Calculating Temp Loss for Mixing Water Streams

  • Thread starter Thread starter cweed
  • Start date Start date
  • Tags Tags
    Formula
AI Thread Summary
To calculate the temperature loss when mixing two water streams, use the weighted average of their temperatures based on their flow rates. The smaller stream flows at 2,400 gph at 85°F, while the larger stream flows at 37,000 gph at 105°F. A mass and energy balance equation is necessary to determine the final temperature, which involves calculating the enthalpy of each stream. Ensure that the inlet temperatures are below the saturation temperature for accurate results. Once the enthalpy is calculated, refer to a steam table or database like REFPROP to find the corresponding exit temperature.
cweed
Messages
2
Reaction score
0
I am working to determine what the temperature loss (minimal at best) would be by mixing a stream of water flowing at 2,400 gph at 85 degree (f) into another stream of water flowing at 37,000 gph. Any help would be great
 
Engineering news on Phys.org
Do you mean you just need the final temperature of the mixture? That would be a weighted average of the two stream temperatures.
 
Yes the final temperature of the two stream the one at flowing 2,400 gph is 85 (f) and the one flowing at 37,000 gph is 105 (F).
 
cweed said:
Yes the final temperature of the two stream the one at flowing 2,400 gph is 85 (f) and the one flowing at 37,000 gph is 105 (F).

This would be a typical mixing chamber type problem, but you'll need to know the pressure. The mass and energy balance yields:

h_3 = \frac{\dot{m_1}h_1 + \dot{m_2}h_2}{\dot{m_1} + \dot{m_2}}

The m_dots with subs 1 and 2 are the respective mass flow rates coming into the mixing chamber. The h's are the respective enthalpies. They can be looked up in a steam table based on the inlet temperatures. This assumes of course that the inlet temperatures are below the saturation temperature of water at the specified pressure (i.e. it is in the compressed liquid state). Assuming that criterion is satisfied, the enthalpy of a compressed liquid can be approximated as a saturated liquid at the given temperature.

Once you have the enthalpy at the exit (h_3) you can look up the corresponding temperature in a steam table (or REFPROP if you have that database). If the exact enthalpy doesn't appear in your table you can interpolate and get a reasonable answer (depending on what accuracy you want).

Hope that helps.

CS
 
Thread 'Where is my curb stop?'
My water meter is submerged under water for about 95% of the year. Today I took a photograph of the inside of my water meter box because today is one of the rare days that my water meter is not submerged in water. Here is the photograph that I took of my water meter with the cover on: Here is a photograph I took of my water meter with the cover off: I edited the photograph to draw a red circle around a knob on my water meter. Is that knob that I drew a red circle around my meter...
Hi all, i have some questions about the tesla turbine: is a tesla turbine more efficient than a steam engine or a stirling engine ? about the discs of the tesla turbine warping because of the high speed rotations; does running the engine on a lower speed solve that or will the discs warp anyway after time ? what is the difference in efficiency between the tesla turbine running at high speed and running it at a lower speed ( as fast as possible but low enough to not warp de discs) and: i...