Calculating cost to heat house using R-values

  • Thread starter Thread starter nerdy_hottie
  • Start date Start date
  • Tags Tags
    Heat
AI Thread Summary
The discussion focuses on calculating the monthly heating cost for a flat-roofed house using R-values for insulation. The house dimensions and R-values for walls and roof materials are provided, along with indoor and outdoor temperature averages. The heating power (P) is calculated using the formula P=(1/R)*A/ΔT, leading to a total heat loss of 2,803,968 Btu over 30 days. The final cost is derived by converting Btu to gallons of oil and multiplying by the cost per gallon, resulting in a monthly heating expense of approximately $112.16. A correction is noted regarding the inclusion of both walls in the calculations.
nerdy_hottie
Messages
19
Reaction score
0

Homework Statement



Consider a flat roofed rectangular house that is 10.0 feet high with 39.0 feet long sidewalls and 20.0 feet long front and back walls.

We are given that:
Wall: (R Value =0.20 plaster)+(R Value=10.00 insulation)+(R Value=0.60 plywood)+(R Value=0.50 cedar shingles).
Roof: Same as walls except R Value=31.00 insulation.
All R values are in units of ft2*oF*hr/Btu

If average winter indoor and outdoor temperatures are 69.0oF and 18.0oF respectively and the furnace produces 105 Btu/gal of oil at $4/gal, what is the monthly heating cost in dollars? (Use 30 days/month and Do not enter units)

Homework Equations



P=(1/R)*A*/\T

The Attempt at a Solution



P=(1/Rfront wall, back wall)/\T*(Afront wall+Aback wall)+(1/Rroof)*/\T*Aroof
=3894.4 Btu/hr
multiply by 24 hours, then by 30 days=2803968 Btu
Divide by 10^5 Btu/gal
multiply by $4/gal
=112.16
 
Physics news on Phys.org
nerdy_hottie said:
=3894.4 Btu/hr
I think you've counted only one wall in each direction instead of a pair.
 
I multiplied the values first without the error limit. Got 19.38. rounded it off to 2 significant figures since the given data has 2 significant figures. So = 19. For error I used the above formula. It comes out about 1.48. Now my question is. Should I write the answer as 19±1.5 (rounding 1.48 to 2 significant figures) OR should I write it as 19±1. So in short, should the error have same number of significant figures as the mean value or should it have the same number of decimal places as...
Thread 'A cylinder connected to a hanging mass'
Let's declare that for the cylinder, mass = M = 10 kg Radius = R = 4 m For the wall and the floor, Friction coeff = ##\mu## = 0.5 For the hanging mass, mass = m = 11 kg First, we divide the force according to their respective plane (x and y thing, correct me if I'm wrong) and according to which, cylinder or the hanging mass, they're working on. Force on the hanging mass $$mg - T = ma$$ Force(Cylinder) on y $$N_f + f_w - Mg = 0$$ Force(Cylinder) on x $$T + f_f - N_w = Ma$$ There's also...