Fire protection -- Water in a cylinder pressurized with Nitrogen
The discussion revolves around the pressure dynamics in a pressurized cylinder used in fire protection, specifically focusing on the relationship between the volume of water expelled and the remaining nitrogen gas pressure. Participants explore the application of Boyle's law and gauge versus absolute pressure in this context.
  • One participant seeks assistance in calculating the remaining pressure after expelling 200 liters of water from a cylinder containing 40 liters of nitrogen at 10.0 bar.
  • Another participant suggests that once the cylinder is empty, the pressure would be at atmospheric pressure, which is 1 bar.
  • A participant notes that the remaining pressure depends on whether gas is expelled with the water and if the valve remains open after the water is expelled.
  • One participant applies Boyle's law to calculate the expected pressure after the water is expelled, considering the initial conditions and whether the pressure is absolute or gauge.
  • Further details are provided regarding the flow rate of water being released and the specific pressure threshold of 7.0 bar that the nitrogen gas pressure must not drop below.
  • Another participant confirms that the pressure being discussed is gauge pressure and explains the difference between gauge and absolute pressure.
  • A participant calculates the volume change of nitrogen gas needed to reach a pressure of 7.0 bar and estimates the time required for this to occur based on the flow rate.
  • One participant points out that the various statements made about the pressure and water release do not all refer to the same scenario.
Participants express differing views on the implications of pressure changes and the conditions under which these calculations apply. There is no consensus on the exact outcomes or interpretations of the pressure dynamics involved.
Participants have not specified all assumptions, such as the behavior of the gas during water expulsion and the design of the cylinder. The discussion also involves the distinction between gauge and absolute pressure, which may affect calculations.
chrismof
I wondered if anyone could help, I work in the fire protection industry. We currently have a project using a pressurised cylinder. The cylinder hold 200 lites of water plus 40 litres of nitrogen gas as a propellant at 10.0 bar. I’m trying to work out once the 200 litre water volume has been expelled what would be the remains pressure. I believe the formula to use is Boyles law but I’m struggling to understand. Would appreciate it if anyone could help.
When it's empty doesn't that mean it's at atmospheric pressure? So 1 bar?
The answer will depend on the amount of gas that has left the tank, which in turn depends on two things you haven't specified: 1) Is the design such that gas sprays out with water? 2) Is the valve left open after the last of the water has been forced out of the tank?
The volume of the reservoir is 200 litres of water plus 40 litres of gas = 240 litre.
40 litres at 10 bar will expand to 240 litres at ? bar, to expel the 200 litres of water.
P1·V1 = P2·V2; holds for absolute pressures.
If the 10 bar is not absolute, but is gauge pressure, then the initial pressure will be 11 bar(abs).
P2 = P1 * V1 / V2 = 11 * 40 / 240 = 1.833 bar(abs) = 0.833 bar(gauge).
Thanks to all your prompt replies. The nitrogen gas is not mixed with the water but remains at the top of the cylinder until activated. Further to my question the release of the water would be at 14.16 litres / minute for approximately 13 minutes. What I am trying to check is at what point the nitrogen gas pressure would drop below 7.0 bar.
Can you confirm that the pressure you are specifying is the gauge pressure, above atmospheric pressure. Do you understand why the absolute pressure is one bar higher than the gauge pressure?
P1 = 10 bar(gauge) = 11 bar(abs);
V1 = 40 litre;
P2 = 7.0 bar(gauge) = 8.0 bar(abs);
V2 = V1 * P1 / P2;
V2 = 40 * 11 / 8 = 55 litres;
The change in gas volume is V2 - V1 = 55 - 40 = 15 litre of water.
For a constant flow rate of 14.16 litres / minute, the pressure would fall to 7.0 bar(gauge) in;
15 / 14.16 = 1.06 minutes = 63.6 seconds.
Hi,
Thank you for your reply the pressure would be the gauge pressure.
These are not all the same point.
  • · Replies 69 ·