Transformer explosions on the university campus may be caused by factors beyond overloading, including degradation of insulation and oil due to high temperatures, leading to leakage currents and potential short circuits. Monitoring the chemical composition of transformer oil is essential to detect breakdown products that indicate internal issues. The primary side of the transformers should be examined for neutral current and potential overloads from third harmonic currents, particularly if connected in a WYE-DELTA configuration. Additionally, the age of the transformers, changes in load nature, and environmental factors like lightning strikes should be considered as possible contributors to the failures. Engaging a professional testing service to assess the transformers and switchgear is recommended for a thorough evaluation.
young e.
Messages
64
Reaction score
0
hi pf folks..

currently i am the electrical engineer incharge in a 152 hectares university campus in our place. commonly our transformer are rated 7620/240 volts, 1p with capacity of 25 KVA, 50 KVA and 100 KVA.. for our three phase loads we used to bank 3- 1p transformer
wye delta...all in all we have a total of 8 transformer substation in our campus.. now few months past we experienced succesive transformer explosion in our campus in different substations, we check the secondary line there's no fault in it,,, being a neophyte in this field of practice (electrical engg.) now my question is:

1. aside from overloading, what are the other causes of transformer explosions?

2. i suspect that the succesive explosion came from the primary side since we had already made an investigation in all of our loads and secondary lines, and we found that everything is all right, now what are the factors affecting transformer explosion with regards to the primary side..

tnx in advance!

:smile: young engineer
 
Engineering news on Phys.org
Just some background information since it's not my speciality.
There is always some leakage current between the winding layers. Over time, and especially with high internal temperature, both the insulation and oil fill degrade and become slightly conductive. This of course increases the leakage currents a little. Eventually the insulation becomes carbonized and rather conductive, then you are on the way to a run-away short circuit and explosion if there ar not any fuses in the primary circuit.

To monitor the internal conditions, a chemical analysis of the oil is periodically done to check for breakdown by-products.

Others here, perhaps @jim hardy or @anorlunda, may have more details.

Cheers,
Tom
 
  • Like
Likes Asymptotic
Monitoring oil is a must.

Are primaries 4 wire connected? In other words, is there a neutral wire?
If so,
Measure the neutral current on WYE side.

Why do i say that ?
It is possible to overload a (4 wire WYE)-DELTA connected transformer with third harmonic current by powering it from a much larger source that has just a few % third harmonic content in its voltage .

Look up "Zero Sequence Current".

old jim
 
  • Like
Likes Asymptotic
Given that they have been providing trouble-free service until just recently.

1. Has the nature of their loads changed?
Has anything unusual (an earthquake, etc.) happened?

2. How old are the transformers?
Date of manufacture will be on their nameplates. If they were all installed at about the same time, and are closing in on expected service life that could explain the rash of failures.

3. Is your area particularly prone to lightning strikes?
Metal oxide, and/or spark gap arresters are popular for transformer/switchgear protection. MO arresters can fail shorted (which is hard to ignore - loud explosion, and likely to take out the primary fuse), but they may also fail open, which isn't easily detectable (special tests are required), and afterward, provides no lightning and surge protection.

A good course of action is look into transformer and switchgear testing services in your area, and have a reputable firm assess your equipment.
 
Others mentioned oil. That is the first place to look.

High harmonic content can also cause transformer explosions. Especially if you had several in the same area during the same period, I would check harmonics.

An arc furnace in a steel recycling plant can be a big source of harmonics.
 
  • Like
Likes jim hardy
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top