choice and the exact calculations needed for airflow.

Contextual Notes

Limitations include the lack of precise pressure measurements and assumptions about the system's characteristics, such as duct friction and fan performance. The discussion also reflects uncertainty about the airflow requirements based on occupancy and environmental conditions.

mess
Messages
59
Reaction score
8
TL;DR
I have a fan blowing air into a tube, I would like to learn how to calculate the air flow so that I can figure out efficiency/losses between fans (axial, centrifugal) and tube diameter/length.
This is for a campervan project I am working on, I am trying to take outside air that is cold (Canadian winter) and mix it into the return air in my diesel heater. I need to hit a specific minimal CFM to maintain proper Co2 levels inside and I would like to be able to calculate this.

The axial fan I am using is 30 CFM, the tubeis 1.5" in inner diameter and the length is 4 feet. I don't have any pressure measurement's but I assume that would be needed? I can probably get an air pressure sensor and stick it in the tube just after the fan if its what is needed.
 
Engineering news on Phys.org
There is a web based fluid flow simulator you can use called SimScale. They have hundreds of examples and one may be close to what you want which you can copy and modify and run all for free up to 3000 core-hours of processor time.

https://www.simscale.com/
 
mess said:
This is for a campervan project I am working on, I am trying to take outside air that is cold (Canadian winter) and mix it into the return air in my diesel heater. I need to hit a specific minimal CFM to maintain proper Co2 levels inside and I would like to be able to calculate this.
To calculate it, you need to the inside pressure. Blowing cold air in could increase pressure, but hot gases going up the chimney could decrease pressure (unless you leave windows open.)
 
  • Like
Likes   Reactions: mess
mess said:
The axial fan I am using is 30 CFM, the tubeis 1.5" in inner diameter and the length is 4 feet. I don't have any pressure measurement's but I assume that would be needed? I can probably get an air pressure sensor and stick it in the tube just after the fan if its what is needed.
You need to obtain a performance curve for the fan ("fan curve") to obtain the pressure available to push through the ductwork at different flow rates. Here's a static pressure calculator:
https://www.engineeringtoolbox.com/duct-friction-pressure-loss-d_444.html
All of the elements of the system matter, though, so you'll need pressure drops for every component.

My gut tells me this could be a problem, because a 30 CFM axial fan sounds like a computer case fan, and they generate close to zero static pressure.

On the other hand, how much airflow are you expecting to need (is this system the outside air only part?)? How many people and how many CFM per person are you calculating? I wouldn't expect a van to be tight enough for CO2 to be an issue (though water vapor/condensation maybe).
 
Does your axial fan look like this?
Fan.jpg

Because if it does, it probably has a fan curve something like this:
Fan Curve.jpg

You can find the pressure loss in your tube by searching duct loss calculator. Here's one that looks good: https://www.engineeringtoolbox.com/duct-friction-pressure-loss-d_444.html. I plugged in 15 CFM, 1.5" diameter, and 4 feet long, and it said 0.1" w.c. pressure loss. That number sounds right to me.

If you have a size reduction at the beginning, add in the velocity pressure for the entrance loss. The velocity pressure for the same conditions is 0.09" w.c., and the total fan pressure needed is the sum of the velocity pressure and the duct friction loss. The total fan static pressure needed to push 15 CFM through your 1.5" duct is thus 0.1 + 0.09 = 0.19" w.c. If you want to measure these pressures, there is no need for a pressure gauge. Use a water manometer. A water manometer is a piece of clear plastic tubing, bent into a U-shape, and with some water in it. The pressure is the difference in water height between the two sides of the U, and is measured with a ruler.

Velocity pressure can be calculated from the Bernoulli equation, but an easier method used in HVAC work is Velocity pressure = (Velocity in FPM / 4005)^2. The velocity pressure is 1.0" w.c. at 4005 FPM (feet per minute), and is proportional to the velocity squared.
 
russ_watters said:
You need to obtain a performance curve for the fan ("fan curve") to obtain the pressure available to push through the ductwork at different flow rates. Here's a static pressure calculator:
https://www.engineeringtoolbox.com/duct-friction-pressure-loss-d_444.html
All of the elements of the system matter, though, so you'll need pressure drops for every component.

My gut tells me this could be a problem, because a 30 CFM axial fan sounds like a computer case fan, and they generate close to zero static pressure.

On the other hand, how much airflow are you expecting to need (is this system the outside air only part?)? How many people and how many CFM per person are you calculating? I wouldn't expect a van to be tight enough for CO2 to be an issue (though water vapor/condensation maybe).

I have several fans ranging between 20-150cfm, some with the computer fan design but higher power, and some centrifuge fans from vacuums that do create a good deal of pressure. but I also need it to be quiet that's why i need to find the best fit.

The calculations from another post say i need about 14cfm under normal circumstances for 1 person, probably about 9cfm when I am sleeping.

Here is my original post showing CO2 becomes an issue within just an hour or less:
https://www.physicsforums.com/threa...entration-in-a-campervan.996832/#post-6426144
 
'Return air in my diesel heater'. Not sure what this means.

Are you trying to pipe exhaust gases into your camper? Where is this CO2 coming from?
 
cmb said:
'Return air in my diesel heater'. Not sure what this means.

Are you trying to pipe exhaust gases into your camper? Where is this CO2 coming from?
It means that the air which the diesel heater intakes for heating (not combustion) is being mixed with the air I am pulling from the outside through a vent :)

And nope, exhaust gases are all outside the van. CO2 is coming from my breathing.
 
  • #10
jrmichler said:
Does your axial fan look like this?
View attachment 273757
Because if it does, it probably has a fan curve something like this:
View attachment 273759
You can find the pressure loss in your tube by searching duct loss calculator. Here's one that looks good: https://www.engineeringtoolbox.com/duct-friction-pressure-loss-d_444.html. I plugged in 15 CFM, 1.5" diameter, and 4 feet long, and it said 0.1" w.c. pressure loss. That number sounds right to me.

If you have a size reduction at the beginning, add in the velocity pressure for the entrance loss. The velocity pressure for the same conditions is 0.09" w.c., and the total fan pressure needed is the sum of the velocity pressure and the duct friction loss. The total fan static pressure needed to push 15 CFM through your 1.5" duct is thus 0.1 + 0.09 = 0.19" w.c. If you want to measure these pressures, there is no need for a pressure gauge. Use a water manometer. A water manometer is a piece of clear plastic tubing, bent into a U-shape, and with some water in it. The pressure is the difference in water height between the two sides of the U, and is measured with a ruler.

Velocity pressure can be calculated from the Bernoulli equation, but an easier method used in HVAC work is Velocity pressure = (Velocity in FPM / 4005)^2. The velocity pressure is 1.0" w.c. at 4005 FPM (feet per minute), and is proportional to the velocity squared.

Thats very helpful thank you! so seems i will have to go with a centrifugal fan to get that pressure up. I will be placing a barometric pressure sensor in the tube after the van so that i can get an idea of the flow rate
 
  • #11
jrmichler said:
If you have a size reduction at the beginning, add in the velocity pressure for the entrance loss. The velocity pressure for the same conditions is 0.09" w.c., and the total fan pressure needed is the sum of the velocity pressure and the duct friction loss. The total fan static pressure needed to push 15 CFM through your 1.5" duct is thus 0.1 + 0.09 = 0.19" w.c.

I understand the Friction Head Loss in Air Ducts - Online Calculator provided .0979 with those parameters, and so i see how you got 0.1, but i don't understand where you got the 0.9 from. I don't understand the size reduction at the begging part you mentioned.

I also tried looking up velocity pressure as you mentioned but didn't find much, is that the same as dynamic pressure?
 
  • #12
Velocity and dynamic pressure are two names for the same thing. The Wikipedia entry for dynamic pressure has a good explanation: https://en.wikipedia.org/wiki/Dynamic_pressure. The Wikipedia article has a nice diagram in it. When you transition from a large duct to a small duct, the air speeds up. It takes pressure to make the air speed up. That pressure is in addition to the friction loss in the duct.

Here is a blower that would deliver 15 CFM through your 1.5" duct:
Blower.jpg
It was found in a quick search in Digikey. It is rated for 12 volts, draws 4 watts of power, and costs $18.00 plus shipping. Since the blower outlet is about the same size as your duct, the velocity pressure loss would be negligible, and you would need only a simple transition piece to connect it to the duct. There's more information in the datasheet: https://www.delta-fan.com/Download/Spec/BFB0712HH-A.pdf. It's not the only blower available, it's the first one I found in a quick search. Digikey is not the only supplier to check, Newark and Mouser may also have blowers.
 

Similar threads

  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
3
Views
3K
Replies
3
Views
2K
  • · Replies 14 ·
Replies
14
Views
2K
Replies
5
Views
3K
  • · Replies 29 ·
Replies
29
Views
4K
Replies
6
Views
4K
Replies
4
Views
4K
Replies
6
Views
6K