Emf without load and load voltage of a generator

AI Thread Summary
An industrial equipment with an ungrounded metal casing showed a ground tension of 382 VAC, but a 220 VAC bulb remained off when tested. The high voltage reading from the Fluke meter is attributed to its high impedance, which creates a voltage divider effect with the generator's lower internal impedance. When a 100-watt bulb was connected, its lower impedance caused the voltage to drop to millivolts. Leakage current through the insulation can increase voltage from the casing to ground, posing a safety risk as insulation deteriorates. Grounding the metal casing is strongly recommended to mitigate hazards associated with increased leakage current.
bachir1994
Messages
18
Reaction score
2
HelloLast week I was confronted with a situation where an industrial equipment, with a large equipotential mass (metal casing) that was not grounded, had a ground tension, measured with Fluke, of 382 vac. I put a 220 Vac bulb and nothing happens, the bulb remains off and is not burned out.

By measuring the voltage with the lamp as a charge it is a few millivolts. I even touch the carcass without feeling anything.

My interpretation is:

The voltage measured with the impedance of the fluke (Zfluke) >>> 20 M Ohm which is surely much higher than the internal impedance of the generator that is seen between the ground and the carcass of the equipment (E generator, Z generator), gives a high voltage (Vfluke) (voltage divider).

As soon as a 100 watt bulb is placed with an impedance close to 500 ohm (Z bulb), this impedance is considerably less than the internal impedance of the generator seen between the ground and the carcass of the equipment, which makes That the voltage at the voltage divisor point drops to the millivolt range.Thank you
 
Physics news on Phys.org
bachir1994 said:
HelloLast week I was confronted with a situation where an industrial equipment, with a large equipotential mass (metal casing) that was not grounded, had a ground tension, measured with Fluke, of 382 vac. I put a 220 Vac bulb and nothing happens, the bulb remains off and is not burned out.

By measuring the voltage with the lamp as a charge it is a few millivolts. I even touch the carcass without feeling anything.

My interpretation is:

The voltage measured with the impedance of the fluke (Zfluke) >>> 20 M Ohm which is surely much higher than the internal impedance of the generator that is seen between the ground and the carcass of the equipment (E generator, Z generator), gives a high voltage (Vfluke) (voltage divider).

As soon as a 100 watt bulb is placed with an impedance close to 500 ohm (Z bulb), this impedance is considerably less than the internal impedance of the generator seen between the ground and the carcass of the equipment, which makes That the voltage at the voltage divisor point drops to the millivolt range.Thank you

You have the basic idea. Leakage current through the insulation system increases voltage from the electrically insulated metal case to ground, and it will approach applied line voltage. I strongly recommend adding a conductor to bond the metal case to ground. As the insulation system ages it will pass progressively more current. Once it is capable of currents of 1 ma and more it becomes a safety hazard, and not too much more leakage current can be lethal.
 
Thread 'Motional EMF in Faraday disc, co-rotating magnet axial mean flux'
So here is the motional EMF formula. Now I understand the standard Faraday paradox that an axis symmetric field source (like a speaker motor ring magnet) has a magnetic field that is frame invariant under rotation around axis of symmetry. The field is static whether you rotate the magnet or not. So far so good. What puzzles me is this , there is a term average magnetic flux or "azimuthal mean" , this term describes the average magnetic field through the area swept by the rotating Faraday...