Does the Order of Voltage Transformation Affect AC Power Supply Output?

AI Thread Summary
The order of voltage transformation does affect the performance of an AC power supply. It is recommended to use the stepdown transformer first, followed by the variac, to ensure better regulation and stability. Stepping down voltage increases current, which can lead to voltage drops in the transformer windings, particularly at lower output voltages. Using the variac first could result in less effective regulation due to higher current handling. The discussion concludes with the user successfully measuring stable output after following the suggested order.
AndrewBourhis
Messages
29
Reaction score
0
Hi all,
I need to create an adjustable power supply (AC) that ranges from 0-6 volts with roughly 1 ampere at 1 volt. I have a variac transformer (0-130 volts), an isolation transformer and a stepdown transformer. My question is, does it matter what order I step the voltage down? In other words, could I keep the variac in front of the stepdown transformer, and vary the input voltage of the stepdown transformer? Or should I step it down first then use the variac (even though the input voltage is rated at 120 v...)

Or does it not matter at all?

Thanks,
-Andrew
 
Engineering news on Phys.org
You can fine-adjust the amplitude of the AC wave using a resistor or potentiometer. You are using a variable transformer though. The relationship between voltage and current depends on the load - you cannot just supply a fixed voltage and current.

For your question - which order you step down will affect the performance ... but you should certainly step down first, and then use the variac. It may be rated at 120V, but what about spikes? Put the highest rated transformer first.
 
AndrewBourhis said:
Hi all,
I need to create an adjustable power supply (AC) that ranges from 0-6 volts with roughly 1 ampere at 1 volt.

Does that mean it'll be 6 amps at 6 volts?

I have a variac transformer (0-130 volts), an isolation transformer and a stepdown transformer. My question is, does it matter what order I step the voltage down? In other words, could I keep the variac in front of the stepdown transformer, and vary the input voltage of the stepdown transformer? Or should I step it down first then use the variac (even though the input voltage is rated at 120 v...)

Or does it not matter at all?

Thanks,
-Andrew

You already know the answer.
As you step voltage down you step current up. The voltage drop in your transformer windings is in proportion to current, it'll amount to a few percent of nameplate volts at nameplate amps..

What is the current rating of your variac? Probably it'll have a volt or two drop at nameplate amps and max setting. That's not bothersome at 130 volts out, but it sure could be at 6 volts out.

Placing variac first will give you better regulation out of it because it'll be handling less current.
old jim
 
Last edited:
  • Like
Likes 1 person
jim hardy said:
You already know the answer.
As you step voltage down you step current up. The voltage drop in your transformer windings is in proportion to current, it'll amount to a few percent of nameplate volts at nameplate amps..

What is the current rating of your variac? Probably it'll have a volt or two drop at nameplate amps and max setting. That's not bothersome at 130 volts out, but it sure could be at 6 volts out.

Placing variac first will give you better regulation out of it because it'll be handling less current.



old jim


Great, I measured the output of using the variac first, and it was fairly stable. Now I need to rectify this into a DC...

Thanks for the help
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...