Estimating the dehumidification rate of an air conditioning unit involves modeling heat transfer through a cooling coil and using psychrometric charts to determine specific humidity changes. The air leaving the unit is often assumed to be saturated, but it quickly mixes with room air, resulting in lower relative humidity. The user needs to achieve a coil surface temperature of -5 degrees Celsius to reach 30% relative humidity at 10 degrees Celsius, which may lead to ice formation on the coil. Selecting an appropriate AC unit requires understanding the manufacturer's ratings, which include inlet temperature, humidity, airflow, and coil capacity. The discussion highlights the complexity of accurately estimating condensation rates and the potential need for alternative dehumidification methods.
preet
Messages
96
Reaction score
0
Hey all,

I'm working on a project where I'm trying to use the inherent dehumidification ability of air conditioners to remove moisture from a closed environment. I would like to estimate the amount of condensation (and hence moisture removal) that occurs. I don't have access to the air conditioning unit -- we're trying to spec the unit based on our estimations. To approximate the condensation rate, I'm modeling the problem as heat transfer through a cooling coil.

[PLAIN]http://img201.imageshack.us/img201/1413/72151171.png

I'd like to know whether the method I'm using is appropriate, or I've overlooked something. Any other feedback/advice would also be awesome :)
 
Last edited by a moderator:
Engineering news on Phys.org
If you have the capacity of the coil, you can't figure out how much sensible vs latent heat cooling you get by calculation alone. You need to use a psychrometric chart to calculate it based on the incoming air conditions and the assumption that the leaving air is saturated.
 
Hey Russ,

Thanks for the reply. Why do I assume the air leaving the unit is saturated? Doesn't the A/C unit dehumidify the air? I understand that the w.vap would be saturated around the coil, but if you put your hand in front of the outlet of an A/C unit the air isn't wet (doesn't feel like RH of 100).

Just to confirm: If I used psychrometric charts, all I'd need to do is guess an output temperature and use an RH of 100%. That'd get me the specific humidity through the chart. Since I can calculate specific humidity at the inlet as well, the difference between the two states would give me the condensation rate right?
 
I read up on this problem more and I think I understand it a bit better. My system needs to go from 60% relative humidity at 26 deg C to 30% relative humidity at 10 deg C. I plotted this process on a psychrometric chart... It's denoted by the '1' line.

[PLAIN]http://img405.imageshack.us/img405/6366/20125266.png

In my case I need a coil surface temp of -5 degrees C to attain 30% RH at 10 deg C.

The chart tells me the ADP of an ideal system where all my air becomes the ADP temp and is 100% saturated at the outlet of the AC unit. This gives me the coil surface temperature of the ideal system. I'm stuck on how to choose an existing AC unit based on this information because all I'm given is the cooling capacity (in BTU for example), but I wouldn't know the surface temperature of the coils. How do I proceed from here?

Preet
 
Last edited by a moderator:
Sorry, it's been a long week at work and I kinda forgot about you, but you seem to have mostly figured it out on your own...
preet said:
Hey Russ,

Thanks for the reply. Why do I assume the air leaving the unit is saturated? Doesn't the A/C unit dehumidify the air? I understand that the w.vap would be saturated around the coil, but if you put your hand in front of the outlet of an A/C unit the air isn't wet (doesn't feel like RH of 100).
In front of the outlet, the air quickly mixes with room air to yield warmer, lower relative humidity air. The air in the unit all passes over the coil and thus all gets cooled. To use another example, a glass of ice water sitting in a room will not cool the air across the room from it, but it does cool the air in a thin film surrounding the glass down to 0C.
Just to confirm: If I used psychrometric charts, all I'd need to do is guess an output temperature and use an RH of 100%. That'd get me the specific humidity through the chart. Since I can calculate specific humidity at the inlet as well, the difference between the two states would give me the condensation rate right?
Correct.
In my case I need a coil surface temp of -5 degrees C to attain 30% RH at 10 deg C.
That's a pretty tall order, particularly because you will get ice on your coil and not water. You may need to pursue an altogether different dehumidification method, such as dessicant dehumidification. If I may ask, what is the reason for this low humidity need?
I'm stuck on how to choose an existing AC unit based on this information because all I'm given is the cooling capacity (in BTU for example), but I wouldn't know the surface temperature of the coils. How do I proceed from here?
Coils are rated under certain conditions (inlet temp, humidity and airflow), so the manufacturer's rating should include the inlet temperature, humidity, airflow and the coil capacity, from which you calculate the leaving temperature, as you did above.
 
Here's a video by “driving 4 answers” who seems to me to be well versed on the details of Internal Combustion engines. The video does cover something that's a bit shrouded in 'conspiracy theory', and he touches on that, but of course for phys.org, I'm only interested in the actual science involved. He analyzes the claim of achieving 100 mpg with a 427 cubic inch V8 1970 Ford Galaxy in 1977. Only the fuel supply system was modified. I was surprised that he feels the claim could have been...
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...