Conductor size and Voltage Drop for Design
The discussion centers on selecting the appropriate conductor size for a 300Hp electric motor installation, focusing on voltage drop calculations over a distance of 700 feet. Participants explore various factors influencing conductor selection, including material type, environmental conditions, and compliance with NEC standards.
  • One participant identifies the full load current of the motor as 361A and seeks assistance in determining the appropriate copper conductor size.
  • Another participant emphasizes that conductor selection depends on various factors such as location, temperature rise, and installation method, referencing NEC guidelines.
  • A suggestion is made that 400kcmil may be the minimum conductor size, but the environment's saltwater exposure raises concerns about corrosion, leading to a preference for aluminum conduit.
  • Concerns are raised about the compatibility of aluminum with saltwater, with a recommendation for PVC conduit instead.
  • One participant suggests that using a larger conductor size, like 500MCM, may be beneficial, especially for starting large motors, despite the difficulty of pulling such large cables.
  • A warning is issued regarding the use of iron conduit fittings with high current AC conductors, highlighting potential heating issues due to magnetic fields.
  • Another participant questions the difference in voltage drop between 400MCM and 500MCM conductors and whether both would meet NEC requirements.
  • A calculation is provided for the voltage drop using 500MCM, indicating a drop of just over 1% for the specified distance and current.
Participants express differing opinions on the best conductor size and material, with no consensus reached on the ideal solution. Concerns about corrosion and installation challenges are acknowledged, but specific recommendations vary.
Participants note the importance of considering both thermal limits and voltage drop in conductor selection, indicating that the long run may present unique challenges. The discussion reflects various assumptions about environmental conditions and installation practices.
Dwa
If specs on a 300Hp electric motor;
480 Volts
3 Phase
60Hz
The full load Amps of the motor is 361A, which I found in the NEC table. My distance is 700ft to a control center and I can't seem to figure out what copper conductor size to use. In order to find the Voltage drop I have to know the CM, I assume. Can anyone help me with my design?
Time for an electrician - the conductor (cable) selection depends on, location, temp rise, how is it run (Conduit, Raceway, underground - etc). This is in the NEC - but available from a number of places online ( http://sparkyjohn.com/ampacity/ampacity.pdf )
The cable is selected to ensure it does not overheat.
Then once the cable is selected you can find the V drop along A length V = Res ( Ohm/foot * 700Ft) * I current. Noting that the voltage at the load has 2 x the voltage drop of on length ( in 3 wire this is not totally accurate but will suffice)
I would also say - the Generator should have a Circut Breaker - at the generator. The cable really needs to be sized based on the breaker rating and or setting - not the generator.
If the load is known, for example a 200A panel, you may also be able to economized by using a smaller breaker at the generator and running a smaller cable.
Since an error in this system can cause a fire (that is why the NEC in part of the Nat Fire Protection Assn) - I refer back to my first line.
Ok, from some Voltage Drop online calculators said 400kcmil would be the minimum conductor size to use in a conduit. Would that be the right ideal? The environment near saltwater, so I'm using Aluminum conduit for no corrosion.
Thanks
Umm - Aluminum and Salt water not a good combo, PVC would be better if you can get it to withstand the cable pull -
Per the NEC - 3 conductors in a conduit, 400MCM is an odd size, you may have better luck with the 500MCM (kcmil) - if you can afford the wire a size larger is often a good idea, espically if you will be starting large motors / high load.
Pulling 4 x 500MCM - in anything - is HARD - again, I refer back to a pro. I am EE with 15 years hands on service of electrical switchgear (480VAC up) - and I would PAY for a union electrician to do this out of my own pocket before I would try to tackle the job.
should be plenty of Ampacity charts from wire suppliers.
On a run that long check voltage drop it may be more limiting than thermal.
http://www.fs.fed.us/database/acad/elec/greenbook/3_basicdesigns.pdf
just a tip -
Beware of iron conduit fittings around high current AC conductors.
If you use any be sure all 3 phases go through same fitting.
Magnetic field around a single phase carrying hundreds of amps can heat a closed iron loop that surrounds the conductor. It makes a 60 hz induction heater.
If all 3 phases go through, currents add to zero of course.
We had trouble with iron conduit elbows in a big run buried under concrete... contractor had run out of PVC ells.
Yes, I do agree that Al is not a good combo, put it's at least can withstand the cable pull. Or maybe steel could be better, but corrosion is worse in that matter. I'm thinking 500MCM could be a better choice. Do you think it wouldn’t make any much difference though between the two sizes? I mean you have lesser Voltage load at the end of the circuit or wire. Heck, will the voltage drop for 400MCM-500MCM or above still meet NEC? You're right though; regardless to pull any wire size like that is unimaginable lol...
Thanks for pdf Jim H, helped me get a better idea.
http://www.pearen.ca/Reference/wire.htm
shows 0.00002074 ohms/ft for 500mcm
which X 700 ft X 360 amps = 5.24 volts drop, just over 1%
  • · Replies 31 ·
  • · Replies 26 ·
  • · Replies 34 ·
10K