  • One participant questions the rationale behind placing positive polarity at the top and negative at the bottom of circuit diagrams, suggesting it may be a habitual practice.
  • Another participant notes that while there are no strict standards, the convention likely stems from the association of the bottom with ground or return paths.
  • A different viewpoint emphasizes that this arrangement is a modern convention, with older configurations sometimes placing ground at the top, which can lead to confusion.
  • One participant mentions that electrical equipment is typically shown at the bottom of pages to maintain a continuous negative connection, which helps prevent corrosion in outdoor installations.
  • There is a mention of split supplies and how they might affect the placement of ground in the middle of the page, along with a personal anecdote about using circuit diagrams as a recruiting question.

Areas of Agreement / Disagreement

Participants express varying opinions on the conventions of polarity arrangement in circuit diagrams. While some agree on the modern convention of placing positive at the top, others highlight the lack of strict standards and the potential for confusion if the convention is altered. The discussion remains unresolved regarding the necessity or benefits of changing these established norms.

Contextual Notes

Participants acknowledge that the conventions may depend on specific applications and historical practices, and there are no universally accepted standards governing these arrangements.

m.s.j
Messages
212
Reaction score
1
Control and protection electrical circuits are one of the important portions of electrical systems designed and shown by standard symbols.
Usually the circuit is supplied by positive and negative polarity of one battery. In almost electrical circuit diagram sheets we can see a positive line of DC polarity in top of sheet and negative line in bottom of sheet that is purposed to supply electrical equipment of circuit.

How can you explain that polarity arrangement? Why the negative polarity is usually located in bottom and positive polarity in top of sheets?
Is it habit activity in drawing circuits or not? If all used electrical equipments, for example auxiliary relays, open and close coil of power circuit breakers and so on could be activated by inverse polarity, would we change that mentioned norm, and use negative in top of sheets and positive polarity in bottom, without any circuit configuration changing.

REGARDS
MSJ

--------------------------------------------------------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 

Attachments

  • 7.GIF
    7.GIF
    1.8 KB · Views: 612
Engineering news on Phys.org
i'm not aware of any standard maybe guidelines?

you can draw anyway you want. i think most of the time people associate the bottom as gnd or return path. if you feel more comfortable with negative on top then sure, but others may be confused and so would you if you get used to that while 99.9% of everyone else does the other way
 
Mainly it's just the modern convention. There are some older circuit configurations where there would be some nodes that had ground near the top, but those are confusing to decipher, now that the convention you mention is the norm. Usually, the more positive supplies are near the top, and more negative supplies are at the bottom of the circuit and page. If there are split supplies (like +/-12V), and some symmetry in the circuit, ground will be near the middle of the page. It is also generally a convention that inputs come in the left side of the page, and go out the right side of the page, although this is not always possible with all circuit diagrams.
 
Generally electrical equipment that used in auxiliary control systems shown in bottom of pages. Therefore equipment (relay etc.) that usually installed in field area is directly connected to one of two polarity continuously, and other polarity connected to the other terminal of equipment via auxiliary contact of controller devices that shown on top of pages transitionally.
Continuous connection must be negative, to prevent corrosion of equipment due to electrolytic action, because they usually installed in outdoor and corrosive area.
Of course this recommendation related to battery system grounding way.



REGARDS
MSJ

-------------------------------------------------------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
berkeman said:
If there are split supplies (like +/-12V), and some symmetry in the circuit, ground will be near the middle of the page.

I use this ask an introductory recruiting question. I draw a transistor with biasing resistors with the same value and Vcc = 10V and Vee = -10V and I ask them what the voltage is at the base.

So far only one person has been able to tell me by just inspection.
 

Similar threads

  • · Replies 25 ·
Replies
25
Views
6K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 31 ·
2
Replies
31
Views
5K
  • · Replies 12 ·
Replies
12
Views
17K
Replies
1
Views
2K
  • · Replies 16 ·
Replies
16
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 14 ·
Replies
14
Views
4K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 4 ·
Replies
4
Views
6K