Current Transformer Accuracy Under %5 Load Level

AI Thread Summary
Current transformers (CTs) exhibit varying accuracy based on load levels, with manufacturers providing specifications primarily for loads above 5%. Below this threshold, accuracy can be uncertain, leading to potential readings of 0.00mA in the secondary circuit when primary currents are low, such as 50A in a 4000/5A CT. Some manufacturers label this as an "unstable zone," indicating that performance may not be guaranteed. Special accuracy classes (0.2S and 0.5S) have lower limitations of 1%, but conventional classes maintain a 5% threshold. Additionally, low burden conditions can also contribute to accuracy loss, raising concerns about the reliability of readings in such scenarios.
HakanEryurt
Messages
2
Reaction score
0
Hello , I would like to ask one question. Current transformers has one of the major component in electricity but we know that per load level, VA, temperature ext accuracy of these transformers can change. CT manufacturers gives accuracy diagrams for different load levels from %5 load to full load. But what is happening when the load level is lower than %5. For example if you have 4000/5 current transformer to measure current and if you have load that can go down for sometime to 50A in primary, is it possible that you can have 0.00mA in secondary?

Some CT manufacturers written specs as <%5 zone unstable zone, where there is no value for accuracy or there is no warranty that CT's are working probably. Is there any technical study that investigate <%5 load conditions?
 
Engineering news on Phys.org
Yes, for conventional measuring transformers with accuracy class of 0.1, 0.2, 0.5,1,3 and 5 this limitation is %5 but for special current transformers with accuracy class of 0.2S and 0.5S this limitation is %1. Error limits for measuring current transformer cores is defined by DIN VDE 0414-1 and IEC 60185

For Measuring core rated output: 2.5 – 5.0 – 10 – 15 – 30 VA; burden output factor = 0.8

Classes: 0.1 – 0.2 – 0.5 – 1: valid in the range of 25 % and 100 % of the rated burden.
Classes: 0.2 s and 0.5 s: For special applications (electrical meters that measure correctly between 50 mA and 6 A, i.e. between 1% and 120% of the rated current of 5A)
Classes: 3 – 5: valid in the range 50% to 100% of the rated burden Label: measuring cores are identified by a combination of the rated output with the overcurrent limit factor and with the class, e.g.

15 VA class 0.5 FS 10
15 VA class 0.5 ext. 150%

-----------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Thank you for your answer. So if you have Class 0.5 current transformer for reactive power compansation, and if utility has 0.5s current tranformer for billing your compansation will not work properly and you can be charged for reactive energy.

But I need to understand why we read 0.00mA or very less current compared to primer in current transformer when there is 50A primer current in 4000/5A current transformer. Where are we loosing this secondary current?

As far as I understood these classes are specified in maximum burden. So my second question is if have a CT of 30VA burden and if we have load of max 0.3VA . Is there any accuracy loss also due to low burden?
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...