Cost Implications Of Low Power Factor

AI Thread Summary
Calculating the cost of operating without power factor correction (PFC) involves understanding the uncorrected power factor and its impact on utility charges. The facility's load is constant at 2.5MW, but without PFC, the utility may charge for excess demand based on the maximum KVA demand, potentially increasing costs significantly. Utilities typically have a threshold for distribution demand charges, and dropping below this can incur additional fees. The increase in kVAr charges due to the PFC being off should be reflected in the next utility bill, providing documentation for an insurance claim. Installing a kVAr meter could help in accurately measuring the impact of the PFC outage.
BIGEYE
Messages
20
Reaction score
0
We operate a 3 phase, 11kV network with automatic power factor correction equipment installed. Over the last four weeks we have had the PFC switched off due to an electrical incident.
How can I calculate the cost of running without PFC for this period of time, our load is fairly constant at around 2.5MW. Our manager wants to include the increased electricity cost on the insurance claim due to operating without PFC.

TIA
 
Engineering news on Phys.org
A power meter that can measure power factor? Something from Fluke (345B), http://www.amprobe.com/cgi-bin/pdc/searchprod.cgi?category=195&type=elec&tid=1&action=search", or your favourite instrumentation supplier.
 
Last edited by a moderator:
Background:
To see this from the Utility's point of view, remember what your uncorrected load is doing: forcing the Utility to supply you surplus current for the same power draw. This doesn't immediately cost them anything, unless it happens to force them to up the current rating of their distribution equipment in the locale of your facility.

Details:
You should have some idea of the uncorrected power factor from the rating on the correction equipment installed. The cost, if any, will depend on the particular utility. Typically total cost is broken down into Distribution Demand in kw (power rating of the distribution to your facility) and another part reflecting actual energy supplied. Dominion Power for instance has an http://www.dom.com/customer/pdf/va/vab8.pdf" Stay above that and there's no penalty. Drop below it and for your Distribution Demand cost, they charge a minimum of 85% of your maximum KVA demand. If your facility's max VA demand peaks up to, say, 3000 KVA, they may charge you for 2.55MW worth of distribution regardless of actual load. If your utility invokes such a trigger it will be no doubt be reflected in the next bill as a new floor for your 'Distribution Demand' as it is called with the supply portion remaining at the 2.5MW average. The cost difference between that bill and earlier ones, with the reason indicated on the utility bill, should be easy to demonstrate for your insurer.
 
Last edited by a moderator:
I have managed to get a look at earlier bills and there is a charge for kVAr, it varies quite a bit, but I'm expecting a big jump due to PFC being turned off. I am thinking along the correct lines?
 
Yes, you are. The purpose of the power factor correction is to reduce the kVAr.
 
Would there be a way to install a kvar-hr meter?
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...