Can I Combine 50A and 30A Outputs on My Portable Generator?

  • Thread starter Thread starter crankybob
  • Start date Start date
  • Tags Tags
    Generator Home
Click For Summary

Discussion Overview

The discussion revolves around the feasibility and safety of combining the outputs of a 50A and a 30A connector from a portable generator to achieve a total output of 80A for home use. Participants explore electrical connections, circuit breakers, and safety considerations related to this setup.

Discussion Character

  • Debate/contested
  • Technical explanation
  • Conceptual clarification

Main Points Raised

  • One participant plans to connect both the 50A and 30A outputs to a transfer box to utilize the full 80A capacity of the generator.
  • Another participant suggests that if the breakers connect to the same power feed, the 30A breaker may trip first under load, potentially leading to issues.
  • Concerns are raised about the safety of paralleling overcurrent protection devices, as it may lead to unequal current sharing and cascading failures.
  • A participant mentions the possibility of combining the lines from two 240V outlets into one to connect to an 80A breaker.
  • There is a discussion about the generator's specifications, including its total output and the need for proper grounding and bonding if permanently mounted.
  • One participant notes that the generator is rated at 15kW with a surge rating of 22.5kW, and considers using a 70A breaker instead of 80A for safety.
  • Another participant questions the necessity of an 80A circuit in typical household applications, suggesting that most circuits are rated for lower amperages.

Areas of Agreement / Disagreement

Participants express differing opinions on the safety and practicality of combining the outputs. Some participants caution against the approach, while others explore potential solutions without reaching a consensus on the best method.

Contextual Notes

Participants mention the need for proper electrical codes and safety measures, including the importance of interlocks in transfer switches to prevent backfeeding into the power grid. There are also references to the generator's wiring and the implications of modifying its setup.

Who May Find This Useful

This discussion may be of interest to individuals considering the use of portable generators for home power, electricians, and those involved in electrical installations or modifications.

crankybob
Messages
10
Reaction score
0
I have a portable generator for my home. it puts out a total of 80 amps at 240v with no problem. what it does not have is a single 80 amp connector. I have a 50amp and a 30 amp. my plan is to connect these both to the CB in the transfer box to attain the full 80 amps to my home. a local "electrician " recommended against this, but had no alternative method. I know parallel circuits have equal voltage and their own amperage. the power is all coming from a single source. am I wrong about this connection.
 
Engineering news on Phys.org
If you assume the breakers in the generator connect to the same power feed point, at the full 80 amp draw to the same load in parallel through those breakers it's likely the 30amp breaker will trip first if the current flows equally (40/40) in the connections from the generator, then the 50amp breaker will trip when it has the full 80amp current load.
 
trough 30 A connector you will have 40 A current, this is not good idea.
 
so I need to form a single output line to connect directly to my 80amp transfer box breaker.
 
Do you have a wiring diagram of your generator? I'm wondering whether it might be feasible to replace the two breakers with a single breaker of 80A ?

Is the generator for emergency use, or routine use?
 
Last edited:
no diagram. that's my big problem. it has a large panel with a total of 8 outlets, each with their own CB. 3 are 240v, the rest 120v. suppose I could just combine the lines to the 2 240v outlets into one. and use my 80 amp CB in line to the transfer box. long time since I did electrical work. was electronics/electrician in air force about 42 years ago.
 
It would be worth trying a google search, using its brand and model number, to see what you can find out about its internals.
 
This is a bad idea.
 
Averagesupernova said:
This is a bad idea.

Agreed.

It is not good practice to parallel overcurrent protection devices . That's because it is difficult to make them share current equally. When one of them opens its current is shifted to the others which overloads them and they all open in a cascade . You gain no reliability and probably lose some. Weakest link opens first which causes the rest to follow.

Also - what did you intend to use for a connector? Biggest NEMA plug i can find is sixty amps, NEMA14.
http://www.generalcable.com/NR/rdon...F60-9E22-4CC19C14F343/0/Pg9698_NEMA_Chart.pdf
 
  • #10
I was hoping to wire directly into a CB . this is a portable generator which I am permanently mounting in a shed next to the transfer box. I will search for a diagram. thanks for the input.
 
  • #11
80 amps at 240 volts is 19.2 KW. That is an unusually large portable generator.

Does your transfer switch disconnect the normal service when the generator is connected to the panel? It should and I suspect the connection will require a permit and inspection.
 
  • #12
crankybob said:
I was hoping to wire directly into a CB . this is a portable generator which I am permanently mounting in a shed next to the transfer box. I will search for a diagram. thanks for the input.

That might work. Your electrician friend can help you find the big wires inside it and you could put a two pole breaker in it.
Be aware that wiring it in that way makes it a "separately Derived Source" under the code and i think no longer a "Portable Generator". Your electrician friend can help you get it grounded, bonded, and be sure the disconnecting means is appropriate per code..

You want this done properly and per electrical code.
I trust the transfer box is physically interlocked so you cannot backfeed into the power company .
Improper(therefore illegal) backfeeds electrocute several innocent linemen in the South every hurricane season and the homeowner is directly at fault .

Please do it right.

old jim
 
  • #13
the transfer box was installed by my local REC when they hooked up my meter to the house. it has an interlock that prevents generator from being on without turning off incoming power. I found the wiring diagram. all power goes into a 50 amp breaker, then passed on to the multiple 20 and 30 amp breakers. the generator is rated at 15kw with a surge rating of 22.5kw. I will most likely settle for a 70amp breaker to keep it down.
 
  • #14
There's a good article here
http://www.google.com/url?sa=t&rct=...=0kLEJe-A9kdXwv4y3NZvng&bvm=bv.74649129,d.b2U

looks like i was wrong about the generator being "separately derived". So long as your transfer switch doesn't switch the neutral wire you're okay. Good drawings in that link.

Glad to know you're doing it right.

15KW at 240 volts is 62.5 amps, divide that by generator's nameplate power factor probably around 0.8 to 0.9

15KW is 20.1 horsepower. Ventilate the shed well.

Good luck !

old jim
 
  • #15
has 30hp engine on it. plan to run exhaust to outside. transfer uses only 2 hot wires. both grounds are separate and not involved.
 
  • #16
Usually, there are few things in a household which require a dedicated 80 A circuit. IDK about 240V houses in Europe, but in the US (with 110V electricity), most home circuit outlets are wired for about 20 A max. A few appliances requiring larger current draws (like central A/C, clothes driers, and hot water heaters) are wired to special circuits which can accommodate their special electrical needs, including higher voltage.
 
  • #17
crankybob said:
I found the wiring diagram. all power goes into a 50 amp breaker

Could it be two 50 amp breakers with one wire into and out of each? If so it would seem you are all set!
 
  • #18
double pole 50A with 2 wires going in and 2 coming out. wires out feed a single 50A receptacle. wires going in travel on to 1 30A 240V, 2 30A 120V, and 4 20A 120V receptacles.50A is separate from the others. so the input to the 50A and the 30A could combine to give me 80A but I am not a pig. 70A will do,
 

Similar threads

Replies
61
Views
10K
Replies
9
Views
8K
  • · Replies 4 ·
Replies
4
Views
3K
Replies
4
Views
3K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
Replies
1
Views
4K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 16 ·
Replies
16
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K