Effect of voltage on resistance wire life expectancy?

AI Thread Summary
Using a 30kW air heater rated at 380V with a supply of 415VAC can significantly impact the life expectancy of the resistance wire, as the higher voltage increases power dissipation and heat generation beyond design specifications. This overheating poses safety risks, potentially damaging the heater and affecting any fan motors. While a step-down transformer could mitigate the voltage issue, it may be costly and hard to find. Renting a 415V heater is suggested as a temporary solution, but it can be more expensive than the existing heater. Consulting an electrician for a dedicated 380V service is also recommended to ensure safe operation.
kyle pender
Messages
6
Reaction score
0
I am using a 30kW air heater which is using resistance wire. I am not exactly sure what type of wire it is and hope this will not be an issue in answering this question.

The heater is rated at 380V and 45amps(max)...my supply is 415VAC (+ 6% and - 10%) and 45amps.

Any idea if this extra voltage will effect the life expectancy of the element?

Thanks
 
Engineering news on Phys.org
Probably bad - if the rating of 380 and the supply of 415 are apples-to-apples numbers. The power dissipated in the element is V^2/R, so the element will be hotter than the heater design anticipates. This is dangerous to do with a heater, imo.

If there is a fan in the heater, the fan motor is potentially going to react poorly to being over-voltaged.
 
http://www.frankshospitalworkshop.com/electronics/training_course/images/bulbs_life_expectancy1.jpg

Incandescent bulbs also heat wires, so this curve should be relevant. Pay attention to what @Grinkle said about safety, especially with so much power involved. you could burn the place down.
 
Last edited by a moderator:
Would a step down transformer be an option?
 
A transformer would work, but it might be hard to find and expensive. If this is temporary and not permanent, Renting a 415v heater might be the cheapest solution.
 
Yeah, I just had a quick look and they are extremely expensive...more than the heater itself! I am having trouble sourcing an off-the-shelf air heater which can provide the output temperature I need (at least 750°C at an air flow rate of 40-55 SCFM).
 
How about an electrician to get you 380v service?
 