Effect of AC powerlines on nearby pipeline

  • Thread starter Thread starter mrmojorizing
  • Start date Start date
  • Tags Tags
    Ac
AI Thread Summary
High voltage overhead AC power lines can influence nearby steel pipelines through magnetic induction, conduction during faults, and capacitive effects. The dielectric coating on pipelines helps prevent corrosion but does not eliminate the potential for induced voltages. Capacitive effects are primarily a concern during above-ground construction due to the negligible capacitance between buried pipelines and the Earth. The discussion clarifies that while buried pipes experience induced voltages from magnetic fields, the electric field's influence is minimal because of the surrounding ground's conductivity and potential. Overall, the interaction between power lines and pipelines involves complex electromagnetic principles that vary based on the pipeline's location and coating.
mrmojorizing
Messages
7
Reaction score
0
Hi,

I've been reading papers about the influence of high voltage overhead AC power lines on steel pipelines that run parallel to the power lines in the same right of way (that is near the power lines). The pipelines are coated in a dielectric coating to prevent corrosion and can be above ground or underground.

Based on the papers I have read there are 3 ways in which the power lines can influence the pipeline:

1) through magnetic induction due to the AC current in the power lines
2) through conduction during a fault where a large current enters the ground causing a rise int he ground potential relative to the pipe metal, due to the dielectric coating separating the pipe form the ground
3)through capacitive effects -- which i believe is the influence of the E field from the power lines on the pipe, although I'm not clear on this. Apparently it's supposed to be due to electrostatic effects, but i don't see how this can be when you have an ac (changing) field.

So anyway, my question is: Do I understand the capacitive effects correctly? Capacitive effects are due to the E field of the EM waves from the power line?

Also the papers mention that: "a [capacitance] potential is not normally induced on a buried pipeline since the capacitance between the pipeline and Earth is negligible,even when dielectric bonded coating sare used." and "However, during installation, a voltage can be produced by the influence of a strong electrical field on an insulated pipe when located above and insulated from the ground."

So my additional questions are: Why is it that voltage induced by the AC magnetic field is a concern on buried pipelines while the voltage induced by the electric field from the power lines is not? why is the capacitive voltage primarily a concern during above ground construction?

Some papers on this topic are at the links below.

Thanks

or wait, I think I see where I misunderstood. 60 Hz is too low to produce any EM waves, so we are really only doing with "electrostatic" influences for that reason -- even though the E field changes?


http://www.elkeng.com/pdfs/11-Basic Concepts of Induced AC101994.pdf
http://www.dipra.org/pdf/ACpowerLines.pdf
http://ie.utcluj.ro/Contents_Acta_ET/2009/Number4/Paper11_Purcar.pdf
 
Last edited by a moderator:
Engineering news on Phys.org
In terms of electric field, perhaps an easy way to see this is to put an unearthed infinite cylinder below an infinite cylinder at some given HV potential and to put these cylinders on top of an infinite plane at potential zero. The electric field generated by the HV line would create a potential in the conductor below. However, if the cylinder is buried, it is at ground potential so there is no potential coming from the E field of the line. In practice, ground has some conductivity as well, so the pipe is part of a surrounding conductor with varying conductivity, but the potential might be negligible for good conductivity soils. Hence, if some part of the pipe is under a line above ground, it will get some potential, while the rest of the pipe which is not under the line will be at another potential. The gradient of potential will create a current density, since the conductivity is different than zero.

On the other hand, whether buried or not, conductors that are submitted to time-varying magnetic field (B) will pickup induced voltage that will create induced current.

Hope this helps,

M.
 
But if the pipe is coated with a dielectric coating, it's not at ground potential, so I don;t understand why below ground pipes don't suffer from capacitive effects -- there will still be a capacitance between the pipe and the ground since they are at different potentials.
 
mrmojorizing said:
But if the pipe is coated with a dielectric coating, it's not at ground potential, so I don;t understand why below ground pipes don't suffer from capacitive effects -- there will still be a capacitance between the pipe and the ground since they are at different potentials.

Because the capacitance between the ground an the pipe is very large (comparatively) and the capacitance between the line and the pipe is very tiny.
 
Actually, not only that, but if the surrounding Earth is at 0 potential, where would the electric potential come from?

M.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...