Causes of Transformer Explosion in 152 Hectares University Campus

AI Thread Summary
Transformer explosions on the university campus may be caused by factors beyond overloading, including degradation of insulation and oil due to high temperatures, leading to leakage currents and potential short circuits. Monitoring the chemical composition of transformer oil is essential to detect breakdown products that indicate internal issues. The primary side of the transformers should be examined for neutral current and potential overloads from third harmonic currents, particularly if connected in a WYE-DELTA configuration. Additionally, the age of the transformers, changes in load nature, and environmental factors like lightning strikes should be considered as possible contributors to the failures. Engaging a professional testing service to assess the transformers and switchgear is recommended for a thorough evaluation.
young e.
Messages
64
Reaction score
0
hi pf folks..

currently i am the electrical engineer incharge in a 152 hectares university campus in our place. commonly our transformer are rated 7620/240 volts, 1p with capacity of 25 KVA, 50 KVA and 100 KVA.. for our three phase loads we used to bank 3- 1p transformer
wye delta...all in all we have a total of 8 transformer substation in our campus.. now few months past we experienced succesive transformer explosion in our campus in different substations, we check the secondary line there's no fault in it,,, being a neophyte in this field of practice (electrical engg.) now my question is:

1. aside from overloading, what are the other causes of transformer explosions?

2. i suspect that the succesive explosion came from the primary side since we had already made an investigation in all of our loads and secondary lines, and we found that everything is all right, now what are the factors affecting transformer explosion with regards to the primary side..

tnx in advance!

:smile: young engineer
 
Engineering news on Phys.org
Just some background information since it's not my speciality.
There is always some leakage current between the winding layers. Over time, and especially with high internal temperature, both the insulation and oil fill degrade and become slightly conductive. This of course increases the leakage currents a little. Eventually the insulation becomes carbonized and rather conductive, then you are on the way to a run-away short circuit and explosion if there ar not any fuses in the primary circuit.

To monitor the internal conditions, a chemical analysis of the oil is periodically done to check for breakdown by-products.

Others here, perhaps @jim hardy or @anorlunda, may have more details.

Cheers,
Tom
 
  • Like
Likes Asymptotic
Monitoring oil is a must.

Are primaries 4 wire connected? In other words, is there a neutral wire?
If so,
Measure the neutral current on WYE side.

Why do i say that ?
It is possible to overload a (4 wire WYE)-DELTA connected transformer with third harmonic current by powering it from a much larger source that has just a few % third harmonic content in its voltage .

Look up "Zero Sequence Current".

old jim
 
  • Like
Likes Asymptotic
Given that they have been providing trouble-free service until just recently.

1. Has the nature of their loads changed?
Has anything unusual (an earthquake, etc.) happened?

2. How old are the transformers?
Date of manufacture will be on their nameplates. If they were all installed at about the same time, and are closing in on expected service life that could explain the rash of failures.

3. Is your area particularly prone to lightning strikes?
Metal oxide, and/or spark gap arresters are popular for transformer/switchgear protection. MO arresters can fail shorted (which is hard to ignore - loud explosion, and likely to take out the primary fuse), but they may also fail open, which isn't easily detectable (special tests are required), and afterward, provides no lightning and surge protection.

A good course of action is look into transformer and switchgear testing services in your area, and have a reputable firm assess your equipment.
 
Others mentioned oil. That is the first place to look.

High harmonic content can also cause transformer explosions. Especially if you had several in the same area during the same period, I would check harmonics.

An arc furnace in a steel recycling plant can be a big source of harmonics.
 
  • Like
Likes jim hardy
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...