Friction loss to vertical pipes in a closed system?

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
5 replies · 4K views
TSN79
Messages
422
Reaction score
0
So in designing closed systems, mostly heating systems, I realized today that I've probably been doing one thing wrong all these years. In such a system one doesn't take elevation loss due to gravity into account since you "get it back" on the way down. This I've always been aware of, but what I've still been doing is treating the vertical lengths of pipe as if they were horizontal, that is applying to them a friction loss per meter. Can someone just confirm that I can stop doing this? I'll just go back to my corner and be ashamed...
 
Physics news on Phys.org
Chestermiller said:
Have you estimated how much of a pressure difference is involved as a result of the elevation differences, as compared with the frictional losses?

Pressure loss due to elevation would be much higher than the major head loss per meter. Elevation loss is just a result of gravity, 9,8 kPa/m in addition to the friction loss, compared to about 0,15 kPa/m in the horizontal piping. But I believe the elevation loss doesn't need to be considered at all in a closed circulating system.
 
Chestermiller said:
What about when you select the fan? Doesn't it need to have enough ooomph to get significant air flow to the upper floor(s)?

It's a central heating system, so there is a water circulation pump, not a fan.
 
TSN79 said:
So in designing closed systems, mostly heating systems, I realized today that I've probably been doing one thing wrong all these years. In such a system one doesn't take elevation loss due to gravity into account since you "get it back" on the way down. This I've always been aware of, but what I've still been doing is treating the vertical lengths of pipe as if they were horizontal, that is applying to them a friction loss per meter. Can someone just confirm that I can stop doing this? I'll just go back to my corner and be ashamed...

Technically you should consider the elevation changes so you can size your pump correctly. I imagine that since it's a closed loop system that is being constantly recirculated that you'll end up with the same answer. Why not just run a couple of hand calcs and do one like you've been doing it and then one that includes the elevations and see what the results tell you?