Fast PLCs for Sensor Monitoring & Relay Triggering

  • Thread starter Thread starter opmal7
  • Start date Start date
AI Thread Summary
The discussion centers on the use of a PLC for monitoring an analog sensor input and triggering a relay for a solenoid. A delay of approximately 75ms is observed from the sensor signal reaching a threshold to the relay activation, primarily attributed to the Siemens PLC's processing time. The PLC scans inputs, stores values, and compares them, which contributes about 65ms to the overall delay. Users are seeking recommendations for faster PLCs or alternative solutions to minimize this delay, highlighting the unexpected slowdown caused by the PLC in a system where speed is typically expected. The conversation suggests contacting PLC manufacturers for potential faster models or configurations.
opmal7
Messages
26
Reaction score
0
I'm working on a project uses a PLC to monitor an analog input from a sensor. Once the sensor's signal exceeds a certain value, the PLC sends a command to a relay to fire a solenoid.

I've hooked the system up to an o-scope, and I'm seeing a delay of about 75ms from the time the sensor reaches the point to when the relay triggers. I am using solid state relays with 5ms delay, and the sensor operates at 500 Hz. I am using a Siemen's PLC, which I believe is causing most of the delay. From reading the PLC literature, it sounds like the PLC scans the input, stores the value to a memory location, and then looks to that memory location to compare the values. This whole process takes about 65ms.

I would like to reduce the delay as much as possible. Are there any super fast PLC's on the market that would operate faster? I would expect to find most of the delay in the sensor, relay, and solenoid and am surprised that the PLC is what is slowing me down. You would think that with computers being so fast nowadays the computing part should be the quickest.

I'm looking for suggestions on fast PLC's, but am open to other ideas that might reduce the delay in this type of system.
 
Engineering news on Phys.org
opmal7 said:
I'm working on a project uses a PLC to monitor an analog input from a sensor. Once the sensor's signal exceeds a certain value, the PLC sends a command to a relay to fire a solenoid.

I've hooked the system up to an o-scope, and I'm seeing a delay of about 75ms from the time the sensor reaches the point to when the relay triggers. I am using solid state relays with 5ms delay, and the sensor operates at 500 Hz. I am using a Siemen's PLC, which I believe is causing most of the delay. From reading the PLC literature, it sounds like the PLC scans the input, stores the value to a memory location, and then looks to that memory location to compare the values. This whole process takes about 65ms.

I would like to reduce the delay as much as possible. Are there any super fast PLC's on the market that would operate faster? I would expect to find most of the delay in the sensor, relay, and solenoid and am surprised that the PLC is what is slowing me down. You would think that with computers being so fast nowadays the computing part should be the quickest.

I'm looking for suggestions on fast PLC's, but am open to other ideas that might reduce the delay in this type of system.

Yikes, that is a long delay. I'd start by calling the Customer Support folks at the company that makes the PLC. They may have some other options for PLC units with (much) faster processing delay.
 
opmal7 said:
From reading the PLC literature, it sounds like the PLC scans the input, stores the value to a memory location, and then looks to that memory location to compare the values. This whole process takes about 65ms.

I'm wondering what all else your PLC is doing?

It takes some time for the processor of the PLC to evaluate all the rungs and update the I/O image table with the status of outputs.[5] This scan time may be a few milliseconds for a small program or on a fast processor, but older PLCs running very large programs could take much longer (say, up to 100 ms) to execute the program.

Programmable logic controller Scan time
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...