Exploring Transformer Connections for Step Up/Down Transformers

AI Thread Summary
The discussion focuses on the transformer connections used in step-up and step-down transformers, highlighting common configurations like star and delta connections. It emphasizes that a star connection with a grounded neutral is typical for secondary sides at 120/240 volts to support single-phase circuits, while primary sides may vary. The conversation also touches on the grounding practices in the UK and the US, noting that neutrals are usually earthed to enhance safety and reliability. Additionally, the use of resistors in grounding configurations is discussed for limiting fault currents and improving system monitoring. Ultimately, the conversation concludes that there is no one-size-fits-all solution for transformer connections, as configurations depend on specific safety and reliability needs.
KraakeCrest
Messages
18
Reaction score
2
Hi
Take a look at the picture below, I am curious of what transformer connections are used at each step up/step down transformer. I am sure that there are several way of connecting them and each have their pros and cons, but what are the most usual connections?

Lets start at the consumer and work backwards:
I would assume that there is a star connection with neutral on the secondary side at the 120/240 voltage level to support single phase circuits etc. On the primary side, maybe a delta connection or star with neutral to be able to support the flow of zero sequence currents?

Green substation step-down transformer:
Not sure, but I would assume a three conductor configuration to avoid the extra cost of a 4th wire on the primary side.

Generator step up transformer:
Same here, three conductor configuration on the secondary to avoid a 4th wire. Unsure about primary side.

And are the star "neutral point" always grounded or are there exceptions?
ElectricPowerSystem.jpg
 
Engineering news on Phys.org
KraakeCrest said:
I would assume that there is a star connection with neutral on the secondary side at the 120/240 voltage level to support single phase circuits etc.
KraakeCrest said:
And are the star "neutral point" always grounded or are there exceptions?
The Neutral is usually Earthed (in the UK) but that Earth isn't always made available to the house, in such cases a local Earth rod may have to be used. There are various earthing strategies used in the UK..

http://wiki.diyfaq.org.uk/index.php/Earthing_Types

Sorry no idea why the font size is off in this post.
 
  • Like
Likes KraakeCrest
KraakeCrest said:
Green substation step-down transformer:
Not sure, but I would assume a three conductor configuration to avoid the extra cost of a 4th wire on the primary side.

Be aware my experience is all In US

Here it's a four wire connection with neutral earthed so that a phase to ground fault will trip its feed.
Look at the poles in your neighborhood,
around here the neutral wire is the smaller one on shorter insulators usually installed lower than the phase conductors.
In high lightning areas it's often run on top to serve as a lightning rod,
in other areas it's run below the others so that should a phase wire fall it will likely hit the neutral and trip the feeder rather than falling across a roadway energized..
Also - should an overheight truck hit a wire you'd want it to be the neutral.

KraakeCrest said:
Generator step up transformer:
Same here, three conductor configuration on the secondary to avoid a 4th wire. Unsure about primary side.
Only configuration I've seen for power plants -

Stepup secondary is wye, grounded neutral for same reason as above.

On primary side the stepup transformer is delta connected and hardwired to generator by what @anorlunda referred to as "isophase" bus.
Generator is wye wound.
Generator's neutral is earthed through a huge high power resistor whose job it is to limit fault current to a value low enough it won't cause an electrical explosion inside the generator, twenty amps or less.. In my plant that resistor was the size of a pickup truck.

old jim
 
  • Like
Likes KraakeCrest and Asymptotic
jim hardy said:
In my plant that resistor was the size of a pickup truck.
Indeed. I just Googled for an image and found this one. (compliments of http://www.kiantajhiz.com/en/Products/211)

dimensions.jpg
 
  • Like
Likes KraakeCrest, Asymptotic and jim hardy
To further Jim's comment... many older systems were Delta secondary, this had been preferred for reliability, as a single ground fault would not cause an outage since it would actually take 2 ground faults, typically on different phases to get the system to trip - but this was very dangerous and unreliable. Then rudimentary Ground Fault detection schemes were set up - the 3 light bulbs... often not causing a trip, but an indicator that there was a fault relying on those inconstant humans to monitor and take action..

Today - the wye secondary, has both safety and filtering benefits. Using a resistor on the neutral-grounding point connection when there is no neutral load, provides a known ground reference to the whole system. Or a known state. It is relatively easy to detect an abnormal conditions now by monitoring the current flow through the resistor. This can trigger an investigation or a system trip, all depending on the application, safety aspects, and reliability requirements. For example feeding a neighborhood the emphasis is on safety, feeding the back-up cooling of a nuke... well reliability.

So - for safety - you may be just wanting to limit the fault current, and trip almost instantly, for reliability, the system can be configured to allow a full time, continuous ground fault, setting off alarms, but not tripping off the system. Also - the Ground Fault current can be traced, sometimes allowing the location of the fault to be identified, and isolated without tripping the entire system.

Basically - there is never a one ideal solution for every situation.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...